Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
[Solved] Sudden drop in COP
I've had a sudden drop in COP, from around 3.8-4.4 a few weeks ago, to 2.4-3.0 recently. Any thoughts as to why?
I have a Samsung 8kw ASHP that for the last month or two I've only been using for DHW. I don't have any advanced monitoring, just the energy use and generation output by the unit itself. Over the last week the COP has been way down and I'm not sure why.
I heat up the DHW once a day between 2pm and 3:30pm, 200L water tank with 3m square heating coil. The unit switches into quiet mode when DWH is active. It's not a heavy use set up, one shower a day and maybe some washing up.
I don't have the heating on this time of year and don't want to turn it on to see what that is running at.
Samsung Gen6 8kw ASHP in a two bed victorian mid terrace.
My guess would be that the unit is measuring combined COP for heating and hot water. Therefore because now you are only heating water at a lower COP than heating your average drops.
House-2 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
I don't have any advanced monitoring, just the energy use and generation output by the unit itself.
How do the energy use and generation output differ between the good COP and bad COP weeks? Is it that the energy used has increased or the energy generated has decreased to give you the lower COP?
My Samsung Gen6 8kw had a bit of brain fade earlier in the year when the recorded energy generation figures became ridiculously high - 1,398kWh for one week in February. The energy consumption was recorded as a (more believable) 90kWh, so a fantastic COP of over 15 🤗 . I knew something was really wrong when I saw that the recorded weekly operation time for that week was 524 hours - around 75hrs a day. Samsung Technical Support talked me through a reset of the Wired Remote Controller and that appeared to sort the issue.
@bontwoody The thing is I have been using it for only DHW for a month or two, i was getting higher cop just on the hot water, so it can’t be that I’ve turned off the heating.
Samsung Gen6 8kw ASHP in a two bed victorian mid terrace.
@sjn Okay so it was a software issue. It appears my energy use is going up, but my energy generation is staying about the same according to the numbers.
Samsung Gen6 8kw ASHP in a two bed victorian mid terrace.
@ecobaker Yes, it must have been a software bug disrupting my historic energy numbers. I haven't looked at them recently so I should check to see if they are still ok.
Your generation staying about the same makes sense for a consistent use of DHW so it is the increased usage that is unexpected.
One thing I have noticed is that there is some rounding going on with the displayed energy numbers - the sum of the energy figures for each day does not add up to the displayed total for the week. I wonder if with DHW only the usage and generation will be quite low so the rounding errors may have a bigger significance to your COP calculations, possibly amplifying any week to week changes due to different outside air temperature 🤔 .
@sjn I've seen this on other brands as well. Rounding for small consumption (for instance only hot water) really messes up the accuracy.
Another thing we've seen is that some manufacturers just add on a flat energy use per hour (during periods when the heat pump is not running). Maybe Samsung did a software update recently and started doing this as well?
CEO and co-founder at HavenWise
@hcas Thing is I've not updated the software, that's actually quite hard to do with Samsung as its not directly connected to the internet.
Samsung Gen6 8kw ASHP in a two bed victorian mid terrace.
SOLVED
So it turns out the problem is, I am a massive Idiot.
A few weeks ago, I had used most of my hot water, and needed a quick shower as I was in a rush and had to go out. So I put on forced mode for DWH and turned on the immersion heater, which I normally have turned off, to turn on after 15 mins. When I had enough hot water I turned off forced mode but forget to turn off the immersion in the field settings.
So my sudden drop in COP has been down to my immersion firing up and helping heat my hot water for the last few weeks 😭
Turned it off and I got 4.1 cop for DHW today
Samsung Gen6 8kw ASHP in a two bed victorian mid terrace.
@ecobaker May I ask a question of you please. I too have a recent install of a gen 6, one of the 16kw units. As it’s warm, only been running DHW cycles and trying to get my head round how it can be tweaked to run optimally.
With my legionella cycle off, and a hot water set point of 45C I’m getting a COP around 3.6. But it’s not behaving as I’d expect, mine seems to ramp up the circulation pump inverter to 100% and ramps up the heat pump power input to about 6kW and then ramp it down again, it finishes the cycle in less than 20mins (a 250L tanks) and uses approx 1.5 kWh. I was expecting it to behave less bruitishly, tickling up the flow temp slowly to get better efficiency.
