Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Samsung E911 intermittent issue
Hi all,
Been having a trawl through the forums for the E911 and have a few other queries.
I have a AE080CXYDEK which was installed back in June and has been working well. Recently, however, we have had a couple of E911 errors which has led me to dig into our install a bit more.
Using our MIM i can see the flow is around 7.2-7.4lpm which is almost at the HP's minimum in which the E911 error starts. I have queried our installer (electrician who installed the solar and battery and subsequently subbed the ASHP install out) and it's taking a while to get anywhere. So my queries are as follows:
We have a Evosta 3 set to fixed curve regulation mode level3. Is this correct?
It looks like the Evosta has been installed upside down but I assume it was done this way due to the flow direct?
I can stop it from erroring by only running the heating and within 15 mins of powering on the DHW it trips (subsequently in the last 12hrs I have had both running and it hasn't tripped). Does this narrow down what the issue could be?
In another thread, Mars mentioned checking the Y strainer. Is this easy to do as a novice or should I be pushing to get the plumber to come out and check. If it's easy where is it usually located and what does it look like?
How happy are other plumbers to come out and diagnose a system they havent put it and is it worth doing this?
Thanks!
@netdonkey The model number for your Samsung indicates it is an 8kW system? The flow rates you are indicating only provide around 2.5kW and the code E911 is related to lack of flow, airlocks, restrictions on flow or other flow sensor issues.
Samsung send an inline strainer with their systems, if this was fitted it will collect debris from the system and block (this is its job) this will need checking 1st, also its worth confirming the length of the primary pipework from the condenser to the plant room (from the condenser to the manifold or plant room, buffer or 1st secondary distribution pipework valves). It worth making sure this pipework is the correct size for the flow rate and distance it serving. 8Kw will need a minimum of 28mm on a short run.
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
@ashp-bobba Thanks. The pipework run from the ASHP to main plant is around 13m. Would the strainer be near the pump or the main plant? I assume the strain would be on the return to protect the pump?
@netdonkey The strainer can be anywhere on the rerun line from the airing cupboard / plant room to the ASHP condenser, so this could be in that room or at the condenser, they look like a Y shape: linked here for you to see.
Please clarify 2 things if you can?
13m from the condenser to the plant room as the main ASHP pipes
What size is the pipework from the condenser (most manufacturers need you to limit the run to a max 10M or calculate an upsize in pipework and pump to cope with the length of run).
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
Posted by: @netdonkeyWould the strainer be near the pump or the main plant?
On our system, originally, it was inside the heat pump unit (we don’t have a Samsung). It was a bloody stupid location because we had to remove heat pump side panels to access it, so we had the installers move it into our plant room. See photo.
I asked installers specifically about Y strainers on a recent podcast and they should be fitted on every installation, so you should have one somewhere.
🔥 Britain’s Heat Pump Shitshow
How Installing a Heating System Became a National Nervous Breakdown
Free UK shipping.
📗 Heat Pumps Explained
A Jargon-Free Guide for Homeowners
Rewritten and updated for 2027
📘 From Zero to Heat Pump Hero
🛠️ Bodge Buster
New to heat pumps?
Take the Heat Pump Fundamentals course and use INTRO50 at checkout for 50% off.
@netdonkey Should be shut of valves either side. the nut can be a bit tight on some of them, be sure to support the pipe when you try.
AAC Group Ltd covering the Kent Area for design, supply and installation of ASHP systems, service and maintenance, diagnostics and repairs.
@netdonkey do exactly what @ashp-bobba says above.
Cleaning it is really easy once you've popped the nut off. It's got a little gauze filter/mesh inside. Give that a rinse under a tap, but before you do, check to see how many corrosive bits are in there as a reference.
🔥 Britain’s Heat Pump Shitshow
How Installing a Heating System Became a National Nervous Breakdown
Free UK shipping.
📗 Heat Pumps Explained
A Jargon-Free Guide for Homeowners
Rewritten and updated for 2027
📘 From Zero to Heat Pump Hero
🛠️ Bodge Buster
New to heat pumps?
Take the Heat Pump Fundamentals course and use INTRO50 at checkout for 50% off.
@editor Can't see anything that resembles a Y filter. There does seem to be a big black fillter (pic attached) which might be a filter?
Before and after the Evosta3 circulation pump there are valves. Is it worth making sure those are fully open?
The heat pump has just came on, the pipes near the water tank start to get a bit warmer and then the HP goes off again so sounds like it might be cycling?
@netdonkey The filter in the first photo looks saucespiciously like a ‘MagnaClean’ type filter; as the flow passes through this, the larger volume of the chamber reduces speed of flow and allows a magnet to attract and retain any particles of ferrous material that passes through the pipework. This chamber is normally cleaned out during any servicing work. Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
-
Issue with Samsung Cascade System
3 months ago
-
First time wall mounting an ASHP
12 months ago
-
How can I programme a setback for my Samsung Gen6 8kW heat pump?
1 year ago
-
Samsung problems
1 year ago
-
Sudden drop in COP
1 year ago
- 27 Forums
- 2,811 Topics
- 66.5 K Posts
- 2,245 Online
- 7,217 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Why don't people choose heat pumps?
It's swings and roundabouts - during off-peak periods t...
By Temperature_Gradient , 41 minutes ago
-
RE: The Changing Jet Stream Could Challenge UK Air Source Heat Pumps
... And that's being generous! I'll tell you a littl...
By SusannaSaunders , 7 hours ago
-
RE: Adding data centre electricity costs to domestic energy bills?
never ceases to amaze me.. Keeping steel works going ...
By Batpred , 8 hours ago
-
RE: Electricity price predictions
great session Reminds me why some politicians can be ha...
By Batpred , 8 hours ago
-
RE: Boiler Upgrade Scheme funding reduced by circa £750 million in 2026 budget
Absolutely agree. The massive Hager CU my vaillant requ...
By Batpred , 8 hours ago
-
RE: How much of your renewable and home setup would still work if the internet went down?
absolutely agree. even if many providers see that extra...
By Batpred , 8 hours ago
-
RE: Octopussy cosy 6 experience
People who have a Cosy appear generally to be happy wit...
By JamesPa , 12 hours ago
-
I thought the cr*p came first and the biofuel came afte...
By Majordennisbloodnok , 16 hours ago
-
RE: Aerotherm and weather compensation
@jamespa I replied yesterday with detailed readings whi...
By DavidB , 2 days ago
-
RE: Marvel Heating liquidation
@editor This is an important point. each winter, you...
By davidnolan22 , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
Very nice. we’ve been super soggy here, but rather m...
By Papahuhu , 4 days ago
-
RE: DIY powerflushing tutorial
Interesting! I toyed with the idea too. But I installed...
By bobflux , 4 days ago
-
RE: 15kw pump for 225m2 1990's house - over kill?
@seaviews Agree with the others on sequence: loft first...
By mk1234 , 4 days ago
-
RE: Vaillant ecoTEC Plus - Flow Temp and Set Up
Heating been on for 4 weeks now, continuous. It's 6C o...
By trebor12345 , 5 days ago