Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Simulation of ASHP with Gas boiler as part of decision process
Hello, new to the forum, thanks for having me.
I would like to transition to an ASHP, but it seems to be fraught with complications, so my brain tells me to experiment before making a decision; get more real data.
My approach is then, to simulate an ASHP with my current gas system boiler over the coming heating season. My question to the forum is if anyone did this before and any tips or tricks to make it as accurate as possible?
My approach so far;
1.Got a FOC heat loss survey.
2. Set my system boiler flow temperature to 50degC and reduced it's power output from 18kW to 8kW in line with total heat loss estimate @ -3C.
3. Downstairs TRVs all set to maximum (6). Upstairs set to 3 on a scale of 6, except bathroom set to max (6).
4. Home most days, set system to heat 6AM - 11PM, main thermostat target 23C (yes that's how the Mrs must have it!). Hot water 5AM - 6AM daily - will manually run weekly legionella heat to 60C on a Sunday.
Anything else I can do?
Known possible issues for accuracy of experiment:
Boiler modulation down to 5kW only - likely to cause cycling
Kitchen has new hydronic baseboard heater, heating system not balanced yet
Unsure about physical location of a future ASHP and pipe runs, how impacting might that be.
No weather compensation.
Thanks!
I did pretty much the same. The overall conclusion for me is that low and slow makes for a more comfortable living environment and it confirmed that my loss calculations based on actual consumption give a figure which keeps me warm.
Because my boiler isn't weather compensated I had to manually adjust the ft during the season which means that the trvs were still kicking in, but I don't think that materially affected the experiment.
Cycling is inevitable if your boiler can't modulate down to match your house demand.
In summary I felt it was a useful experiment that will remain in place until I can get an ashp because it results in a greater level of comfort.
I can't really offer any tips beyond what you have done, like me the missing feature is weather compensation but my feeling is that this will further improve comfort.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa thanks for the reply, we tried this last year and we couldn't keep the living room to the tropical temperature required, which actually led me to investigate more and found some missing insulation, so whatever happens it's helped us.
Posted by: @scalextrix@jamespa thanks for the reply, we tried this last year and we couldn't keep the living room to the tropical temperature required, which actually led me to investigate more and found some missing insulation, so whatever happens it's helped us.
Better insulation is best but of course bigger radiators may also be necessary to get tropical room temperature with low flow temperature. That's part of the design process (t's not much use having an ashp that can kick out 12kW if your rads can only do 8kW at your chosen flow temp). In a living room consider fancoils, large output, small footprint, can also be used for mild cooling. Costly for anything well styled (they appear to be most common in Italy, so quite a few are) and of course there is a background hum from the fan, but a useful addition to the low temperature heating retrofit toolbox
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
We tried the retrofit fans that stick with magnets to the rads a few years ago just for fun. While they were silent before putting on the rad, once they were in place the radiator made an irritating buzz/rattle that wasn't acceptable for a living room. Other people may have different experiences.
We have 2 rads in there, one is a type 22 and can be made a bit wider, the other is a type 21, while it can't be any bigger, we can upgrade to a type 22. I'm hoping with the improved insulation that should be enough to get what we need.
Posted by: @scalextrixWe have 2 rads in there, one is a type 22 and can be made a bit wider, the other is a type 21, while it can't be any bigger, we can upgrade to a type 22.
I have a small old leaky listed building with limited wall space. As a very general rule of thumb, if you have correctly sized radiators for a fossil fuel system running at high flow temps, then for an ASHP system running at the upper end of acceptable flow temps, then you will need new rads that have twice the effective area of the fossil fuel rads. This is quite a big jump, something not always appreciated in the early planning stages. Doubling the area of the rad is one option, but so too are different form factors. I ended up with all K3 rads bar two, and some of the K3s needed to be quite a bit larger than the K2s they replaced. Instead of rads that were relatively discrete, I now have rads that no doubt an estate agent would describe as 'a feature'...
1330: Edited to change 'twice the output of the fossil fuel rads' to 'twice the effective area of the fossil fuel rads' as in my experience this is an area in which it is easy to get very confused very quickly... The key point to understand is that the heat transfer to the room depends on the 'delta t' (temperature difference) between the mean radiator temp and the room temp. Halve the mean rad temp, and keep everything else constant, then the heat transfer will be give or take half what it was at the higher temp. To compensate (get the same amount of heat transferred), you have to double the effective size (area) of the radiator.
Midea 14kW (for now...) ASHP heating both building and DHW
Posted by: @cathoderayI ended up with all K3 rads bar two, and some of the K3s needed to be quite a bit larger than the K2s they replaced. Instead of rads that were relatively discrete, I now have rads that no doubt an estate agent would describe as 'a feature'...
