We have our legionella cycle once a week set at 55deg as we run it midday when our Elec is cheap (cosy tariff) so its at 55deg for several hours.
It runs shortly after our usual DHW cycle which we have set at 48deg and the heatpump takes approx. 1hr to get to 48deg and it then takes the immersion (3kW) a little over 1 hr to go from 48 to 55
I found this graphic from heat geeks useful on deciding my temperature.
“Anything worth doing, is worth doing right.”
I think the clue to this problem is in the first post here from @richard24738
He has a 250-litre tank...
... and is presumably running a milking parlour!
The specific heat capacity of water is 4,200 joules per kilogram per degree Celsius (J/kg°C)
The energy required to raise 250l by 10°C (from 50 to 60°C) is therefore 4200 x 250 x 10 which equals 10,500,000 J
- 1 watt is one joule per second
- 1kW is 1000 joules/sec
- 1kWh is 3,600,000J
10,500,000J / 3,600,000 = just under 3kWh
So a 3kW immersion heater will take an hour to raise the temperature from 50 to 60°C
Either Richard's immersion heater isn't being turned full on during the heating cycle
or else there's a significant heat loss somewhere.
Can someone else please check my maths?
Save energy... recycle electrons!
My Tank is 250L
and looking at the last cycle it took 1hr 10mins to raise the temp 7deg so it looks like your math is not far off maybe we are not getting exact 3kw from the immersion heater.
Edit
Just checked and the last cycle took 3.297 kWh and was 1hr 8mins to be precise.
Looks like my immersion never quite hits 3kW
“Anything worth doing, is worth doing right.”
@transparent Thanks. You have confirmed my belief that when running the immersion it should reach the desired 50 > 60c after 1 hour confirming my gut feeling that 1.5 hours is too long.
@trbob had a similar problem and I have asked how it was resolved.
By the way, it's a Telford Tempest Heat Pump Cylinder and I spoke to them. They were adamant that it's a Mitsubishi software issue.
Install 13 April 2024 - 4 Bedroom Brick Detached - Heat Loss 9,281w, Design 45c at -2 - Ecodan 11.2kw R32 - 25L Buffer - 250L Telford Tempest HP DHW - All 16 radiators replaced - Auto Adapt - Octopus Fixed Rate
@richard24738 Perhaps I need to re-visit mine for a closer inspection, thanks. I would not be surprised at all if there were gremlins in the Mitsubishi software.
Mitsubishi Ecodan 8.5kWh
4.4kW Solar PV
5.2 kWh Battery Storage
1983 build, 300mm loft insulation, cavity wall insulation (beads)
Posted by: @richard24738it's a Telford Tempest Heat Pump Cylinder and I spoke to them. They were adamant that it's a Mitsubishi software issue.
In future, please try to use email rather than phone calls when pursuing 'issues' with manufacturers, suppliers and installers.
The text in an email is clear evidence, timed and dated.
It can be used in the event of a claim made under the Consumer Rights Act.
On the other hand, you can freely make guesses and incorrect assumptions here on the Forum.
If you get the maths wrong, it doesn't matter because someone else can step in and correct it.
Try to imagine this topic rather like a conversation in a pub, where everyone is able to chip in with what they think.
If I were in your house, I'd be doing a couple of test investigations.
For example:
1: What happens if I disconnect the supply to the immersion heater from the Mitsubishi controller, and instead use a 13A mains socket to power it?
Does it then operate at the specified 3kW rating and heat the water faster?
2: Whilst the mains is off, undo the cover of the immersion heater and have a look at the wiring.
There should be two thermostats in series, one of which is usually adjustable.
The live wire then goes to the heating element.
But what if your particular model has two elements in parallel, each rated 1.5kW?
If only one is functional, then that would account for the symptoms you're reporting here.
Save energy... recycle electrons!
@transparent Thank you for your comments.
Unfortunately what you suggest I do is beyond my technical abilities so I will have to wait for the installer/mitsubishi.
Install 13 April 2024 - 4 Bedroom Brick Detached - Heat Loss 9,281w, Design 45c at -2 - Ecodan 11.2kw R32 - 25L Buffer - 250L Telford Tempest HP DHW - All 16 radiators replaced - Auto Adapt - Octopus Fixed Rate
That's fine @richard24738
We always try to leave technical suggestions like mine in topics.
Others will soon come across this discussion, and some might have the tools and experience to try what I've posted.
This is very much a shared investigation.
Not everyone here can attempt everything; we pool the knowledge.
Perhaps, however, there's a model number on the end of your immersion heater which you could post here.
There are different versions of the Thermowatt.
I can then look it up and see what its specification is.
Save energy... recycle electrons!
@transparent the details on the plate are:
000003402550 RT IH IN1 14/RTS-ERP A 3KW 240V
Install 13 April 2024 - 4 Bedroom Brick Detached - Heat Loss 9,281w, Design 45c at -2 - Ecodan 11.2kw R32 - 25L Buffer - 250L Telford Tempest HP DHW - All 16 radiators replaced - Auto Adapt - Octopus Fixed Rate
Thanks Richard. That's the detail we need.
Here's what I've found.
RT IH IN1 14 tells us that you have an immersion heater with a 1¾-inch threaded flange.
There's a single heating element within an Incoloy metal outer sleeve.
The sleeve is doubled over to present a length of 14-inches (350mm) within the tank.
The element is rated 3kW for a supply voltage of 240v AC.
If you have only 230v, then it operates at 2.7kW.
The thermostat component is the higher-quality version of the usual RTS.
It is certified to the ErP Standard which requires both the live and neutral to disconnect in the event of over-temperature.
