Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Is my Ecodan well installed and setup?
@trbob I realise that this thread is a bit old but I have a similar problem with the Legionnaires cycle taking too long. In particular, it is the initial immersion bit which takes 1 hour to get from 50c to 54.5c.
Did you every resolve your issue with the legionnaire Cycle?
Install 13 April 2024 - 4 Bedroom Brick Detached - Heat Loss 9,281w, Design 45c at -2 - Ecodan 11.2kw R32 - 25L Buffer - 250L Telford Tempest HP DHW - All 16 radiators replaced - Auto Adapt - Mel-Pump app - Octopus Cosy Fixed
10 March 2026 - now 2 x Sigenstor 10 batteries with 8kw Inverter
Hi Richard, what I do now (I'm on Octopus Cosy) is to have my Hot Water come on at 12:45pm (heated by the ASHP, the load isn't too bad in the first 15 minutes) and my Legionella Cycle is set to come on at 1pm and lasts for 2 hours. It will let the ASHP get to 51.5 before switching to the immersion element. This seems to be the best way I could find of doing it. I noticed a few weeks ago that it got up to temperature on the Legionella cycle relatively quickly as it was a fairly mild(ish) day, it's a shame that it doesn't end the cycle itself as we could have banked some heating before 4pm.
Mitsubishi Ecodan 8.5kW
4.4kW Solar PV
5.2 kWh Battery Storage
1983 build, 300mm loft insulation, cavity wall insulation (beads)
@trbob Thanks. Does that mean your system reached the 60c within the 2 hours?
Not sure if I understand your last comment concerning ending the cycle.
According to my Ecodan Legionnaire settings, it's supposed to reach 60c and the stay there for 5 minutes. After 5 minutes it should end the cycle. Unfortunatley, in my case it never reaches the 60c before tiiming out at 2 hours.
Install 13 April 2024 - 4 Bedroom Brick Detached - Heat Loss 9,281w, Design 45c at -2 - Ecodan 11.2kw R32 - 25L Buffer - 250L Telford Tempest HP DHW - All 16 radiators replaced - Auto Adapt - Mel-Pump app - Octopus Cosy Fixed
10 March 2026 - now 2 x Sigenstor 10 batteries with 8kw Inverter
@richard24738 Yes it's usually 59 or 60 thereabouts (or sits at 59.5 for ages, not drawing any power), yes mine is set for 5 minutes as well I think, but it has never to my knowledge ended the cycle, it just times out in the end at 3pm.
Mitsubishi Ecodan 8.5kW
4.4kW Solar PV
5.2 kWh Battery Storage
1983 build, 300mm loft insulation, cavity wall insulation (beads)
@trbob Sounds like the software is switching off the immersion at 59.5c and as it's not reaching the desired 60c, it continues with the cycle waiting to reach 60c, which never comes, and times out after the 2 hours.
I wonder if we are the only Ecodans with this problem?
Install 13 April 2024 - 4 Bedroom Brick Detached - Heat Loss 9,281w, Design 45c at -2 - Ecodan 11.2kw R32 - 25L Buffer - 250L Telford Tempest HP DHW - All 16 radiators replaced - Auto Adapt - Mel-Pump app - Octopus Cosy Fixed
10 March 2026 - now 2 x Sigenstor 10 batteries with 8kw Inverter
@richard24738 My next L cycle is tomorrow conveniently, I'll try to keep an eye on it to see what it does.
Mitsubishi Ecodan 8.5kW
4.4kW Solar PV
5.2 kWh Battery Storage
1983 build, 300mm loft insulation, cavity wall insulation (beads)
I lowered the temp to 60 (the lowest it will go) for today's cycle. It got to 58 in the expected amount of time, then the element went off and came on after a while, did a bit more and went off again and again it hit the end of the 2 hour window.
I called Mitsubishi and the tech logged in to have a look at it. He seems to think that it may be either the immersion element or some faulty wiring causing the problem. He recommended getting an accredited installer out to look at it rather than Mitsubishi (wait times and £292 fee).
He also said that they normally set it to come on in the early morning, which I might as well do now that the Sun (significant PV power) is gone until Spring. Probably the 10pm to midnight Cosy slot as we don't have the heating on then.
Speaking of which, I asked why we can't have the heating on when the ASHP switches to the immersion element in the L cycle and he said that it's just how their systems are set up unfortunately.
I'll tag @transparent too as there is some cross over with the other thread we've been using.
Mitsubishi Ecodan 8.5kW
4.4kW Solar PV
5.2 kWh Battery Storage
1983 build, 300mm loft insulation, cavity wall insulation (beads)
@trbob I went down the Mitsi Engineer route unfortunately with the fee.
Report has just come in to say that the immersion had "irregular figures when carrying out Ohm check" so essentially saying faulty immersion heater.
