Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Vaillant Arotherm Plus Help needed
I installed Vaillant Arotherm Plus as per diagram, replaced gas boiler:Appliances: aroTHERM plus VWL < 10 kW, VWZ MEH 97 , VWZ MWT 150 Controls: VRC720, VR71, underfloor heating.
VRC720 shows now HP control module fault: anyone knows what is this about and which control module is this? Vaillant seems got no idea how to find the source of this fault. On top of it, getting F.1100 fault whenever VWZ MEH 97 gets switched on. I am in the middle of nowhere in france, getting someone to help going to be a nightmare and will cost me a fortune. ( i should have bought reliable asian appliances, grm made now looks like crap, sorry for my french). i checked all ebus cables, connections all setup correctly. do i miss smtg, like do i need to get another control installed, like vwz-ai vwl control module? thanks in advance
Posted by: @vlp2024I installed Vaillant Arotherm Plus as per diagram, replaced gas boiler:Appliances: aroTHERM plus VWL < 10 kW, VWZ MEH 97 , VWZ MWT 150 Controls: VRC720, VR71, underfloor heating.
VRC720 shows now HP control module fault: anyone knows what is this about and which control module is this? Vaillant seems got no idea how to find the source of this fault. On top of it, getting F.1100 fault whenever VWZ MEH 97 gets switched on. I am in the middle of nowhere in france, getting someone to help going to be a nightmare and will cost me a fortune. ( i should have bought reliable asian appliances, grm made now looks like crap, sorry for my french). i checked all ebus cables, connections all setup correctly. do i miss smtg, like do i need to get another control installed, like vwz-ai vwl control module? thanks in advance
I would suggest that you read through the attached guide and see if it throws any light onto your problems.
Posted by: @vlp2024I installed Vaillant Arotherm Plus as per diagram, replaced gas boiler:Appliances: aroTHERM plus VWL < 10 kW, VWZ MEH 97 , VWZ MWT 150 Controls: VRC720, VR71, underfloor heating.
VRC720 shows now HP control module fault: anyone knows what is this about and which control module is this? Vaillant seems got no idea how to find the source of this fault. On top of it, getting F.1100 fault whenever VWZ MEH 97 gets switched on. I am in the middle of nowhere in france, getting someone to help going to be a nightmare and will cost me a fortune. ( i should have bought reliable asian appliances, grm made now looks like crap, sorry for my french). i checked all ebus cables, connections all setup correctly. do i miss smtg, like do i need to get another control installed, like vwz-ai vwl control module? thanks in advance
Did you resolve your problem?
Feedback is required to prevent wasted effort.
@derek-m thank you for a wonderful guide, i know it i think by now by heart :). HP control module fault i found is due to bended cable. F.1100 i could not solve, just will not go away unless i set heater to external type. But now i got a new challenge: it will not run DHW and Heating same time, wonderful engineering, very clever. so, i am struggling now to solve this puzzle. for f1100 i probably have ot purchase new cut off thermostat. it costs around 110euros. I tried different circuits to get both heating and DHW same time with no success, ( heating goes via HEX) and tried circuits from 8 to 16. why engineers did come up with that idea. vaillant reminds me expensive but useless skin care for ladies: lots of marketing with horsesht but in reality suppose to heat only.
Posted by: @vlp2024@derek-m thank you for a wonderful guide, i know it i think by now by heart :). HP control module fault i found is due to bended cable. F.1100 i could not solve, just will not go away unless i set heater to external type. But now i got a new challenge: it will not run DHW and Heating same time, wonderful engineering, very clever. so, i am struggling now to solve this puzzle. for f1100 i probably have ot purchase new cut off thermostat. it costs around 110euros. I tried different circuits to get both heating and DHW same time with no success, ( heating goes via HEX) and tried circuits from 8 to 16. why engineers did come up with that idea. vaillant reminds me expensive but useless skin care for ladies: lots of marketing with horsesht but in reality suppose to heat only.
Heat pumps are not designed to provide central heating and DHW heating at the same time.
DHW heating requires a much higher leaving water temperature than central heating would normally need. The heat pump therefore cannot do both at the same time.
It would appear that the safety cut-out has operated, which is causing the F.1100 fault to appear. I would suggest you check to see if the fuse has blown, also see if there is a reset pushbutton that may need to be pressed.
@derek-m thanks Derek, any idea where that magic fuse i located? i imagine engineers did design this system with fuse in mind, but i could not find it (for cut-off thermostat). reset is clear, it was pressed with no luck.
Posted by: @vlp2024@derek-m thanks Derek, any idea where that magic fuse i located? i imagine engineers did design this system with fuse in mind, but i could not find it (for cut-off thermostat). reset is clear, it was pressed with no luck.
All that I can suggest is that you trace back along the cable to the place from which the heater is supplied.
Is this heater the DHW cylinder immersion heater or the back-up heater used to help out the heat pump in very cold weather? If it is the latter, do you actually need it?
Download and read through this document.