One of the two internal thermostatic disconnectors is adjustable for different temperatures.
Possibly your installer hasn't set that thermostat to at least 60°C.
Thus it could be switching off before reaching the target temperature.
The Mitsubishi software might be able to detect that, but I don't know.
Someone else with an Ecodan is better placed to comment on that.
... and now you see the benefit of posting model numbers here 😀
Save energy... recycle electrons!
I managed to partially keep an eye on mine today for it's cycle (200L tank btw);
13:27 Tank temp 49.5°C ASHP goes off
3kW load in addition to baseline
13:40 Tank temp 52.5°C
13:58 Tank temp 55.5°C
14:20 Tank temp 59.5°C (I was out and unable to manually verify this one, so it's taken from the MEL Cloud app graph which is not great).
Just checked my settings on the controller and the target temperature is 61°C for 5 minutes. Once it hit 59.5°C the element stops drawing power, but I'm pretty sure that the program continues running until 15:00, preventing the heating from coming on.
Not needed today, but when it gets cooler it is annoying, even more so, because surely the heating should be made available anyway as the ASHP is not doing anything when the element in the tank takes over right?
Mitsubishi Ecodan 8.5kWh
4.4kW Solar PV
5.2 kWh Battery Storage
1983 build, 300mm loft insulation, cavity wall insulation (beads)
@trbob Very interesting.
It took round about an hour for your immersion to get from 49.5 to 59.5. Probably acceptable
It looks like the Mitsi software switched the immersion off at 59.5 instead of going on to your set 61 degrees for 5 minutes and simply waited to time out at 2 hours.
Yes, annoying as it doesn't release back to heating and I think a bit more worrying in that you haven't really been running your full legionnaire cycle at all!
Something is definately wrong with the software. It's not just my Ecodan.
Thanks for following up.
Install 13 April 2024 - 4 Bedroom Brick Detached - Heat Loss 9,281w, Design 45c at -2 - Ecodan 11.2kw R32 - 25L Buffer - 250L Telford Tempest HP DHW - All 16 radiators replaced - Auto Adapt - Octopus Fixed Rate
- 21 Forums
- 1,962 Topics
- 42.6 K Posts
- 69 Online
- 2,275 Members
Join Us!
Heat Pump Dramas?
Thinking about installing a heat pump but unsure where to start? Already have one but it’s not performing as expected? Or are you locked in a frustrating dispute with an installer or manufacturer? We’re here to help.
✅ Pre-Installation Planning
✅ Post-Installation Troubleshooting
✅ Performance Optimisation
✅ Complaint Support (Manufacturer & Installer)
Latest Posts
-
RE: What is the best strategy for operating a very oversized heat pump?
@jamespa Samsung has it 'Quiet mode' and I use it a ...
By IRMartini , 1 minute ago
-
RE: Setback savings - fact or fiction?
We certainly are, and that's why I am here too. But tha...
By cathodeRay , 8 minutes ago
-
RE: Newbie out of her depth – Samsung AE120RXYDEG 12kW heat pump
No need for apologies, just cautioning about getting to...
By JamesPa , 14 minutes ago
-
RE: Samsung Gen 7 R290 12kW is not behaving how I expected
Definitely its in the 20xx FSVs. Conversely it may be...
By JamesPa , 16 minutes ago
-
RE: Towel rails. An unexpected final hurdle
We have both Normal Rad for heating the room and then a...
By IRMartini , 2 hours ago
-
RE: Heat Pump Sizing & Installation Costs
Perhaps useful to have installed date too? To get conte...
By Tim441 , 4 hours ago
-
RE: SolarPV tables / online calculator
I'd be interested what others find whilst using that we...
By Majordennisbloodnok , 6 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
The debate over buffer tanks in heat pump systems has b...
By Mars , 7 hours ago
-
RE: F.788 Building circuit pump reports internal fault - Vaillant Arotherm
Guess I have to wait for engineer visit. I really hope ...
By jeegnesh , 18 hours ago
-
RE: Act now to defer the UK road tax increase on EVs
@majordennisbloodnok Damn right sir. my attempt at iron...
By Jancold , 21 hours ago
-
RE: ASHP and heating issues in new build house
That’s good gives you more capacity. It made me think, ...
By Terry1812 , 22 hours ago
-
RE: Seewet manhole cover within r290 exclusion zone
Thanks! I asked Vaillant, and they say I should be fi...
By dbrb2 , 1 day ago
-
Looking for the Grant Aerona 3 setting to turn off completely at 20 OAT
I'm running my Aerona 3 on WC and the 'warm end of that...
By damonc , 1 day ago
-
RE: Do I just go with the lowest quote for my heat pump?
So after signing in Sept in two weeks the install may s...
By Jancold , 1 day ago
-
RE: Victorian Semi Retrofit / Extension ASHP and UFH Advice
When you are renovating is always a good time, as it ma...
By JamesPa , 1 day ago
-
RE: Just one room not reaching desired temperature
Looks like this issue is now resolved. Aira installed a...
By ChandyKris , 1 day ago
-
There have been several people on the OpenEnergyMonitor...
By RobS , 2 days ago
-
RE: Say hello and introduce yourself
Good point @jamespa But that probably strengthens @ch...
By Transparent , 2 days ago
-
RE: Visit a Heat Pump sessions.
Congratulations @toodles, that's a fantastic result. We...
By Old_Scientist , 2 days ago
Latest Topics
-
Heat Pump Sizing & Installation Costs
By Mars 6 hours ago
-
Volumisers in Heat Pump Systems: Does Placement Matter?
By Mars 7 hours ago
-
SolarPV tables / online calculator
By MichelleC 14 hours ago
-
By Toodles 2 days ago