Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
[Solved] Sudden drop in COP
I've had a sudden drop in COP, from around 3.8-4.4 a few weeks ago, to 2.4-3.0 recently. Any thoughts as to why?
I have a Samsung 8kw ASHP that for the last month or two I've only been using for DHW. I don't have any advanced monitoring, just the energy use and generation output by the unit itself. Over the last week the COP has been way down and I'm not sure why.
I heat up the DHW once a day between 2pm and 3:30pm, 200L water tank with 3m square heating coil. The unit switches into quiet mode when DWH is active. It's not a heavy use set up, one shower a day and maybe some washing up.
I don't have the heating on this time of year and don't want to turn it on to see what that is running at.
Samsung Gen6 8kw ASHP in a two bed victorian mid terrace.
My guess would be that the unit is measuring combined COP for heating and hot water. Therefore because now you are only heating water at a lower COP than heating your average drops.
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
I don't have any advanced monitoring, just the energy use and generation output by the unit itself.
How do the energy use and generation output differ between the good COP and bad COP weeks? Is it that the energy used has increased or the energy generated has decreased to give you the lower COP?
My Samsung Gen6 8kw had a bit of brain fade earlier in the year when the recorded energy generation figures became ridiculously high - 1,398kWh for one week in February. The energy consumption was recorded as a (more believable) 90kWh, so a fantastic COP of over 15 🤗 . I knew something was really wrong when I saw that the recorded weekly operation time for that week was 524 hours - around 75hrs a day. Samsung Technical Support talked me through a reset of the Wired Remote Controller and that appeared to sort the issue.
@bontwoody The thing is I have been using it for only DHW for a month or two, i was getting higher cop just on the hot water, so it can’t be that I’ve turned off the heating.
Samsung Gen6 8kw ASHP in a two bed victorian mid terrace.
@sjn Okay so it was a software issue. It appears my energy use is going up, but my energy generation is staying about the same according to the numbers.
Samsung Gen6 8kw ASHP in a two bed victorian mid terrace.
@ecobaker Yes, it must have been a software bug disrupting my historic energy numbers. I haven't looked at them recently so I should check to see if they are still ok.
Your generation staying about the same makes sense for a consistent use of DHW so it is the increased usage that is unexpected.
One thing I have noticed is that there is some rounding going on with the displayed energy numbers - the sum of the energy figures for each day does not add up to the displayed total for the week. I wonder if with DHW only the usage and generation will be quite low so the rounding errors may have a bigger significance to your COP calculations, possibly amplifying any week to week changes due to different outside air temperature 🤔 .
@sjn I've seen this on other brands as well. Rounding for small consumption (for instance only hot water) really messes up the accuracy.
Another thing we've seen is that some manufacturers just add on a flat energy use per hour (during periods when the heat pump is not running). Maybe Samsung did a software update recently and started doing this as well?
CEO and co-founder at HavenWise
@hcas Thing is I've not updated the software, that's actually quite hard to do with Samsung as its not directly connected to the internet.
Samsung Gen6 8kw ASHP in a two bed victorian mid terrace.
SOLVED
So it turns out the problem is, I am a massive Idiot.
A few weeks ago, I had used most of my hot water, and needed a quick shower as I was in a rush and had to go out. So I put on forced mode for DWH and turned on the immersion heater, which I normally have turned off, to turn on after 15 mins. When I had enough hot water I turned off forced mode but forget to turn off the immersion in the field settings.
So my sudden drop in COP has been down to my immersion firing up and helping heat my hot water for the last few weeks 😭
Turned it off and I got 4.1 cop for DHW today
Samsung Gen6 8kw ASHP in a two bed victorian mid terrace.
@ecobaker May I ask a question of you please. I too have a recent install of a gen 6, one of the 16kw units. As it’s warm, only been running DHW cycles and trying to get my head round how it can be tweaked to run optimally.