Does yours go flat out too please?
thanks
-
First time wall mounting an ASHP
4 months ago
-
How can I programme a setback for my Samsung Gen6 8kW heat pump?
5 months ago
-
Samsung problems
6 months ago
-
Nibe F2040 periodic warm water increase fails
10 months ago
-
Samsung E911 intermittent issue
1 year ago
- 27 Forums
- 2,541 Topics
- 59.2 K Posts
- 1,426 Online
- 6,822 Members
Join Us!
Worth Watching
Latest Posts
-
The UFH system was installed at the same time as the GS...
By phowardstutterheim , 31 minutes ago
-
RE: Heat pump Surge protection
@transparent Many thanks for the advice and I will cert...
By DavidAlgarve , 45 minutes ago
-
RE: Aerotherm 12+12kw cascade huge power utilisation
@editor This is really crazy. I can sort of understan...
By JamesPa , 7 hours ago
-
Or just add any further discussion to the other thread....
By cathodeRay , 8 hours ago
-
RE: NIBE Heat Pump Warranty: What's an Adequate Engineer Attendance Time?
@hughmark, great to hear. Fingers crossed that it’s sor...
By Mars , 19 hours ago
-
RE: Daikin high temperature heat pump
I’ll check in with Daikin to see if they can help answe...
By Mars , 19 hours ago
-
RE: Samsung Gen 7 16kW Integrated unit Modbus monitoring
@johnnyb HI,I have an integrated unit with all componen...
By antonical , 21 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@papahuhu Ironical isn’t it? The last few days, the ‘Ag...
By Toodles , 22 hours ago
-
RE: Setback savings - fact or fiction?
I answered that days back, I even provided a summary of...
By RobS , 23 hours ago
-
RE: If a heat pump can only heat DHW to 50C then what? Issue with 18KW Heliotherm heat pump
I must say that this install is sounding more and more ...
By Mars , 1 day ago
-
RE: Who's your electricity provider and what's your tariff?
@chandykris Thanks, that’s a fair point and I agree th...
By Eliuccio , 2 days ago
-
-
RE: The law of unintended consequences....
Oh Thank you Major, I was just beginning to wonder wher...
By Toodles , 3 days ago
-
RE: Forum updates, announcements & issues
I know that the notifications are being delivered now w...
By Mars , 3 days ago
-
RE: Advice needed after a successful "leftfield" experiment.....
@pauli I have sent a direct message with the financial ...
By ChandyKris , 3 days ago
-
RE: Octopus Cosy 12 Heat Pump Regret: Incredibly Loud, Poor Heating & Constant Hum - Help!
Does it disappear when the heat pump is off? What abou...
By JamesPa , 3 days ago
-
RE: Fitting heat pump plumbing and pipes in advance?
Great tips, thanks. The PEX/Al/PEX option sounds much m...
By Jonatan , 3 days ago
-
RE: Struggling to get CoP above 3 with 6 kw Ecodan ASHP
Those control valves on the UFH manifold could be an is...
By Travellingwave , 3 days ago
-
RE: Daikin Altherma 3 LT compressor longevity question
Up to a point yes. However every heat pump (and every ...
By JamesPa , 4 days ago
-
RE: New Build ASHP Defects - Looking for Advice, Support & Shared Experiences
Is that a single pair only? If so it may be part if th...
By JamesPa , 4 days ago
-
@batpred, you’re quite right; it does work well. I don’...
By Majordennisbloodnok , 4 days ago
-
RE: Ecodan Cylinder Possible Weeping Around Thermostat Port
Update: Mitsubishi sent an engineer around. It was li...
By Gruff2001 , 4 days ago
-
RE: A Smarter Smart Controller from Homely?
@benson Agreed. I believe the COP gains with homely, i...
By Papahuhu , 4 days ago
-
How to Find All Your Posts and Topics on the Forum – A Quick Guide
If you’ve ever posted something on the forum and then s...
By Mars , 4 days ago