Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Heat pump delta T too low - 2c
So we have an Ecodan 14kW heat pump. Had it a few years and it’s worked well but a bit expensive.
whenevrr I’ve checked the stats the delta between flow and return has always been 5c on the dot.
This year I’ve been balancing radiators and removing zones to make one big zone to improve efficiency. Which it has!
However I’ve noticed that now the Delta T is 2c most of the time. 3c max.
Which would indicate not enough heat is leaving the rads / UFH?
What do I need to check/adjust?
250sqm house. 30kWh Sunsynk/Pylontech battery system. 14kWp solar. Ecodan 14kW. BMW iX.
250sqm house. 30kWh Sunsynk/Pylontech battery system. 14kWp solar. Ecodan 14kW. BMW iX.
Posted by: @bensebSo we have an Ecodan 14kW heat pump. Had it a few years and it’s worked well but a bit expensive.
whenevrr I’ve checked the stats the delta between flow and return has always been 5c on the dot.
This year I’ve been balancing radiators and removing zones to make one big zone to improve efficiency. Which it has!
However I’ve noticed that now the Delta T is 2c most of the time. 3c max.
Which would indicate not enough heat is leaving the rads / UFH?
What do I need to check/adjust?
Is your heat pump running in weather compensation mode and if so, what are the slope settings?
Are you getting much cycling?
The temperature readings may vary dependent upon the speed of the water pump and whether the water is fully mixed by the time it reaches the sensors. Obviously monitor what is happening, but if your system appears to be functioning correctly it may not be something of great concern.
@derek-m Thanks Derek
Were in Weather Comp mode. 45c @-2, 25c @ 12c
This has been fine, but I have bumped it up +4 this week with it being windy as our house can be a bit leaky and it’s quite exposed.
As far as cycling, I can’t see much evidence of this. Maybe 1 or 2 cycles per hour but mostly a steady flow temp. Heating has been actively running for 45% of the time in the last 7 days but we do have a log burner which tends to turn it off in the day and a 2c overnight setback so sounds about right?
I think our heat pump flow is a bit low (29l/s vs recommended 35-40) but not much we can do about that without a lot of upheaval.
I was wondering if the flow on the secondary side was correct. No way to measure that. They just used the existing pipework and whacked a 40-70 Evosta DAB pump on it, on full whack! We also have an UFH zone coming off it too. I’ve no way really of measuring the flow and knowing If the pump is on too high? (We have a buffer so it’s not same flow rate as HP)
ben
250sqm house. 30kWh Sunsynk/Pylontech battery system. 14kWp solar. Ecodan 14kW. BMW iX.
Without knowing the full details of your system, including the heat loss calculations, it is difficult to provide advice.
Do you have any thermostats within your system, and if so, are they actively switching your secondary pump and heat pump on and off?
Running a wood burner will further complicate the control of the system. Is your wood burner on all day? Where is it located? Does it draw air from the room or does it have a separate ducted supply?
I am not surprised that you had to set your WC at +4, since LWT of 25C @ 12C ambient is quite low. LWT of 25C @ 20C would probably be more appropriate.
A buffer will further complicate your system even more. In an ideal World, the water flow rate going into the top of the buffer from your heat pump, will be matched by the flow rate of the warm water being drawn out of the top of the buffer and fed to the heat emitters. The return water flow rate from the heat emitters going back into the bottom section of the buffer, will be matched by the flow rate of the return water being drawn out of the bottom of the buffer and sent to the heat pump. We don't live in an ideal World.
More than likely there will be mixing of the water within the buffer, which could lead to cooler water being fed to the heat emitters and lower overall efficiency.
As far as temperature and flow measurements are concerned, it is unlikely that they will be totally accurate, and the accuracy could even vary under different operating conditions.
If you have a suitable thermometer, I would suggest measuring the temperature at the inlet and outlet pipes at your buffer and compare these with the ones provided by the controller. Note the changes with the heat pump running, and after it has been stopped for a period of time. Monitor the operation under varying weather conditions.
Balancing with weather compensation on gas boilers and heat pumps is about distributing heat evenly and appropriately through the system, not about achieving any particular delta t accross the rads.
So open the valves more to enable the system to stabilise as it was before!
Professional installer
@benseb the Delta T should be between 5 and 10 Deg C. Try reduce the speed on one of the circulating pumps. This will increase the Delta T and further reduce your running cost. Do you have a buffer tank? If so see if you can pipe it out, this will further increase your performance.
Thanks all.
