Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
IVT greenline HT Plus E - Circulation Pump Constantly On
Hi, I moved into a new house 6 months ago with an IVT Greenline HT Plus E. I have gone on a big learning curve to optimise usage. Including managing the temperature, enabling wi-fi (using husdata), managing the hot water. That has brought bills down a lot. But the radiator pump is constantly on (even when heating is off) and I’m not sure why. Is this to make sure pipes don’t clog up? Or is this something I can/should turn off? Many thanks
Welcome to the forums.
Irrespective of which brand you have, the circulation pump running constantly when heating is off is not normal. It shouldn’t stay on in standby and that’s not an intentional “anti-clog feature”.
A few questions:
- If you turn the controller to “off” (not standby) does the circulation pump still remain on?
- When the unit is in standby, what does Husdata show for the heating circuit pump status?
- Is this the original pump inside the heat pump unit, or has an extra one been added? I’m assuming there’s a buffer tank.
🔥 Britain’s Heat Pump Shitshow
How Installing a Heating System Became a National Nervous Breakdown
Pre-order with free UK shipping.
Rewritten and updated for 2027
📘 From Zero to Heat Pump Hero
🛠️ Bodge Buster
New to heat pumps?
Take the Heat Pump Fundamentals course and use INTRO50 at checkout for 50% off.
- 27 Forums
- 2,750 Topics
- 64.7 K Posts
- 2,978 Online
- 7,158 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Who's your electricity provider and what's your tariff?
@papahuhu I prefer to look at it simplistically. We d...
By Old_Scientist , 3 minutes ago
-
RE: To re-pipe or not to re-pipe? Moving from oil boiler to air source heat pump.
Sooooo, what did we do in the end? We approached three ...
By Penval , 34 minutes ago
-
RE: How Accurate Is My DIY Heat Loss Calculation?
D'oh - of course. I shouldn't post before my brain is f...
By Old_Scientist , 6 hours ago
-
RE: Questions about A2A for heating as well as cooling
@rob-of-york I would concur with the underfloor insulat...
By Toodles , 8 hours ago
-
RE: New Vaillant Arotherm controls link to existing thermostats ; wired vs wireless
Nothing attached! I have rads but UFH makes the case ...
By JamesPa , 8 hours ago
-
RE: Cooling with air to water heat pumps
Passive cooling should always be the first call. Keep ...
By JamesPa , 9 hours ago
-
RE: Do I add Air Con or MVHR to existing A2W ASHP?
@rob-of-york Thank you, I’m thinking along these same l...
By Toodles , 1 day ago
-
@Mars Good questions! The downstairs unit did the maj...
By Rob of York , 1 day ago
-
RE: Volumisers in Heat Pump Systems: Does Placement Matter?
@dave, I think @jamespa has probably identified the mos...
By Mars , 2 days ago
-
RE: Plug and play solar. Thoughts?
My thought is simple. Bring it on and bring on plug in...
By JamesPa , 2 days ago
-
RE: Heat Geek mini store vs pump size
Yes I agree, that’s why Heat Geek have most likely sele...
By Tomtheheatingengineer , 3 days ago
-
@tomtheheatingengineer, thank you, and welcome to the f...
By Mars , 3 days ago
-
RE: HeatGeek vs Octopus surveys: puzzling disparity - any ideas why?
@majordennisbloodnok @tomtheheatingengineer For my ...
By JamesPa , 3 days ago
-
RE: Is the "divide by 2900" rule still valid?
Really flow rate is a pipework limitation not a water p...
By JamesPa , 4 days ago