Predicted Heat Loss & Needs from MCS calcs vs EPC vs actual
LG therma V installed 2020. 16kw monobloc. Initially on fixed flows then weather compensation
Looking back at the info from design in 2020
EPC 2020 predicted
The annual Space Heating requirement for your property is: 19,242kWh The annual Hot Water requirement for your property is: 2,997kWh
MCS 2020 predicted:
The annual Space Heating requirement for your property is: 23,776kWh The annual Hot Water requirement for your property is: 3,957kWh
Based on fixed flow temp 50deg
A difference of almost 5500kWh
Recent EPC 2025 predicted
32,443 kWh per year for heating
3,283 kWh per year for hot water
Total 35,726kWh!!
Actual metered heat pump usage was just over 8000kWh for the first 2 years on fixed flows and 5800kWh for the next 3 years on weather compensation.
At a total guess average COP across heating and hot water is 3? So my true heat loss & hot water requirement is probably in the region of 18000kWh (half the recent epc prediction!!!)
We heat main areas of the house to 21deg but bedrooms and lesser used rooms are much cooler. We normally have only 2 living at home so hot water usage is lower thsn predicted.
All the same it shows huge differences.
I think its a depressing example of the value of all these calcs. I'm sure there are other examples which are much closer to reality?
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
My gut feeling is that the heat pump is right sized.
- it does not seem to cycle
- It heats the house comfortably
- costs/usage seems reasonable - especially against predictions by EPC or MCS
- the spare capacity would probably allow us to heat all rooms to 21deg if we wanted to
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
-
Heat Pump Heats the House… But It’s Not Cosy. Emitter Changes or System Tweak?
3 weeks ago
-
How to choose Towel Rails for an ASHP
4 months ago
-
Compute heat loss from energy used
6 months ago
-
Air Changes per Hour - ACH and the MCS requirement
7 months ago
-
Non standard houses with non standard owners
1 year ago
Currently viewing this topic 1 user ( Tim441 ) .
- 26 Forums
- 2,396 Topics
- 54.3 K Posts
- 146 Online
- 6,077 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Recommended home battery inverters + regulatory matters - help requested
The diagram below is a simplified view of the internals...
By Batpred , 7 hours ago
-
RE: Heat pump not reaching flow temperature
@davec Ive had a look at the screenshots. Lots of th...
By JamesPa , 8 hours ago
-
RE: Vaillant aroTherm not heating with many faults
When I had a series of apparently unrelated faults my i...
By JamesPa , 8 hours ago
-
RE: Considering MLCP (Multi-Layer Composite Pipe) for ASHP
OK, TBH I dont know enough about MLCP to comment with a...
By JamesPa , 11 hours ago
-
RE: Predicted Heat Loss from MCS calcs vs EPC vs actual
My gut feeling is that the heat pump is right sized. ...
By Tim441 , 11 hours ago
-
RE: Power outages and storms: A surprisingly good DNO experience
Agreed, which is no more nor less than a customer shoul...
By Majordennisbloodnok , 13 hours ago
-
RE: Running from backup generaor in powercut?
@batpred In our case, 3 times each day when the Octopus...
By Toodles , 13 hours ago
-
RE: Advice for a novice on Mitsubishi Ecodan 6kW
Hi @sheriff-fatman Cycling at 5C and below is usuall...
By RobS , 13 hours ago
-
RE: New Fogstar 15.5kWh upright solution
@batpred Here's the latest Fogstar ready built pack....
By Bash , 15 hours ago
-
RE: RDSAP10 effect on existing heat pump EPC rating?
@mike-patrick yes, even though the current system is ru...
By Tim441 , 15 hours ago
-
RE: Solis inverters S6-EH1P: pros and cons and battery options
Solis confirmed that the S6 works with a single battery...
By Batpred , 16 hours ago
-
RE: Who has a V2G EV installation
I am wondering if in any V2X, would the car battery eve...
By Batpred , 16 hours ago
-
RE: Setback savings - fact or fiction?
Yes, by calculating it manually from the minute data, w...
By cathodeRay , 18 hours ago
-
Fan unit Making terrible noise HELP!!
One of a pair of fan units on an Earth Save Classic II ...
By GutoFfowc , 18 hours ago
-
RE: New Mitsubishi Ecodan 11.2kW installation - L9 errors and maybe more
OK. I think your system, which seems well designed, is...
By JamesPa , 20 hours ago
-
RE: Heatpunk Floor plan issues
It's usually the complete opposite... seldom that Safar...
By Mars , 1 day ago
-
RE: Fan is clipping ice build up from the front of unit.
@majordennisbloodnok I’ll not go there thanks! Toodles.
By Toodles , 2 days ago
-
RE: Running my new Nibe ASHP efficiently
I'm new to the forum. Did you get a reply to this last ...
By Mike @ Camelot , 2 days ago
-
RE: ASHP Energy Consumption: Aira 12kW heat pump
@grantmethestrength MCS requirements for DHW capacity h...
By Toodles , 2 days ago