Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Vaillant Arotherm Plus Help needed
Posted by: @fazelPosted by: @vlp2024(don't tell me this is not possible, mitsubishi, daikin and samsung do it).
How they achieve that? technically.. any pdf?
Â
I suspect that they just remove the 3-way diverter valve, so that the heat pump supplies both central heating and DHW heating at the same time, though I'm not certain how successful that may be. 🙄Â
Â
Posted by: @vlp2024@derek-m you just made entire arotherm plus technology useless, by notion it should heat both DHW and UFH in parallel. what i have so far achieved is having hydraulic stations to up cylinder and then auto switch to heating and so on, unfortunately no parallel operation. i am going to phone vaillant to clarify if this thing will ever work in parallel. (don't tell me this is not possible, mitsubishi, daikin and samsung do it). my cop so far is above 4.32, electrical heating? i got PV for electricity and solar to water to cylinder
Â
And gas boiler that operates weather compensation does exactly the same, for the simple reason that you need a higher flow temp for dhw than for space heating.
We haven't typically done weather compensation in the UK with fossil fuel burners, but other European countries have. Thus it's perfectly normal for space and water heating not to happen since simultaneously and nothing special to ashps. Â
Â
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
I guess that in principle, with the right plumbing, you could run both together at the ft of the dhw. Lousy efficiency and the output is divided between the two so possibly lousy performance, but a dhw tank is just another heat sink.
Why you would choose to do this escapes me however.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa just wanted to understand why would Vaillant not officially admit it: simply cannot run in parallel unless some work arounds like you said implemented, in the end, pipe can feed both ends. maybe modern competition became unpleasant game of plays or smtg else. my mistake was i opted for german made hoping i am getting quality, thats all. i run air to air in two other rooms also, electricity comes from pv plus main electricity. same here, but in that case for top performance one could have get 97/6 only for UFH and end one like 4-5kw for cylinder, seating on top of each other. just ideas.
Posted by: @vlp2024just wanted to understand why would Vaillant not officially admit it: simply cannot run in parallel unless some work arounds like you said implemented, in the end, pipe can feed both ends. maybe modern competition became unpleasant game of plays or smtg else. my mistake was i opted for german made hoping i am getting quality, thats all.
All a2w heat pumps work this way so far as I know, because it makes sense, Vaillant is no different. Ditto gas boilers with weather compensation.
Of course with any device you can do all sorts of things other than the standard ones, but few want to so why are manufacturers going either to confuse their documentation by documenting it, or support it, especially when all domestic a2w heat pumps are the same in this respect. It's nothing conspiratorial and Vaillant competitors do the same.
The subtle difference is that Vaillant (probably not uniquely) don't interfere with the immersion at all so you are free to use it as you wish. Some other manufacturers commandeer the immersion for the disinfection cycle, vaillant r290 pumps do the disinfection natively.
Â
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @vlp2024@jamespa just wanted to understand why would Vaillant not officially admit it: simply cannot run in parallel unless some work arounds like you said implemented, in the end, pipe can feed both ends. maybe modern competition became unpleasant game of plays or smtg else. my mistake was i opted for german made hoping i am getting quality, thats all. i run air to air in two other rooms also, electricity comes from pv plus main electricity. same here, but in that case for top performance one could have get 97/6 only for UFH and end one like 4-5kw for cylinder, seating on top of each other. just ideas.
I don't know of any heat pump that can provide both central heating and DHW heating at the same time, which could drastically reduce its efficiency.
It is possible to obtain a DHW cylinder which has a small inbuilt heat pump that solely does DHW heating. I know of one of the forum members that has had one installed.
Since you have a solar PV system, are you not heating the DHW via a power diverter?
Â
@derek-m agree, with solar i get up to 45-55C max , during sunny days i get temperatures on panels around 110-120 and DHW around 55-58, but those are during hot days( we got plenty of sun anyway). i only raised this point because of expectations, you know when you expect ( falsely assumed). you right and solar panels cover 260-280 days min (2 panesl, 2sqm each). i am extremely happy with solar heating. i trust arotherm will do its work too, maybe needed a bit of playing around. house is 170sqm with water UFH 100sqm, rest with electrical UFH. it was extremely difficult to plan arotherm plus, i dont know why we got HEX< maybe to save money on glycol, but then why we need glycol if we got 280 sunny days and -5-15 is a rare commodity here. i should have gone with simple install, my mistake. what i am happy about is with UFH thermostats and how easy it was to split into zones ( 6 of them per room) , all RF based, using shk.