Posted by: @vlp2024@derek-m have you seen built in immersion heater in 97/6?
It is actually called a 'back-up heater' and is in addition to the immersion heater, which would be located in the hot water cylinder. The purpose of the back-up heater is to provide addition thermal energy if the outside heat pump cannot provide sufficient thermal energy. Obviously, it is direct electrical heating with a COP of 1, so should only be used when absolutely necessary.
It would appear that you probably have the choice of disabling the back-up heater by deselecting it, as I think you have already done, or replace the cut-out unit which would then make the back-up heater available for use once more.
The choice is yours to make.
@derek-m you just made entire arotherm plus technology useless, by notion it should heat both DHW and UFH in parallel. what i have so far achieved is having hydraulic stations to up cylinder and then auto switch to heating and so on, unfortunately no parallel operation. i am going to phone vaillant to clarify if this thing will ever work in parallel. (don't tell me this is not possible, mitsubishi, daikin and samsung do it). my cop so far is above 4.32, electrical heating? i got PV for electricity and solar to water to cylinder
Good morning,
Arotherm owner for 18 months here.
@Derek-m is indeed correct. Arotherm will do one, or the other, not both together. Ours is set for hot water priority so kicks the heating off for the time it takes for the water tank to heat.
its all about planning when is best. We heat our water in the early morning, cheap electricity, and in the afternoon when we get the highest solar gain.
atb
Drew
Posted by: @vlp2024@derek-m you just made entire arotherm plus technology useless, by notion it should heat both DHW and UFH in parallel. what i have so far achieved is having hydraulic stations to up cylinder and then auto switch to heating and so on, unfortunately no parallel operation. i am going to phone vaillant to clarify if this thing will ever work in parallel. (don't tell me this is not possible, mitsubishi, daikin and samsung do it). my cop so far is above 4.32, electrical heating? i got PV for electricity and solar to water to cylinder
If you wish to supply your central heating and DHW heating from one heat pump at the same time then please feel free to do so.
- 26 Forums
- 2,590 Topics
- 60.3 K Posts
- 546 Online
- 6,922 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Air-to-air heat pumps - best models and installers
@ashp-bobba, do I remember correctly that you install A...
By Mars , 7 hours ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
There isn’t as far as I know, @djh, but you’re welcome ...
By Majordennisbloodnok , 11 hours ago
-
RE: Can anyone explain the following behaviour with a Grant Aerona 3 R30 / Smart Controller?
Final Update. Yesterday, I was going through the moti...
By Unsure , 13 hours ago
-
RE: How much can an east/west solar solar system be oversized?
Best performance occurs with PV string near inverter no...
By bobflux , 13 hours ago
-
RE: Forum updates, announcements & issues
Thank you Mars for all your dedication to improvements;...
By Toodles , 16 hours ago
-
RE: Who do I complain to about a poor ECO4 installation, can anyone advise?
Take it one step at a time. If you can get the dhw and...
By JamesPa , 22 hours ago
-
RE: Selling 2 x Kensa Shoebox 7kw GSHP (New)
Hi Jain, we’ve got an ashp so I’m afraid we won’t be yo...
By Judith , 22 hours ago
-
No buffer or low loss header Grant controller in sens...
By JamesPa , 1 day ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
That's an amazing job to get all that in there! A truly...
By Batpred , 1 day ago
-
RE: Anyone concerned about GivEnergy?
Thanks for your advice - I'll keep trying with the inst...
By JohnDwyer , 2 days ago
-
RE: Plug and play solar. Thoughts?
I am also yet to find a case where an installation that...
By Batpred , 2 days ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
This is what I got from OVO. At least it was quick.. ...
By Batpred , 2 days ago
-
RE: IVT greenline HT Plus E - Circulation Pump Constantly On
Welcome to the forums. Irrespective of which brand yo...
By Mars , 2 days ago
-
RE: 7.5kW Heat Loss, But Quoted a 10kW Midea. No Re-Pipe, No Buffer Tank. Does This Add Up?
Oh, how I love these old scientists!I'm in with your 5 ...
By LeJamaisContent , 2 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@jamespa Someone who is not easily phased I suppose.
By Toodles , 3 days ago
-
@downfield Once OE had removed our gas meter and capped...
By Toodles , 3 days ago
-
Living with a Low Loss Header (Or Measure For Measure, it’s All About the Pump)
I know, low loss headers (LLHs) aren’t necessarily ‘low...
By Toodles , 3 days ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
After seeing umpteen negative price slots again today, ...
By ChandyKris , 3 days ago
-
RE: The Reality Behind a Failed Heat Pump Installation – and an IWA Insurance Rejection
@ian-w Getting back to the problem in hand, what do yo...
By JamesPa , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@papahuhu Generally, I leave Homely to take care of mat...
By Toodles , 3 days ago
-
@judith, glad you found the story interesting. On eff...
By Mars , 4 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
The vaillant controller and app do all of that (and mor...
By JamesPa , 4 days ago