Install 13 April 2024 - 4 Bedroom Brick Detached - Heat Loss 9,281w, Design 45c at -2 - Ecodan 11.2kw R32 - 25L Buffer - 250L Telford Tempest HP DHW - All 16 radiators replaced - Auto Adapt - Mel-Pump app - Octopus Cosy Fixed
10 March 2026 - now 2 x Sigenstor 10 batteries with 8kw Inverter
Posted by: @richard24738"irregular figures when carrying out Ohm check" so essentially saying faulty immersion heater.
Eh?
It's just a coil of wire.
How the heck do you get 'irregular figures"?
Check what I said here about Richard's heater being rated by the manufacturer at 3000watts at 240v and 2700watts at 230v
I realise it's actually being driven by an AC waveform, but a quick rule of thumb indicates:
3000 watts of power divided by 240v gives us 12½ Amps [Power in watts = volts x amps]
240v divided by 12½ Amps gives us a (DC) resistance of 19.2 Ω [R=V/I]
So if I disconnected the immersion heater from the mains, and put a meter across the Live & Neutral terminals I'd expect to see a reading around 20-ohms-ish.
Bear in mind that this test is being done on a heater whilst it's cold, and that the resistance is likely to be lower when hot.
The two other possible readings are:
Zero ohms if it's a short-circuit, in which case the fuse/trip should've blown
100,000 Ω or more which is typical of an open circuit when the wire coil is broken
Does 'irregular' mean that none of those three options was encountered?
If so, then why can't a £300 engineer's inspection provide you with the figure? 🤔
Save energy... recycle electrons!
-
Mitsubishi Ecodan not good enough ?
2 weeks ago
-
Struggling to get CoP above 3 with 6 kw Ecodan ASHP
4 weeks ago
-
Mitsubishi Ecodan circulation pump running.
1 month ago
-
Ecodan Auto Adapt Options
1 month ago
-
Ecodan heat pump leak
1 month ago
- 26 Forums
- 2,618 Topics
- 61.1 K Posts
- 922 Online
- 6,993 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Indevolt Batteries UK Support & Info Thread
Thanks @editor , @indevolt-uk Subject to any comments ...
By JamesPa , 7 hours ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
@seoras Sorry to hear that. I found Vaillant very help...
By JamesPa , 8 hours ago
-
The Watchdog That Watched and Waited
On 9 January 2026, Consumer Energy Solutions collapsed ...
By Mars , 11 hours ago
-
RE: GSHP Kaput After 16 Years: New Compressor or Switch to ASHP? Advice Welcome
Cool Energy in Grimsby sell ground source heat pumps an...
By DerekDeLeon , 12 hours ago
-
RE: Valliant Heat Pump Settings
Thats arguably a sign of a good installer - they unders...
By JamesPa , 13 hours ago
-
RE: Electricity price predictions
Well, we have so many cases where rain water mixes with...
By Batpred , 14 hours ago
-
RE: Two heating zones to one zone
@profzarkov They arent obviously wrong, but the only...
By JamesPa , 16 hours ago
-
RE: Towns water feed to air source heat pump system
The DHW circuit cant be separated (well it could, you c...
By JamesPa , 16 hours ago
-
Solis AC-coupled 3kW storage inverter
Solis AC-coupled 3kW storage inverterPylontech batterie...
By MartinRobinson , 22 hours ago
-
RE: My NIBE ASHP Nightmare: No Commissioning, High Bills and a Hostile Installer
As @transparent has observed above, this is not bad, an...
By cathodeRay , 23 hours ago
-
RE: The Grid Says Yes.. Until It Doesn’t: Why Britain's Net Zero Push is Stalling at the Plug Socket
As I was reading this article Mars, I was thinking that...
By Toodles , 2 days ago
-
RE: Tell us about your Solar (PV) setup
Installed in May 2011: 16*Sharp 245 W monocrystalline p...
By txmartyn , 2 days ago
-
-
RE: Say hello and introduce yourself
That doesn't sound 'right' to me. The national Smart ...
By Transparent , 3 days ago
-
RE: Growatt battery disconnected
I doubt this will happen, but I will try and suggest it...
By Eliuccio , 3 days ago
-
Understood. That's why I decided from the outset on a ...
By JamesPa , 3 days ago
-
RE: My experience with 3 heat pump surveys: Heat Geek, British Gas & Octopus
On the litigation, I would not go there and definitely ...
By Batpred , 3 days ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
I suppose if your pv inverter packs up, you have a plan...
By Batpred , 4 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Firstly check you are using sound power not sound press...
By JamesPa , 4 days ago
-
That’s the solar up and running, I don’t think it’s the...
By David999 , 4 days ago
-
RE: Seeking ideas / information / commiseration - Pure Drive
I agree with @colinc that you can reuse some of it. A s...
By Batpred , 4 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@toodles Im trying me best to ignore orangeman, I figur...
By Papahuhu , 5 days ago
-
@toodles That’s way better per kWp performance than our...
By Papahuhu , 6 days ago