Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Samsung E911 intermittent issue
Posted by: @netdonkey@editor it’s one of their agents. They did say the name of the company but can’t remember it!
just remembered the name! https://atlasservicessolutions.co.uk/
Just a quick update. It looks like it may be the actual Samsung is broken. Whether it's been caused by the 16 litres of glycol the installer put in for our 12 radiator system or not is still to be seen. Waiting for Samsung to open tomorrow to get them to come out
Just an update to let everyone know that we are now all back up and running after 2 weeks of no heat in the coldest January in a while.
We finally had the installed agree to drain the system and flush everything through. When he was disconnecting the ASHP from the outside flow and return he removed some lagging beside the shut off valves and spotted something he hadn't noticed before. The shut off valves also had filters in them
Opened them up and they were caked. Cleaned them out and did another flush for good measure and we are back with heating!
Thanks for everyones input into this!!
-
First time wall mounting an ASHP
7 months ago
-
How can I programme a setback for my Samsung Gen6 8kW heat pump?
7 months ago
-
Samsung problems
9 months ago
-
Sudden drop in COP
10 months ago
-
Samsung's Cold Shoulder: Should Heat Pump Manufacturers Be More Accountable?
2 years ago
- 26 Forums
- 2,643 Topics
- 61.7 K Posts
- 308 Online
- 7,043 Members
Join Us!
Latest Posts
-
Mentally you have to separate the ac side and the DC si...
By JamesPa , 10 hours ago
-
RE: Help me keep the faith with my air source heat pump installation
My heating developed a really severe case of noise and ...
By JamesPa , 13 hours ago
-
RE: Octopus Cosy 12 Heat Pump Regret: Incredibly Loud, Poor Heating & Constant Hum - Help!
@l2jad I was just thinking all things being equal. Our ...
By AndrewJ , 19 hours ago
-
RE: Heat Pump Manufacturers Recommending Buffer Tanks
Hopefully the ambient temperature sensor drives a weath...
By JamesPa , 1 day ago
-
RE: How many people are happy with their ASHP and do you believe them?
Im looking into these and my figures. The think that I...
By JamesPa , 1 day ago
-
Hi, Does anybody have experience with Heat Geek insta...
By sttpd1917 , 1 day ago
-
RE: Heat Pump Operation in Summer - Valliant 7kW
Yes - we use our Mitsi 14kW unit for cooling. I have j...
By downfield , 2 days ago
-
I will soon be struggling. Admittedly it is the summer,...
By Batpred , 2 days ago
-
RE: Indevolt Batteries UK Support & Info Thread
Not known yet. I've asked a local Councillor to follo...
By Transparent , 2 days ago
-
Hard to tell but I think I have placed the arrow on wha...
By ASHP-BOBBA , 3 days ago
-
RE: Who do I complain to about a poor ECO4 installation, can anyone advise?
Great. My guess is that you will need to re-adjust yo...
By JamesPa , 3 days ago
-
RE: UK warm homes plan - how can it be delivered?
I know it is not as simple as going from a fossil fuel ...
By Batpred , 3 days ago
-
@editor this is great news.
By ASHP-BOBBA , 4 days ago
-
RE: Daikin Altherma 3 with Fan Coils in Puglia (Italy)… Sanity Check on System Operation
AH (Absolute humidity) is grams of moisture per volume ...
By bobflux , 4 days ago