Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Samsung E911 intermittent issue
Posted by: @netdonkey@editor it’s one of their agents. They did say the name of the company but can’t remember it!
just remembered the name! https://atlasservicessolutions.co.uk/
Just a quick update. It looks like it may be the actual Samsung is broken. Whether it's been caused by the 16 litres of glycol the installer put in for our 12 radiator system or not is still to be seen. Waiting for Samsung to open tomorrow to get them to come out
Just an update to let everyone know that we are now all back up and running after 2 weeks of no heat in the coldest January in a while.
We finally had the installed agree to drain the system and flush everything through. When he was disconnecting the ASHP from the outside flow and return he removed some lagging beside the shut off valves and spotted something he hadn't noticed before. The shut off valves also had filters in them
Opened them up and they were caked. Cleaned them out and did another flush for good measure and we are back with heating!
Thanks for everyones input into this!!
-
Issue with Samsung Cascade System
2 months ago
-
First time wall mounting an ASHP
11 months ago
-
How can I programme a setback for my Samsung Gen6 8kW heat pump?
12 months ago
-
Samsung problems
1 year ago
-
Sudden drop in COP
1 year ago
Currently viewing this topic 3 guests.
- 27 Forums
- 2,792 Topics
- 66 K Posts
- 3,203 Online
- 7,197 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Heat pump branding. Clever, contemporary… or a bit too much?
I think Heat Geek have done an amazing job on their bra...
By Tomtheheatingengineer , 7 hours ago
-
RE: HeatGeek vs Octopus surveys: puzzling disparity - any ideas why?
I have just had 3 heat loss surveys, one by heat geek o...
By David , 7 hours ago
-
RE: Heat Geek Zero Disrupt: Are We Sleepwalking Into Another Race to the Bottom?
I think that's the key question. After all inverter uni...
By Prunus , 9 hours ago
-
RE: battery storage without solar
As of October 1st they need specific qualifications to ...
By EtchedPixels , 10 hours ago
-
RE: How should the Boiler Upgrade Scheme be reformed?
A unit which uses water to transfer the heat/chill from...
By Temperature_Gradient , 10 hours ago
-
RE: Renewables & Heat Pumps in the News
With regards to the BUS grant raid, I gave it more thou...
By ASHP-BOBBA , 10 hours ago
-
RE: Why are ASHP installs so expensive?
The whole system seems to work on the basis of...
By ian33a , 11 hours ago
-
RE: Missing flow temperature in Heat Geek proposal
Good plan. If you can get half hourly meter readings a...
By JamesPa , 16 hours ago
-
RE: Heat Pumps Without Grants: Would You Have Installed One & Will You Now?
@editor Most certainly. The heat pump was an ideal s...
By Abernyte , 16 hours ago
-
Although regulations may well vary from country to coun...
By Majordennisbloodnok , 17 hours ago
-
RE: Does anyone have experience of a smart water meter?
Yep I caught our slow leak from a £100 bill rise 8)
By EtchedPixels , 17 hours ago
-
RE: Do You Need a Buffer Tank or Low Loss Header for Underfloor Heating in a Large Property?
@jamespa in some cases, failing the Turing test might b...
By GrahamF , 20 hours ago
-
RE: Passiv Smart Thermostat - Help & Forum Support
@energystoragetech The heat capacity of some...
By JamesPa , 22 hours ago
-
RE: tepeo ZEB UK Support & Info Thread
Sorry you are correct, I was remembering figures from t...
By JamesPa , 1 day ago