Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Posted by: @ashp-bobba@netdonkey Primary pump should run as follows:
Heating demand on
DHW demand on
Defrost demand on
Secondary pump should run as follows:
Heating demand on
Defrost demand on (only of the volume of the buffer is not enough for the min volume for the ASHP to defrost)
Primary pump runs as described above. Secondary pump is constantly on until DHW is activated
@netdonkey so you may find the pump is wired through the 3 port switch so when sitting in heating mode but the demand is off the pump runs all the time but when switched to DHW it switches off as the movement of the 3 port would break the 3 port switch, if so this would be the wrong way to wire, your wire centre with the ASHP should have electrical connections for the primary and secondary pump set, you should also be able to dip switch or programme the ASHP so it knows if you are using a buffer or just 3 port valve, this way the ASHP will know if to just run one or 2 pumps and when. Not all ASHP are exactly the same and I don't know all of them but most are very simular.
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Posted by: @ashp-bobba@netdonkey so you may find the pump is wired through the 3 port switch so when sitting in heating mode but the demand is off the pump runs all the time but when switched to DHW it switches off as the movement of the 3 port would break the 3 port switch, if so this would be the wrong way to wire, your wire centre with the ASHP should have electrical connections for the primary and secondary pump set, you should also be able to dip switch or programme the ASHP so it knows if you are using a buffer or just 3 port valve, this way the ASHP will know if to just run one or 2 pumps and when. Not all ASHP are exactly the same and I don't know all of them but most are very simular.
Just heard back from Samsung and there is a software upgrade that will fix this logic so the secondary pump isnt always running.
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Posted by: @netdonkeythere is a software upgrade that will fix this logic so the secondary pump isnt always running
Is that upgrade applied automatically over-the-air to all Samsung units?
Or does it require the householder or installer to do something?
Save energy... recycle electrons!
Sheesh! Ash him/her how many sites they have to visit to implement the firmware change.
... and why they couldn't devise a system to do this remotely.
Yes, it might need the homeowner to authorise the upgrade within the App,
and it might need to be undertaken within a time-window in order to prevent hackers attempting such a route in future.
But we already have such functionality on the UK Smart Meter system, and that was designed a decade ago.
Save energy... recycle electrons!
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Posted by: @netdonkey@transparent Samsung service rep coming out on 3/1
Did you have to pay for the visit?
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
@netdonkey could this be a first for Samsung? 😂 They do have a habit of charging for visits. I’m curious to see whether it’s an actual Samsung engineer or one of their many agents handling the call-out.
But fully agree in you maximising the visit and getting as much as info as you can out them. Looking forward to the update.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
-
First time wall mounting an ASHP
7 months ago
-
How can I programme a setback for my Samsung Gen6 8kW heat pump?
8 months ago
-
Samsung problems
9 months ago
-
Sudden drop in COP
10 months ago
-
Samsung's Cold Shoulder: Should Heat Pump Manufacturers Be More Accountable?
2 years ago
- 26 Forums
- 2,675 Topics
- 62.6 K Posts
- 242 Online
- 7,090 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
@majordennisbloodnok @jamespa I stand corrected, A2A...
By Batpred , 17 minutes ago
-
RE: Help me keep the faith with my air source heat pump installation
I didn't know about those, they look like good pieces o...
By JamesPa , 2 hours ago
-
@mkz, that's very helpful. Even if Urban Plumber are no...
By Majordennisbloodnok , 3 hours ago
-
RE: Several AC coupled batteries
That is a good point, a manufacturers can stop trading,...
By Batpred , 3 hours ago
-
My first question is why bother with the auto balancin...
By JamesPa , 4 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
Hi @hanno - good question. The range of hybrid invert...
By Transparent , 4 hours ago
-
RE: GivEnergy inverter tripping due to over-voltage?
@transparent the inverter was installed in 2021 and afa...
By Tim441 , 4 hours ago
-
I share the same experience as @majordennisbloodnok hav...
By Old_Scientist , 5 hours ago
-
RE: Say hello and introduce yourself
I hope so, @toodles. It's not often that we see a situa...
By Majordennisbloodnok , 8 hours ago
-
RE: Heat pump design review please: 5 kW Vaillant aroTHERM Plus heat pump
@jamespa many thanks, definitely i will give the pre...
By ragtime27 , 19 hours ago
-
RE: Heat pump installation quotations
@jamespa I noticed that in the Heat Geek design consult...
By Batpred , 21 hours ago
-
RE: Electricity price predictions
Good point, I do expect the bonus of putting my energy ...
By Batpred , 1 day ago
-
RE: Daikin ESPAltherma and Home Assistant installation
@bash, something we haven't touched on already relates ...
By Majordennisbloodnok , 1 day ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Vaillant arotherm plus 12kW. Installed March 2025. Ex...
By Harebell , 2 days ago