Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Testing new controls/monitoring for Midea Clone ASHP
Ok some more info on the new setup which may be of interest- specifically the comfort offset automation which adjusts the flow temperature if the IAT is outside of the comfort parameters, and an interesting observation over the last couple of days now that it is a bit warmer.
The above shows the comfort offset history for the month, so it will adjust the LWT by 2 degrees C either way, depending if the IAT is undershooting or overshooting. It hasn't actually run that much, which is what I was hoping/expecting. On 13th March it must have been windy and needed a boost. On the other days where it has offset -2, this will be down to solar gain.
What the adjustment effectively does when warmer, is that it turns the ashp off- so if the set LWT is then below 29 degrees C which is the lowest temp that it will run. This actually works perfectly. As per this graph (red arrow where the comfort offset has pushed the set LWT below 29)
I think now I can confidently say this is our ideal setup in terms of control strategy, and I can probably leave as it is.
@benson — well done! My auto-adapt does pretty much the same thing, infrequent but useful adjustments. The advantage of using our own code is that we can tweak it to achieve control that works for our particular setup.
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @cathoderayMy auto-adapt does pretty much the same thing, infrequent but useful adjustments.
I presumed when Gemini was writing the automation code for me, that it was data farming from your forum posts about your set up 😆
It does work well- thanks for all of your help, and everyone else who has advised along the way.
Posted by: @bensonI presumed when Gemini was writing the automation code for me, that it was data farming from your forum posts about your set up
Spooky! I think you already know I don't use AI much, but if I did, and found myself asking it a question and finding the answer seemed curiously familiar, I might end up thinking I need to start taking the tablets again!
Posted by: @bensonIt does work well- thanks for all of your help
A pleasure, and thank you for documenting what you have done here. I am sure the other who have contributed have also been glad to do so.
Midea 14kW (for now...) ASHP heating both building and DHW
@cathoderay For what is worth, it was recently pointed out to me, in a Greek heat pump forum, that certain high-end manufacturers, like Hitachi or Daikin, do indeed offer an IAT compensation mode.
So I had a look at a Hitachi Yutaki ASHP manual and indeed there is an option of room temperature compensation, which I quote:
"Room Temperature Compensation
If room compensation is enabled, the calculated OTC supply set-point is adjusted based on the difference between room temperature and room set-point in order to reduce the room error. The amount of room influence can be adjusted by the room temperature compensation factor setting (can be adjusted, default 2).
Example
Compensation factor = 2,
SR1 (room set-point) = 20,
TR1 (room temperature) = 23
=> S1 (supply set-point) reduced by 2 * (23 – 20) = 6C "
Even though this is a rather crude approach, I think it does show the future, which is very well predicted by your reported actions here.
Midea MHCV10WD2N7 R290, 5.8kWp energy community solar power.
@tasos — despite what Gemini may have been up to, I don't claim any originality for what I did, which was simply to implement a basic feedback loop! I had the idea of such a DIY implementation after hearing about Ecodan's auto adapt mode, and thinking setting up something similar in python should be very straight forward (and it turns out it is). I haven't done the same thing for forecast weather, because a forecast is only a forecast, but I am sure it could be done without too much extra effort ('if forecast windchill > X then increase LWT by 1°' etc) by anyone who wanted to add it.
Midea 14kW (for now...) ASHP heating both building and DHW
- 26 Forums
- 2,590 Topics
- 60.3 K Posts
- 989 Online
- 6,922 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Air-to-air heat pumps - best models and installers
@ashp-bobba, do I remember correctly that you install A...
By Mars , 5 hours ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
There isn’t as far as I know, @djh, but you’re welcome ...
By Majordennisbloodnok , 9 hours ago
-
RE: Can anyone explain the following behaviour with a Grant Aerona 3 R30 / Smart Controller?
Final Update. Yesterday, I was going through the moti...
By Unsure , 10 hours ago
-
RE: How much can an east/west solar solar system be oversized?
Best performance occurs with PV string near inverter no...
By bobflux , 10 hours ago
-
RE: Forum updates, announcements & issues
Thank you Mars for all your dedication to improvements;...
By Toodles , 13 hours ago
-
RE: Who do I complain to about a poor ECO4 installation, can anyone advise?
Take it one step at a time. If you can get the dhw and...
By JamesPa , 20 hours ago
-
RE: Selling 2 x Kensa Shoebox 7kw GSHP (New)
Hi Jain, we’ve got an ashp so I’m afraid we won’t be yo...
By Judith , 20 hours ago
-
No buffer or low loss header Grant controller in sens...
By JamesPa , 1 day ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
That's an amazing job to get all that in there! A truly...
By Batpred , 1 day ago
-
RE: Anyone concerned about GivEnergy?
Thanks for your advice - I'll keep trying with the inst...
By JohnDwyer , 1 day ago
-
RE: Plug and play solar. Thoughts?
I am also yet to find a case where an installation that...
By Batpred , 2 days ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
This is what I got from OVO. At least it was quick.. ...
By Batpred , 2 days ago
-
RE: IVT greenline HT Plus E - Circulation Pump Constantly On
Welcome to the forums. Irrespective of which brand yo...
By Mars , 2 days ago
-
RE: 7.5kW Heat Loss, But Quoted a 10kW Midea. No Re-Pipe, No Buffer Tank. Does This Add Up?
Oh, how I love these old scientists!I'm in with your 5 ...
By LeJamaisContent , 2 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@jamespa Someone who is not easily phased I suppose.
By Toodles , 2 days ago
-
@downfield Once OE had removed our gas meter and capped...
By Toodles , 3 days ago
-
Living with a Low Loss Header (Or Measure For Measure, it’s All About the Pump)
I know, low loss headers (LLHs) aren’t necessarily ‘low...
By Toodles , 3 days ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
After seeing umpteen negative price slots again today, ...
By ChandyKris , 3 days ago
-
RE: The Reality Behind a Failed Heat Pump Installation – and an IWA Insurance Rejection
@ian-w Getting back to the problem in hand, what do yo...
By JamesPa , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@papahuhu Generally, I leave Homely to take care of mat...
By Toodles , 3 days ago
-
@judith, glad you found the story interesting. On eff...
By Mars , 4 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
The vaillant controller and app do all of that (and mor...
By JamesPa , 4 days ago