With my legionella cycle off, and a hot water set point of 45C I’m getting a COP around 3.6. But it’s not behaving as I’d expect, mine seems to ramp up the circulation pump inverter to 100% and ramps up the heat pump power input to about 6kW and then ramp it down again, it finishes the cycle in less than 20mins (a 250L tanks) and uses approx 1.5 kWh. I was expecting it to behave less bruitishly, tickling up the flow temp slowly to get better efficiency.
Does yours go flat out too please?
thanks
-
First time wall mounting an ASHP
6 months ago
-
How can I programme a setback for my Samsung Gen6 8kW heat pump?
6 months ago
-
Samsung problems
8 months ago
-
Nibe F2040 periodic warm water increase fails
12 months ago
-
Samsung E911 intermittent issue
1 year ago
- 26 Forums
- 2,618 Topics
- 61.1 K Posts
- 648 Online
- 6,994 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Renewables & Heat Pumps in the News
An article on funding for heat pumps in case anyone is ...
By Jeff , 33 minutes ago
-
RE: Indevolt Batteries UK Support & Info Thread
Thanks @editor , @indevolt-uk Subject to any comments ...
By JamesPa , 8 hours ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
@seoras Sorry to hear that. I found Vaillant very help...
By JamesPa , 9 hours ago
-
The Watchdog That Watched and Waited
On 9 January 2026, Consumer Energy Solutions collapsed ...
By Mars , 12 hours ago
-
RE: GSHP Kaput After 16 Years: New Compressor or Switch to ASHP? Advice Welcome
Cool Energy in Grimsby sell ground source heat pumps an...
By DerekDeLeon , 13 hours ago
-
RE: Valliant Heat Pump Settings
Thats arguably a sign of a good installer - they unders...
By JamesPa , 14 hours ago
-
RE: Electricity price predictions
Well, we have so many cases where rain water mixes with...
By Batpred , 15 hours ago
-
RE: Two heating zones to one zone
@profzarkov They arent obviously wrong, but the only...
By JamesPa , 17 hours ago
-
RE: Towns water feed to air source heat pump system
The DHW circuit cant be separated (well it could, you c...
By JamesPa , 17 hours ago
-
Solis AC-coupled 3kW storage inverter
Solis AC-coupled 3kW storage inverterPylontech batterie...
By MartinRobinson , 23 hours ago
-
RE: My NIBE ASHP Nightmare: No Commissioning, High Bills and a Hostile Installer
As @transparent has observed above, this is not bad, an...
By cathodeRay , 1 day ago
-
RE: The Grid Says Yes.. Until It Doesn’t: Why Britain's Net Zero Push is Stalling at the Plug Socket
As I was reading this article Mars, I was thinking that...
By Toodles , 2 days ago
-
RE: Tell us about your Solar (PV) setup
Installed in May 2011: 16*Sharp 245 W monocrystalline p...
By txmartyn , 2 days ago
-
-
RE: Say hello and introduce yourself
That doesn't sound 'right' to me. The national Smart ...
By Transparent , 3 days ago
-
RE: Growatt battery disconnected
I doubt this will happen, but I will try and suggest it...
By Eliuccio , 3 days ago
-
Understood. That's why I decided from the outset on a ...
By JamesPa , 3 days ago
-
RE: My experience with 3 heat pump surveys: Heat Geek, British Gas & Octopus
On the litigation, I would not go there and definitely ...
By Batpred , 3 days ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
I suppose if your pv inverter packs up, you have a plan...
By Batpred , 4 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Firstly check you are using sound power not sound press...
By JamesPa , 4 days ago
-
That’s the solar up and running, I don’t think it’s the...
By David999 , 4 days ago
-
RE: Seeking ideas / information / commiseration - Pure Drive
I agree with @colinc that you can reuse some of it. A s...
By Batpred , 4 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@toodles Im trying me best to ignore orangeman, I figur...
By Papahuhu , 5 days ago