Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
[Sticky] Struggling to Find a Top Heat Pump Installer? We Can Connect You With the Best Installers in the UK
Interesting. Ecogenica appear to be an Australian manufacturer trying to break into the UK. I downloaded the user manual and it is remarkable in that it actually tells you how to run a heat pump properly, not just what the controls do. Very admirable I must say and very unusual also.
My worry would be support if they don't succeed in getting sufficient business to make them viable long term in the UK. That's a bit of an unknown.
In terms of the quote it's light on detail but has no buffer or external controls which is good, and indeed what the manual says. However I presume this is pre survey so it's just preliminary.
How large and what construction is your house and do you have consumption figures for the current heating. Asking to sense check sizing.
Apart from the support question (which you may consider definitively terminal) I see no red flags at this stage and some reason to be encouraged. What are your other quotes saying?
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Hey everyone.
I had a quote from OVO southwest that I'm progressing to a heat survey. I do have to say that their ways of doing quotes was by far the best out of all the companies I spoke with, having me go room to room on the phone to give rad types and sizes and then them being very flexible in improving their offer.
I'd love to get opinions on Midea and the overall price I've been given. I've seen that Midea systems can be given a limited level of Home-assistant intergration, which is of interest to me.
According to to OVO Midea is doing a big push for the self branded units to be brought into the UK so they added quite a few incentives.
The proposed system highlights:
Midea R290 M thermal Arctic HT Series V8
3 rad changes
Elite Cyl Heatpump Unvented 250l tank
Ariator.
Magnet strainer
System flush + inhibitor.
All for £2,378 inc VAT (post BUS grant).
From my perspective this means that the system would pay itself off after about 4 years.
They have also offered a Vaillant 7kw for an extra £2.5k.
@jamespa Yes very much at preliminary stage.
It's a 1960s semi detached bungalow total area 64m2. Cavity wall construction with wall and loft insulation and double glazing. It will be replacing a combi so no cylinder currently in the property.
Most other suppliers have specified 5KW ashp and are coming in nearer 5K apart from Octopus who were around 3.8k
We have only been here since December so don't have our own annual consumption figures but from the EPC report
- 8,657 kWh per year for heating
- 1,921 kWh per year for hot water
OK I can't believe that's more than 5kW, probably only 3kW so the 8kW machine, unless the sticker capacity is very misleading, would almost certainly be well oversized (too much for it to be a good choice). Of course this could just be cautious quoting to be reduced on survey.
5kW is the smallest commonly available (there are firmware limited models with a lesser rating but not much point really) so not surprised several are quoting that.
Octopus seems to deliver consistently and are obviously well established.
It's a difficult choice TBH. Depends on your view of risk!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa I'm waiting for them to come back to me with a date for the survey and I will see what the outcome of that is.
My issue with Octopus is I don't like the look of the cost heat pump. I know it's subjective but to me it looks a bit like a bin you see in fast food car parks but I'm sure lots of people love the look of it?
Posted by: @damo76My issue with Octopus is I don't like the look of the cost heat pump. I know it's subjective but to me it looks a bit like a bin you see in fast food car parks but I'm sure lots of people love the look of it?
I have never seen one in the flesh but I do agree about the similarity based on the pictures!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Hello
I’ve sent an email to @editor asking if there are any recommended ASHP installers in County Durham.
Equally if anyone else has any recommendations on here, it would be great to hear them!
We’d want to install UFH at the same time - in case that’s relevant to the recommendations.
Thanks
Hi, I am new joiner to the forum. I am thinking of getting a heat pump for my house.
It's a three storey townhouse 90m2 built 2010 in Derbyshire
I have been given a quote of 4k
Heat loss of 4kW
Replace the hot water cylinder
And changes to some of radiators for water flow temp of 45
Does it seem right?
@little-lights welcome to the forums and I'll try connect you with installers on Monday.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
Posted by: @derbygrahamHi, I am new joiner to the forum. I am thinking of getting a heat pump for my house.
It's a three storey townhouse 90m2 built 2010 in Derbyshire
I have been given a quote of 4k
Heat loss of 4kW
Replace the hot water cylinder
And changes to some of radiators for water flow temp of 45
Does it seem right?
In a word yes, based on what you have told us.
You wont find many heat pumps with an output less than 5kW, and unless your house is very badly built its <<4kW
However you need to check
- No buffer tank, LLH, PHE (volumiser, connected to either flow or return but not both is OK)
- No third party controls, run on weather compensation not thermostats (so 45 max, decreasing as OAT increases)
You will also need to check workmanship as they go along
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@derbygraham fully agree with James, and it’d be good to know what brand of heat pump has been quoted for…
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
I have been quoted for a Midea R290 4kW unit
The installer has gone for midea over a Vaillant, as the unit will be located under a window and midea would fit better
- 26 Forums
- 2,721 Topics
- 63.7 K Posts
- 1,156 Online
- 7,123 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
It's a great looking piece of kit and the 5kw is very q...
By avenir , 9 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
I can't quite get my head around part 7 in the Indevolt...
By BlizzardGreen , 9 hours ago
-
RE: Advice on my Heat Pump Journey: Old Stone Built Detached Cottage
Well deserved! 👌 55°C to the rads is really h...
By bobflux , 12 hours ago
-
Potentially a winner this idea if it can be made cheapl...
By JamesPa , 1 day ago
-
RE: Existing Solar Panel installation - structural roof calculation check
My own solar panel fixing rails wouldn't pass the MCS r...
By Transparent , 1 day ago
-
RE: Vaillant Arotherm Pro vs new Plus
So with the dedicated Hager CU, flipping the big red bu...
By Batpred , 2 days ago
-
Well I usually do it by feel, which is a slight problem...
By Transparent , 2 days ago
-
@jeff I am well aware of the riskiness of such investme...
By Toodles , 2 days ago
-
Fully understood and entirely reasonable! On the home ...
By JamesPa , 2 days ago
-
RE: Electricity price predictions
So I am really having difficulty trying to work out wha...
By bontwoody , 3 days ago
-
Ok Well almost certainly it could be used instead of ...
By JamesPa , 3 days ago
-
RE: Samsung heat pump - data cable issue
Samsung reference it as "RS485 - COMM" in my manual. ...
By Old_Scientist , 3 days ago
-
RE: SolarEdge SE5000H Inverter Failure
Update. My SolarEdge inverter was replaced yesterday wi...
By L8Again , 3 days ago
-
For cooling a whole building, or even a big room with l...
By EtchedPixels , 4 days ago
-
RE: Comms and power cabling to outside unit
@old_scientist 100%, the cover is for warrantied unit...
By Papahuhu , 4 days ago