Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Testing new controls/monitoring for Midea Clone ASHP
Ok some more info on the new setup which may be of interest- specifically the comfort offset automation which adjusts the flow temperature if the IAT is outside of the comfort parameters, and an interesting observation over the last couple of days now that it is a bit warmer.
The above shows the comfort offset history for the month, so it will adjust the LWT by 2 degrees C either way, depending if the IAT is undershooting or overshooting. It hasn't actually run that much, which is what I was hoping/expecting. On 13th March it must have been windy and needed a boost. On the other days where it has offset -2, this will be down to solar gain.
What the adjustment effectively does when warmer, is that it turns the ashp off- so if the set LWT is then below 29 degrees C which is the lowest temp that it will run. This actually works perfectly. As per this graph (red arrow where the comfort offset has pushed the set LWT below 29)
I think now I can confidently say this is our ideal setup in terms of control strategy, and I can probably leave as it is.
@benson — well done! My auto-adapt does pretty much the same thing, infrequent but useful adjustments. The advantage of using our own code is that we can tweak it to achieve control that works for our particular setup.
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @cathoderayMy auto-adapt does pretty much the same thing, infrequent but useful adjustments.
I presumed when Gemini was writing the automation code for me, that it was data farming from your forum posts about your set up 😆
It does work well- thanks for all of your help, and everyone else who has advised along the way.
Posted by: @bensonI presumed when Gemini was writing the automation code for me, that it was data farming from your forum posts about your set up
Spooky! I think you already know I don't use AI much, but if I did, and found myself asking it a question and finding the answer seemed curiously familiar, I might end up thinking I need to start taking the tablets again!
Posted by: @bensonIt does work well- thanks for all of your help
A pleasure, and thank you for documenting what you have done here. I am sure the other who have contributed have also been glad to do so.
Midea 14kW (for now...) ASHP heating both building and DHW
@cathoderay For what is worth, it was recently pointed out to me, in a Greek heat pump forum, that certain high-end manufacturers, like Hitachi or Daikin, do indeed offer an IAT compensation mode.
So I had a look at a Hitachi Yutaki ASHP manual and indeed there is an option of room temperature compensation, which I quote:
"Room Temperature Compensation
If room compensation is enabled, the calculated OTC supply set-point is adjusted based on the difference between room temperature and room set-point in order to reduce the room error. The amount of room influence can be adjusted by the room temperature compensation factor setting (can be adjusted, default 2).
Example
Compensation factor = 2,
SR1 (room set-point) = 20,
TR1 (room temperature) = 23
=> S1 (supply set-point) reduced by 2 * (23 – 20) = 6C "
Even though this is a rather crude approach, I think it does show the future, which is very well predicted by your reported actions here.
Midea MHCV10WD2N7 R290, 5.8kWp energy community solar power.
@tasos — despite what Gemini may have been up to, I don't claim any originality for what I did, which was simply to implement a basic feedback loop! I had the idea of such a DIY implementation after hearing about Ecodan's auto adapt mode, and thinking setting up something similar in python should be very straight forward (and it turns out it is). I haven't done the same thing for forecast weather, because a forecast is only a forecast, but I am sure it could be done without too much extra effort ('if forecast windchill > X then increase LWT by 1°' etc) by anyone who wanted to add it.
Midea 14kW (for now...) ASHP heating both building and DHW
- 26 Forums
- 2,623 Topics
- 61.3 K Posts
- 709 Online
- 7,004 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Is Traditional Radiator Balancing Tosh?
@markspencersmith Before I offer my thoughts I am...
By JamesPa , 10 hours ago
-
RE: Brown Oily Residue Blocking Air Vent and Weeping Relief Valve... Anyone Seen This?
@editor i'm SEPA Registered with a waste license, we du...
By Aventus Eco , 12 hours ago
-
RE: Grant Aerona3 - Home Assistant control via Modbus
what controller are you using?
By Grantmethestrength , 14 hours ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Manufacturer: appliances direct/superheat Model: 7Kw ...
By Adrian , 16 hours ago
-
RE: Peak Energy Products V therm 16kW unit heat pump not reaching flow temperature
As a final update on this thread from me; Ribble Valley...
By DaveC , 16 hours ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Fantastic. This is all I needed. Afew planning applic...
By Batpred , 19 hours ago
-
RE: Renewables & Heat Pumps in the News
Commentary on DCs and the grid in the EU. A bit on some...
By Jeff , 23 hours ago
-
RE: Mitsubishi Ecodan not good enough ?
If you put a fan in a pipe you get a much more efficien...
By bobflux , 1 day ago
-
RE: Mitsubishi ecodan settings
As the owner of a 8kW Ecodan R290 maybe I can help. ...
By RobS , 1 day ago
-
Wall mounting makes sense. We are now looking for an in...
By Batpred , 2 days ago
-
RE: Vaillant AroTherm Plus 7kW
Thank you, watson did allow me to find this one! Our ...
By Batpred , 2 days ago
-
RE: Our 10 year old Grant heat pump failed
Sorry to hear. Grant seem to be selling the R290 pump...
By Batpred , 2 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
.. apparently with american fuel. 🙃
By Batpred , 2 days ago
-
RE: The Watchdog That Watched and Waited
Spot on. The watchdog that knows how to never take the ...
By Batpred , 2 days ago
-
RE: Indevolt Batteries UK Support & Info Thread
Yes, the cost difference may be marginal, if you are lu...
By Batpred , 2 days ago
-
RE: Don’t Install a Heat Pump Until You Read This
In our latest update, we attempt to show what a poor he...
By Mars , 2 days ago
-
RE: Heat Pump Pipe Sizing Question
No the retrofit strategy is already published. It's on...
By JamesPa , 2 days ago
-
RE: Ecodan spells out end of R32 for real environmental alternative
I think I saw the answer to this on another thread but ...
By Batpred , 2 days ago
-
RE: Mitsubishi Ecodan FTC6, Evohome & Economy 7. Getting Two Zones to Work Together
This is what we are trying to avoid if we go Ecodan, mu...
By Batpred , 2 days ago
-
Great points, I agree it is overused. It is also a grea...
By Batpred , 2 days ago
-
RE: GSHP Kaput After 16 Years: New Compressor or Switch to ASHP? Advice Welcome
On old (non inverter) compressors there’s sometimes a ‘...
By robl , 2 days ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
@editor It's available here -
By HarrisonC , 3 days ago
-
@painter26 i am in Lightwater and midea trained. Sounds...
By Wizard , 3 days ago