Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
[Sticky] Struggling to Find a Top Heat Pump Installer? We Can Connect You With the Best Installers in the UK
@jamespa - taking into account the usage of the wood burners and the energy profile that they chuck out over an evening, the divide by 2900 figure gives me 11.63 KW, the divide by 2 16.9 and the divide by 3 11.24 - these all having been corrected by 13/10.5.
I can see where the 2900 figure comes from but where do the 2000 and 3000 correction factors come from ? (I did search, but without success).
With regard to the thermal store, yes I am aware of this issue - the thermal store runs reasonably hot and is a totally unsuitable way to use a heat pump.
The installer who came out (but seems to have disappeared) said that the manifolds would benefit from replacement on account of the fact that they don't have flow meters and the mixer valves are no longer necessary (as you stated). To be honest, the manifolds we have are a pain in the neck as we have experienced leaks and I am unable to get the mixers to drop the flow temperatures sufficiently (they sit at about 45 degrees at present). That the actuators are forever causing issues would go away as they would be removed and flows set via flow valves.
thanks for the information that you have been feeding.
Ironically, our village is currently in the midst of a power cut .... thank goodness for battery backup and the capability of it to drive most of the light loads in the house and so keep me internet entertained !
Posted by: @ian33ao the 2000 and 3000 correction factors come from ? (I did search, but without success).
Me, I invented them (starting from 2900) to help with people on this forum who were getting silly quotes, and allowing for the fact that some oversizing isnt a disaster and anyway heat pumps have discrete steps in power (eg Vailant 5, 7, 12) and of course many people operate some kind of night time setback. Only a tiny amount of science behind it, but useful to give people some pretty hard limits to exclude silly heat loss surveys which still appear to be common (as in if your heat pump installer is suggesting that the loss > gas consumption/2000, probably best look elsewhere). 2000 could probably be 2500.
Posted by: @ian33aThe installer who came out (but seems to have disappeared) said that the manifolds would benefit from replacement on account of the fact that they don't have flow meters and the mixer valves are no longer necessary (as you stated). To be honest, the manifolds we have are a pain in the neck as we have experienced leaks and I am unable to get the mixers to drop the flow temperatures sufficiently (they sit at about 45 degrees at present). That the actuators are forever causing issues would go away as they would be removed and flows set via flow valves.
Sounds like he has his head screwed on! He is right, ditch the actuators and mixing, balance the loops for the desired differences in room temperature using flow adjusting valves, then let weather compensation do its job!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa thanks - that clears up my question on where the numbers come from - although I would be interested to understand why it may be acceptable to change the 2000 factor to 2500?
So, with my numbers using oil consumption coupled with your calculation method coming out at 11.24 11.63 and 13.49 (using a factor of 2500 for the latter) and 16.86 (using a factor of 2000) and my HeatPunk figure of 12 - is it fair to say in your mind that there is a reasonable correlation between what is being measured from oil usage and what HeatPunk is saying and that these could be used as a basis for a discussion with heat pump installers (once I can get somebody willing to actually set foot in the house and have a chat!) as a starting point for a heat loss analysis?
Posted by: @ian33aSo, with my numbers using oil consumption coupled with your calculation method coming out at 11.24 11.63 and 13.49 (using a factor of 2500 for the latter) and 16.86 (using a factor of 2000) and my HeatPunk figure of 12 - is it fair to say in your mind that there is a reasonable correlation between what is being measured from oil usage and what HeatPunk is saying and that these could be used as a basis for a discussion with heat pump installers (once I can get somebody willing to actually set foot in the house and have a chat!) as a starting point for a heat loss analysis?
Yest it is fair to say thats a reasonable correlation and in this circumstance I would be tempted to believe heatpunk.
I totally agree its a reasonable starting point, even then you may have problems with installers that ignore fabric upgrades they cant see or those that use unreasonably high ACH.
Posted by: @ian33a@jamespa thanks - that clears up my question on where the numbers come from - although I would be interested to understand why it may be acceptable to change the 2000 factor to 2500?
Well consider a 7kW house, in principle 20300kWh/year. Perhaps subtract up to 20% (unlikely) for fairly extreme part time heating - 16240 . Now take a gas boiler that is actually condensing with 110% 'efficiency' (obviously not strictly efficiency, just how the declared calorific value is calculated - but anyway very unlikely because of the (bad) way plumbers set up gas boilers) - 14700. So that would be a case of divide by 2000 to get loss. However the probability of both these occurring is very small, so somewhere in between is a reasonable point at which to raise suspicion, even if its not a hard limit. Furthermore if dividing by 2500 leaves you just above a size boundary, so you are pushed to the next, its perhaps time to think harder/get some more evidence.
Like I said not terribly scientific , but its only intended to weed out the silly quotes.
With half hourly meter readings I plotted daily average OAT vs daily consumption. I did a few other checks, but as I say with gas its easier.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa - Thanks ever so much - your patience and help has been much appreciated.
As a now retired engineer, I hate to have to accept blind faith numbers without reasonable science behind them. That my HeatPunk numbers broadly line up with the oil usage calculations gives me the confidence to have a meaningful discussion with an installer .... if I can find one who fancies visiting me !
@ian33a keep the faith. I am also a retired engineer and sympathise with your problem.
For me it was.a 2 year journey which culminated in an two paragraph, informal RFQ that basically told prospective installers what the loss was (with evidence) and what system configurations I was prepared to accept.
Of course some couldn't cope with this approach, but the ones that engaged were good. They had to go through the motions to satisfy MCS, but they found ways to interpret the rules to get the right result.