This is an area where the industry tendency to oversize can cause a real problem. I decided to start rad upgrades in advance so far for half of the house only) and based the sizing initially on the MCS assumptions. This gave me one K3 in the master bedroom which my wife hates. Subsequently I have concluded that the MCS assumptions lead to an over estimate of the loss and, had I known this earlier, I could have got away with a much more acceptable K2.
Sizing doesn't just affect the odu, it affects the whole system, so it's important imho to get it as accurate as possible if wrong sizing is likely to drive difficult to reconcile design decisions
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@cathoderay 🤩 Toodles
Toodles, heats his home with cold draughts and cooks food with magnets.
Posted by: @jamespaSizing doesn't just affect the odu, it affects the whole system, so it's important imho to get it as accurate as possible if wrong sizing is likely to drive difficult to reconcile design decisions
I strongly endorse this. Some of the quotes I had from various goons claiming to be heating engineers had hopelessly out of whack rad specs. For radiator sizing, the steps are:
1. Accurate heat loss calcs for each room
2. Select a radiator that will (a) fit in the available space (a sina qua non) and (b) has the right heat output at AHSP flow temps for that room
Follow that procedure, and you won't go far wrong.
Midea 14kW (for now...) ASHP heating both building and DHW
I took this ‘simulation approach’ last year. Based on my own heat loss calculations (including a very wet finger in the air for air change), I suspect that I will need to change many of the radiators. One of my concerns (largely due to it being big concern of my wife) is that the 10mm radiator pipe work downstairs comes out of the wall so the pitch of the valve connections and their distance from the wall are fixed. Replacement radiators will likely need a couple of additional pipe fittings at each end - not an aesthetic solution and additional resistance to the flow.
Posted by: @ianmk1310mm radiator pipe work
10mm pipe is ok for about 1kW at dT5. So really depends how the system is laid out and how you transition to 10mm and the other piping sizes. Lots of consideration other than just replacing pipe tails
-
New Vaillant Arotherm Plus 7kW (cooling enabled) + Jaga Briza cooling + Sunamp Thermino – costs, experiences & Sunamp choice (EnerPHit-level retrofit)
1 week ago
-
Surface mount or bury primaries for heat pump installation?
3 weeks ago
-
Design Of Cascade System Replacing Undersized ASHP
3 weeks ago
-
High air source heat pump running costs – Vaillant AroTherm Plus
3 months ago
-
Bosch CS5800i 7kW replacing Greenstar Junior 28i
4 months ago
Currently viewing this topic 3 guests.
- 26 Forums
- 2,725 Topics
- 63.8 K Posts
- 970 Online
- 7,126 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Jokes and fun posts about heat pumps and renewables
@transparent I’ve heard that that is why American cars ...
By Toodles , 4 hours ago
-
RE: HeatGeek vs Octopus surveys: puzzling disparity - any ideas why?
Have either quote provided room by room heat loss calcu...
By Old_Scientist , 18 hours ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@old_scientist if you are going DIY then you may wan...
By Papahuhu , 2 days ago
-
RE: Indevolt Batteries UK Support & Info Thread
After a short while that was followed by the 'power war...
By JamesPa , 2 days ago
-
RE: Samsung heat pump - data cable issue
That's well done. Cable is the correct type (LIYCY = 2x...
By bobflux , 2 days ago
-
RE: Electricity price predictions
I agree, we will find out at the next budget whether th...
By Old_Scientist , 3 days ago
-
RE: Missing flow temperature in Heat Geek proposal
@editor I went through HG website, so should be ok for ...
By sttpd1917 , 3 days ago
-
Who did the Freedom Heat Pump cloud server and what did...
By Mars , 3 days ago
-
RE: Who's your electricity provider and what's your tariff?
Reading between the lines of what octopus are doing wit...
By JamesPa , 3 days ago
-
RE: Air to air bus grant installer anywhere
The through wall two hole ones have their place (listed...
By EtchedPixels , 3 days ago
-
I hope it goes ok, Hon can be hard to set up IF the sof...
By Graham Hendra , 3 days ago
-
@clockworks Hi, So there is a big difference between st...
By ASHP-BOBBA , 3 days ago
-
@editor wellvery comprehensive answer. I will get all i...
By Keithb , 3 days ago
-
RE: Advice on my Heat Pump Journey: Old Stone Built Detached Cottage
all good advice I will follow this up
By PaulC , 3 days ago
-
Heat of vaporization of water is 2.25 MJ/kg (0.625 kWh/...
By bobflux , 4 days ago