Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
@justme Even the condensing gas boilers were sometimes incapable of running well but carried the badge ‘Condensing’. We had a BG badged Glow Worm boiler that was well oversized and could not condense as it heated the hot water as well as heating BUT ONLY HAD ONE TEMPERATURE DIAL for DHW and Heating. You want condensing and cooler hot water or to hell with condensing! (In addition, BG had slapped the boiler in just set to its’ maximum capacity rating!) Who cares? We were paying BG for the fossil burning!!! Regrets, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
@toodles I got this from my new best friend (Google AI mode):
"If a condensing boiler's flow temperature (often set via a dial on the boiler itself) is too high, the return water from the radiators will be too hot to allow the boiler to enter condensing mode. (Note the source - The Heating Hub)
Condensing boilers reach their maximum efficiency (90%+) by recovering latent heat from exhaust gases. This process only happens effectively if the water returning from your radiators is cool enough to turn the water vapour in those gases back into liquid."
I have the thermostat of my backup oil boiler set to minimum. In my case it just sends water to the buffer tank but does so at a rather higher temperature than the heat pump. I'd prefer that the two sources were at the same temperature but I might be able to drop the boiler water temperature by altering the pump speed on that short loop - something to experiment with in the next cold snap.
@dr_dongle Precisely! Which is why a single temperature controller on a condensing gas boiler is just a joke and (cynically) probably just claimed to be a condensing system to satisfy some regulation or grant scheme. Cynical Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
@toodles I am on E.On Next Drive, no I don't have an EV.
I have compared other tariffs and even though I am pulling a small amount from the grid at the end of the day it still works out cheaper than octopus cosy tariff and other available tariffs, we already load shift the washing machine and Dishwasher to the cheap time and hardly use a tumble dryer, meaning that the house is generally on tickover for the rest of the day about 200w even when I am working from home.
At the moment on calculations its not viable to get a second battery as it will only save us about £30 a month for the winter months.
@n1ckw 200 Watts when working from home?! You are obviously not working hard enough!😉 Lovely weather today and the ASHP (keeping us at 22.5 degrees C.) is running on ~ 300 - 400 Watts when not on idle😊 Our average ‘house draw’ (without the heat pump) is `300 - 400 watts an hour. We are all electric of course and today we have harvested 18.4 kWh of solar energy so far and the sun still has a few more minutes of glory to share with us. This is the best day so far this year and very welcome after all the rain clouds of the last few months.
As you mention, a small amount of peak rate consumption is ‘cheaper’ than investment in a second Powerwall. I didn’t fancy changing my allegiance away from Octopus as I have previously had bad experience with other suppliers but don’t have a vehicle at all. Whether an EV tariff would be cheaper in my circumstances, I am unsure but I like Octopus’s ethos and straight dealings so will stick with them. The IOF tariff is possibly my next move though (just for the summer months) then back to Cosy if it is still available. Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
Posted by: @jamespaThe other difference is that boilers with weather compensation are generally European, whereas heat pumps are frequently far eastern. The European manufacturers, because they were forced to do it for boilers (it is mandatory in some enlightened EU countries), have sometimes developed a better, albeit still not perfect, interface to WC than the far eastern manufacturers.
For a heatpump system that cannot respond as quickly to heat loss as a gas boiler, some would need some sort of weather anticipation feature. 😁
I remember that my previous bosch/worcester boiler also had an external sensor that would enable it to have warmed the solid brick home to the target temperature by the set time..
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
Posted by: @toodlesWe had a BG badged Glow Worm boiler that was well oversized and could not condense as it heated the hot water as well as heating BUT ONLY HAD ONE TEMPERATURE DIAL for DHW and Heating. You want condensing and cooler hot water or to hell with condensing!
I find it almost incredible that they could get away with it.. 🤔Probably when a customer is desperate, after the breakdown of a previous boiler.. Was it not BG that had some warranty that would at some point allow them to choose any boiler they wanted?
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
Posted by: @batpredFor a heatpump system that cannot respond as quickly to heat loss as a gas boiler, some would need some sort of weather anticipation feature.
That's not necessary so far as I can see. Measuring the current weather tells the heat pump or boiler whats currently happening to the outside of house. The inside of the house will respond much slower than the heat pump or boiler can.
What we don't have at present is heating systems that take into account solar gain or wind factors. Neither is that dramatic in most cases, but it is a refinement that some here have experimented with on here. However its quite plausible that mild auto adapt of the sort featured by many boilers and heat pumps is sufficient to deal with this and if so it should probably be left at that. Boiler/Heat pump control systems are already too complex for many, perhaps most, ordinary people to cope with, adding additional factors needs to be carefully considered!
Anticipation might be useful for tariff optimisation, but do we really want another level of internet-driven complexity to an already complex control system. Personally I think heat pump manufacturers should leave this sort of thing to the geeks, and instead optimise the basic controls and function for ease of use.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Has anyone heard of or had a survey/design done by Apex?
A company I'm currently in talks with has used them for the heat loss survey + design and there are some very questionable things in there.
One example is a hallway area (4.75m x 1.3m, 2.4m high with 1 standard size external door and roughly 2m² window area) having a supposed 1290W heat loss (all other surveys I had averaged out to about 700W).