I ended up with two quotes that realistically I could have accepted, either of which I could have chosen on price and technical grounds, so it came down to proximity.
I count that as a good result, the (very simple) system is great in operation, far better than my boiler, and the price was pretty much the lowest I was quoted.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Of course some couldn't cope with this approach, but the ones that engaged were good. They had to go through the motions to satisfy MCS, but they found ways to interpret the rules to get the right result.Posted by: @jamespa
Same here lol
The fact the house had been heated for 40 years by a 12kW ground source heat pump could provide a bit of a hint about the actual heat loss...
I also had 5 years of data about the actual run time of the heat pump recorded by home automation...
After this I installed 200mm rockwool exterior insulation, double glazed windows, 400mm blown in fiberglass in the loft, etc...
My heat loss calculations still pointed towards 12kW, this time considering it would only run during the day to maximize photovoltaic self consumption, so already about 2x oversized...
I'm also installing 20kW log boiler disguised as fireplace...
Drum roll 🥁🥁🥁🥁🥁🥁
Every single installer went full retard, some of them wanted cascade, also all of them wanted buffer tanks, and I could only talk one down to "only a 16kW Mitsu with huge electric backup" after about two weeks of emails.
That's because if it is not powerful enough to heat the house to 21°C when it's -7°C outside (which never happens) they can be liable, so they play it safe.
I ordered the 16kW LG R290 from internet, put it in the garden, done. It's the exact same machine as the 12kW so the low end of the modulation range is the same, about 3500W, but it has 15kW cooling power. Nice. Also 10k€ cheaper than the Vaillant installer quote.
@jamespa Well, something along the lines of "three buses coming along at once" : Yesterday evening I approached two companies who are "emerging" on this website. First thing this morning I rattled the cage of the installer who visited last week and went quiet on me.
I got an invite to a 1:1 web based discussion with one of the companies (which is scheduled for tomorrow), the cage rattling worked and I got an estimate from the people who visited last week, and I spoke with the other company that I approached yesterday and they are visiting in a week from now to do a exploratory investigation and a heat loss calculation.
It looks like I may be getting somewhere afterall.
I applaud you for this initiative; however, I can see a problem with the Heat Geek offer (compared to, say, Octopus, CB Heating; Aria etc).
The Heat Geek offer is primarily one where the customer pays for a heat loss survey and on the basis of that survey a contract may be entered into to install a heat pump with Heat Geek. They appoint and pay the installation company. Despite the fact that the installer carries out a heat loss survey, the system design responsibility sits with Heat Geek and it is based on Heat Geek software. Heat Geek also provides the installer with the heat pump; controls; pipe and fittings, and insulation. From this point forward, the customer's engagement is with the installer. The final installation is commissioned and signed off by the installer with no Heat Geek involvement. Post installation issues are dealt with by the installer. This is different from Octopus etc in that they manage commissioning and issues top down not sideways as is the case with Heat Geek.
It follows that a customer might have a very neat installation from a heat pump siting and pipework point of view but one which is not efficient as suggested in the Heat Geek contract. Who is to blame for this: is it the design software or the installer/surveyor (GIGO)? In recent months, I have been told 'we would not have designed it this way or used these materials'. I was also told that the installer doesn't get to see the design maximum flow temperature until the commissioning paperwork has been completed.
I could recommend my installer to others on the basis of the work that has been completed. I would however be reluctant to recommend them to anyone who was looking for an installation outwith the HeatGeek system. Equally, I am reluctant to recommend Heat Geek as I do think that they need to take some oversight responsibility for their completed installations. I also think that they should be the first port of call for any post installation issues. In this regard, their technical specialists should be able to opine on whether the customer has a legitimate technical concern that needs to be addressed. Understandably, installation engineers are proud people and they tend to get a bit defensive when a lay person suggests that work has not been completed properly. It is a difficult conversation to have. From what I read, other large installation companies manage this relationship better. You might like to ask Heat Geek for comment.
- 26 Forums
- 2,721 Topics
- 63.7 K Posts
- 1,158 Online
- 7,124 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Air to air bus grant installer anywhere
society and politics require things to be made more com...
By Batpred , 2 hours ago
-
RE: Advice on my Heat Pump Journey: Old Stone Built Detached Cottage
I would also look at an air/air install if you've got t...
By EtchedPixels , 3 hours ago
-
That's more or less what octopus posted about on Facebo...
By JamesPa , 3 hours ago
-
RE: Existing Solar Panel installation - structural roof calculation check
What will also happen is that they see that there is so...
By EtchedPixels , 3 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
@indevolt-tech can you please assist @blizzardgreen.
By Mars , 5 hours ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
It's a great looking piece of kit and the 5kw is very q...
By avenir , 2 days ago
-
RE: Vaillant Arotherm Pro vs new Plus
So with the dedicated Hager CU, flipping the big red bu...
By Batpred , 3 days ago
-
Well I usually do it by feel, which is a slight problem...
By Transparent , 3 days ago
-
@jeff I am well aware of the riskiness of such investme...
By Toodles , 3 days ago
-
Fully understood and entirely reasonable! On the home ...
By JamesPa , 4 days ago
-
RE: Electricity price predictions
So I am really having difficulty trying to work out wha...
By bontwoody , 4 days ago
-
Ok Well almost certainly it could be used instead of ...
By JamesPa , 4 days ago
-
RE: Samsung heat pump - data cable issue
Samsung reference it as "RS485 - COMM" in my manual. ...
By Old_Scientist , 4 days ago
-
RE: SolarEdge SE5000H Inverter Failure
Update. My SolarEdge inverter was replaced yesterday wi...
By L8Again , 4 days ago