Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Low flow rate on Samsung Gen6 12KW heat pump
Posted by: @riponowlAs far as I can see there is no way that the Eastron could possibly know which zone is active. It's not incorrectly wired, it's not wired at all.
You are correct. There should be a cable from terminal B17 in the control kit (the large white metal box with all the electrics inside) that goes to the L2 terminal in the Eastron. B17 becomes live when DHW is being heated and so when B17 is
connected to L2 in the Eastron, this becomes live as well. This tells the Eastron to label the flow temperature reading as DHW (there is only one flow temperature reading - it is just the label that changes). When L2 is not live the flow temperature is labelled as space heating.
It took 3 months for G L to get Passivliving to work at all. The G L electrician, who eventually sorted it, seemed very capable, but I presume they are instructed not to bother to connect a cable between B17 in the control kit and L2 in the Eastron. It is quite clearly explained in the Passivliving MMSP installation guide, so why they don't follow it, beats me. In my case there is a connection between L1 and L2, which there shouldn't be, which means that L2 is permanently live and my flow temperature is always labelled DHW. I did finally get a date for another G L electrician to correct this, but I had to cancel it and despite leaving messages they never got back to me. I asked Ofgem if it was important to rectify and they never replied, so I left it.
Posted by: @riponowl@iancalderbank Where do you go to set a reheat timer for the HW? I'll try adding some lagging to the pipework and see if that helps.
settings button , buttom right hand corner of your controller.
scroll right -> schedule
fairly intuitive from there on
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
-
Hypothetical House Design
3 weeks ago
-
Flow Rate & Low Loss Headers
1 year ago
-
Primary Pump positioning for Samsung Gen6 system
2 years ago
-
Training videos/course/whatever. Control settings
3 years ago
- 26 Forums
- 2,720 Topics
- 63.7 K Posts
- 904 Online
- 7,122 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
Well I usually do it by feel, which is a slight problem...
By Transparent , 3 hours ago
-
RE: Existing Solar Panel installation - structural roof calculation check
@hml1827 I couldn't have put it better, possibly with t...
By JamesPa , 3 hours ago
-
@jeff I am well aware of the riskiness of such investme...
By Toodles , 6 hours ago
-
Fully understood and entirely reasonable! On the home ...
By JamesPa , 12 hours ago
-
RE: Electricity price predictions
So I am really having difficulty trying to work out wha...
By bontwoody , 15 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
We already do this - non grid tie self installed panels...
By EtchedPixels , 21 hours ago
-
Ok Well almost certainly it could be used instead of ...
By JamesPa , 1 day ago
-
RE: Samsung heat pump - data cable issue
Samsung reference it as "RS485 - COMM" in my manual. ...
By Old_Scientist , 1 day ago
-
RE: Vaillant Arotherm Pro vs new Plus
It kind of should not matter... My main thought is to a...
By Batpred , 1 day ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Looks beautifully integrated.. We had our done as wel...
By Batpred , 1 day ago
-
RE: SolarEdge SE5000H Inverter Failure
Update. My SolarEdge inverter was replaced yesterday wi...
By L8Again , 1 day ago
-
For cooling a whole building, or even a big room with l...
By EtchedPixels , 2 days ago
-
RE: Comms and power cabling to outside unit
@old_scientist 100%, the cover is for warrantied unit...
By Papahuhu , 2 days ago
-
I don't remember the manufacturer name, but I saw simil...
By bobflux , 2 days ago
-
RE: Weather compensated secondary circuits with Biomass
UFH is ideal to get max efficiency with a heat pump, bu...
By bobflux , 2 days ago