I will do some measurements and also try opening some valves
i did try turning the pump down from 3 to 1 but the delta didn’t shift, still 2c
250sqm house. 30kWh Sunsynk/Pylontech battery system. 14kWp solar. Ecodan 14kW. BMW iX.
What are people trying to achieve by widening the delta 2
the best approach is maximum flow and key the heat pump decide the rest
gas boilers are slightly different, but with weather compensation a delta t is fine especially at low temps
Professional installer
I would not get too fixated on the DeltaT reading, which may not be correct anyway. As Alec has pointed out, concentrate more on how your system is performing. If you have a suitable thermometer then measure the temperatures around your buffer, and record them over a period of time under different operating conditions. Ensure that the thermometer is in good thermal contact with the pipework and suitably insulated from the surrounding air.
If you need any help in interpreting the results then please post them on the forum.
The Heat Geek YouTube channel have released all their data on their own office's heat pump openly here: https://emoncms.org/heatgeek/graph . You can see that their DeltaT is typically less than 3 degrees C. Echos what the experts here are saying, but nice to have actual data from a real install to compare with.
ASHP: Mitsubishi Ecodan 8.5kW
PV: 5.2kWp
Battery: 8.2kWh
@scrchngwsl The ideal Delta T for a heat pump is 8 Deg C. Any variance, either way, will reduce performance. The good units on the market will control this temperature gap by varying the compressor and pump speeds to achieve permit performance.
- 26 Forums
- 2,618 Topics
- 61.1 K Posts
- 884 Online
- 6,993 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Indevolt Batteries UK Support & Info Thread
Thanks @editor , @indevolt-uk Subject to any comments ...
By JamesPa , 6 hours ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
@seoras Sorry to hear that. I found Vaillant very help...
By JamesPa , 7 hours ago
-
The Watchdog That Watched and Waited
On 9 January 2026, Consumer Energy Solutions collapsed ...
By Mars , 10 hours ago
-
RE: GSHP Kaput After 16 Years: New Compressor or Switch to ASHP? Advice Welcome
Cool Energy in Grimsby sell ground source heat pumps an...
By DerekDeLeon , 11 hours ago
-
RE: Valliant Heat Pump Settings
Thats arguably a sign of a good installer - they unders...
By JamesPa , 12 hours ago
-
RE: Electricity price predictions
Well, we have so many cases where rain water mixes with...
By Batpred , 12 hours ago
-
RE: Two heating zones to one zone
@profzarkov They arent obviously wrong, but the only...
By JamesPa , 15 hours ago
-
RE: Towns water feed to air source heat pump system
The DHW circuit cant be separated (well it could, you c...
By JamesPa , 15 hours ago
-
Solis AC-coupled 3kW storage inverter
Solis AC-coupled 3kW storage inverterPylontech batterie...
By MartinRobinson , 21 hours ago
-
RE: My NIBE ASHP Nightmare: No Commissioning, High Bills and a Hostile Installer
As @transparent has observed above, this is not bad, an...
By cathodeRay , 22 hours ago
-
RE: The Grid Says Yes.. Until It Doesn’t: Why Britain's Net Zero Push is Stalling at the Plug Socket
As I was reading this article Mars, I was thinking that...
By Toodles , 2 days ago
-
RE: Tell us about your Solar (PV) setup
Installed in May 2011: 16*Sharp 245 W monocrystalline p...
By txmartyn , 2 days ago
-
-
RE: Say hello and introduce yourself
That doesn't sound 'right' to me. The national Smart ...
By Transparent , 3 days ago
-
RE: Growatt battery disconnected
I doubt this will happen, but I will try and suggest it...
By Eliuccio , 3 days ago
-
Understood. That's why I decided from the outset on a ...
By JamesPa , 3 days ago
-
RE: My experience with 3 heat pump surveys: Heat Geek, British Gas & Octopus
On the litigation, I would not go there and definitely ...
By Batpred , 3 days ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
I suppose if your pv inverter packs up, you have a plan...
By Batpred , 4 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Firstly check you are using sound power not sound press...
By JamesPa , 4 days ago
-
That’s the solar up and running, I don’t think it’s the...
By David999 , 4 days ago
-
RE: Seeking ideas / information / commiseration - Pure Drive
I agree with @colinc that you can reuse some of it. A s...
By Batpred , 4 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@toodles Im trying me best to ignore orangeman, I figur...
By Papahuhu , 4 days ago
-
@toodles That’s way better per kWp performance than our...
By Papahuhu , 5 days ago