Posted by: @vlp2024@derek-m agree, with solar i get up to 45-55C max , during sunny days i get temperatures on panels around 110-120 and DHW around 55-58, but those are during hot days( we got plenty of sun anyway). i only raised this point because of expectations, you know when you expect ( falsely assumed). you right and solar panels cover 260-280 days min (2 panesl, 2sqm each). i am extremely happy with solar heating. i trust arotherm will do its work too, maybe needed a bit of playing around. house is 170sqm with water UFH 100sqm, rest with electrical UFH. it was extremely difficult to plan arotherm plus, i dont know why we got HEX< maybe to save money on glycol, but then why we need glycol if we got 280 sunny days and -5-15 is a rare commodity here. i should have gone with simple install, my mistake. what i am happy about is with UFH thermostats and how easy it was to split into zones ( 6 of them per room) , all RF based, using shk.
Where are you located?
I don't wish to appear too negative, but the consensus of opinion is that having lots of zones with a heat pump is not the most ideal way to operate. For best overall efficiency, it is thought that keeping the maximum amount of heat emitter capacity active, means that the heat pump can operate at the lowest required Leaving Water Temperature (LWT), which increases the efficiency of the heat pump. Having zones switching on and off reduces the overall heating capacity, requiring a higher LWT and possibly causing premature cycling to occur, which again can reduce efficiency.
Â
- 26 Forums
- 2,590 Topics
- 60.3 K Posts
- 439 Online
- 6,922 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Air-to-air heat pumps - best models and installers
@ashp-bobba, do I remember correctly that you install A...
By Mars , 7 hours ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
There isn’t as far as I know, @djh, but you’re welcome ...
By Majordennisbloodnok , 11 hours ago
-
RE: Can anyone explain the following behaviour with a Grant Aerona 3 R30 / Smart Controller?
Final Update. Yesterday, I was going through the moti...
By Unsure , 13 hours ago
-
RE: How much can an east/west solar solar system be oversized?
Best performance occurs with PV string near inverter no...
By bobflux , 13 hours ago
-
RE: Forum updates, announcements & issues
Thank you Mars for all your dedication to improvements;...
By Toodles , 16 hours ago
-
RE: Who do I complain to about a poor ECO4 installation, can anyone advise?
Take it one step at a time. If you can get the dhw and...
By JamesPa , 22 hours ago
-
RE: Selling 2 x Kensa Shoebox 7kw GSHP (New)
Hi Jain, we’ve got an ashp so I’m afraid we won’t be yo...
By Judith , 22 hours ago
-
No buffer or low loss header Grant controller in sens...
By JamesPa , 1 day ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
That's an amazing job to get all that in there! A truly...
By Batpred , 1 day ago
-
RE: Anyone concerned about GivEnergy?
Thanks for your advice - I'll keep trying with the inst...
By JohnDwyer , 2 days ago
-
RE: Plug and play solar. Thoughts?
I am also yet to find a case where an installation that...
By Batpred , 2 days ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
This is what I got from OVO. At least it was quick.. ...
By Batpred , 2 days ago
-
RE: IVT greenline HT Plus E - Circulation Pump Constantly On
Welcome to the forums. Irrespective of which brand yo...
By Mars , 2 days ago
-
RE: 7.5kW Heat Loss, But Quoted a 10kW Midea. No Re-Pipe, No Buffer Tank. Does This Add Up?
Oh, how I love these old scientists!I'm in with your 5 ...
By LeJamaisContent , 2 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@jamespa Someone who is not easily phased I suppose.
By Toodles , 3 days ago
-
@downfield Once OE had removed our gas meter and capped...
By Toodles , 3 days ago
-
Living with a Low Loss Header (Or Measure For Measure, it’s All About the Pump)
I know, low loss headers (LLHs) aren’t necessarily ‘low...
By Toodles , 3 days ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
After seeing umpteen negative price slots again today, ...
By ChandyKris , 3 days ago
-
RE: The Reality Behind a Failed Heat Pump Installation – and an IWA Insurance Rejection
@ian-w Getting back to the problem in hand, what do yo...
By JamesPa , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@papahuhu Generally, I leave Homely to take care of mat...
By Toodles , 3 days ago
-
@judith, glad you found the story interesting. On eff...
By Mars , 4 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
The vaillant controller and app do all of that (and mor...
By JamesPa , 4 days ago