For context they, and most others, considered a ground floor extension of 2.5m x 3.8m with 4 standard-sized velux windows, a high vaulted ceiling, fully-glazed double french doors and in addition to the velux windows another 3.64m² of windows being around 1310W heat loss. Clearly these 2 rooms are absolutely nowhere close in terms of heat loss, and yet they've got a very similar number according to Apex.
They also disregarded some of my criteria (vertical radiator in the hallway due to size limitations) and instead listed 2 horizontal radiators. If I didn't have room for 1 horizontal radiator, where is this second one going to go??? And similarly for a bedroom I'm using as an office I requested it to be designed for 21c, they did it at 18c like all the other bedrooms.
They also seem to be really overestimating the output of my existing radiators and their proposed radiators. At a design flow of 47.5c in a room targeting 18c they've got down a P+ 600x1100 outputting 700W, but if I run the numbers (which I could be doing wrong) I only get 600W.
Can't say I'm thrilled from what they've given and I'll be speaking to the installer about my concerns and maybe question if they should find another company to do their surveys for them? It's a small operation so I don't blame them for outsourcing the heat loss and design, but I wouldn't be happy to proceed with it myself.
Posted by: @petchHas anyone heard of or had a survey/design done by Apex?
There are quite a few installers I know that are called 'Apex' - can you please give me the full name?
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
@editor I'm fairly certain it's this company but I'll have to check with the installer https://www.apex-surveys.co.uk/
@petch, nope, never came across these guys. I’ll look into them later this week.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
-
Is this ASHP install OK?
10 months ago
-
My Journey to Finding the Best Heat Pump for My Home in France
1 year ago
-
What is the most important factor for you when choosing a heat pump brand?
2 years ago
-
Mid terrace - ASHP Install location
2 years ago
-
Any installer recommendations for Samsung ASHP?
2 years ago
Currently viewing this topic 1 guest.
- 26 Forums
- 2,623 Topics
- 61.3 K Posts
- 739 Online
- 7,004 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Is Traditional Radiator Balancing Tosh?
@markspencersmith Before I offer my thoughts I am...
By JamesPa , 11 hours ago
-
RE: Brown Oily Residue Blocking Air Vent and Weeping Relief Valve... Anyone Seen This?
@editor i'm SEPA Registered with a waste license, we du...
By Aventus Eco , 13 hours ago
-
RE: Grant Aerona3 - Home Assistant control via Modbus
what controller are you using?
By Grantmethestrength , 15 hours ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Manufacturer: appliances direct/superheat Model: 7Kw ...
By Adrian , 17 hours ago
-
RE: Peak Energy Products V therm 16kW unit heat pump not reaching flow temperature
As a final update on this thread from me; Ribble Valley...
By DaveC , 17 hours ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Fantastic. This is all I needed. Afew planning applic...
By Batpred , 20 hours ago
-
RE: Renewables & Heat Pumps in the News
Commentary on DCs and the grid in the EU. A bit on some...
By Jeff , 1 day ago
-
RE: Mitsubishi Ecodan not good enough ?
If you put a fan in a pipe you get a much more efficien...
By bobflux , 1 day ago
-
RE: Mitsubishi ecodan settings
As the owner of a 8kW Ecodan R290 maybe I can help. ...
By RobS , 1 day ago
-
Wall mounting makes sense. We are now looking for an in...
By Batpred , 2 days ago
-
RE: Vaillant AroTherm Plus 7kW
Thank you, watson did allow me to find this one! Our ...
By Batpred , 2 days ago
-
RE: Our 10 year old Grant heat pump failed
Sorry to hear. Grant seem to be selling the R290 pump...
By Batpred , 2 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
.. apparently with american fuel. 🙃
By Batpred , 2 days ago
-
RE: The Watchdog That Watched and Waited
Spot on. The watchdog that knows how to never take the ...
By Batpred , 2 days ago
-
RE: Indevolt Batteries UK Support & Info Thread
Yes, the cost difference may be marginal, if you are lu...
By Batpred , 2 days ago
-
RE: Don’t Install a Heat Pump Until You Read This
In our latest update, we attempt to show what a poor he...
By Mars , 2 days ago
-
RE: Heat Pump Pipe Sizing Question
No the retrofit strategy is already published. It's on...
By JamesPa , 2 days ago
-
RE: Ecodan spells out end of R32 for real environmental alternative
I think I saw the answer to this on another thread but ...
By Batpred , 2 days ago
-
RE: Mitsubishi Ecodan FTC6, Evohome & Economy 7. Getting Two Zones to Work Together
This is what we are trying to avoid if we go Ecodan, mu...
By Batpred , 2 days ago
-
Great points, I agree it is overused. It is also a grea...
By Batpred , 2 days ago
-
RE: GSHP Kaput After 16 Years: New Compressor or Switch to ASHP? Advice Welcome
On old (non inverter) compressors there’s sometimes a ‘...
By robl , 2 days ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
@editor It's available here -
By HarrisonC , 3 days ago
-
@painter26 i am in Lightwater and midea trained. Sounds...
By Wizard , 3 days ago