Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
We have our legionella cycle once a week set at 55deg as we run it midday when our Elec is cheap (cosy tariff) so its at 55deg for several hours.
It runs shortly after our usual DHW cycle which we have set at 48deg and the heatpump takes approx. 1hr to get to 48deg and it then takes the immersion (3kW) a little over 1 hr to go from 48 to 55
I found this graphic from heat geeks useful on deciding my temperature.
“Anything worth doing, is worth doing right.”
I think the clue to this problem is in the first post here from @richard24738
He has a 250-litre tank...
... and is presumably running a milking parlour!
The specific heat capacity of water is 4,200 joules per kilogram per degree Celsius (J/kg°C)
The energy required to raise 250l by 10°C (from 50 to 60°C) is therefore 4200 x 250 x 10 which equals 10,500,000 J
- 1 watt is one joule per second
- 1kW is 1000 joules/sec
- 1kWh is 3,600,000J
10,500,000J / 3,600,000 = just under 3kWh
So a 3kW immersion heater will take an hour to raise the temperature from 50 to 60°C
Either Richard's immersion heater isn't being turned full on during the heating cycle
or else there's a significant heat loss somewhere.
Can someone else please check my maths?
Save energy... recycle electrons!
My Tank is 250L
and looking at the last cycle it took 1hr 10mins to raise the temp 7deg so it looks like your math is not far off maybe we are not getting exact 3kw from the immersion heater.
Edit
Just checked and the last cycle took 3.297 kWh and was 1hr 8mins to be precise.
Looks like my immersion never quite hits 3kW
“Anything worth doing, is worth doing right.”
@transparent Thanks. You have confirmed my belief that when running the immersion it should reach the desired 50 > 60c after 1 hour confirming my gut feeling that 1.5 hours is too long.
@trbob had a similar problem and I have asked how it was resolved.
By the way, it's a Telford Tempest Heat Pump Cylinder and I spoke to them. They were adamant that it's a Mitsubishi software issue.
Install 13 April 2024 - 4 Bedroom Brick Detached - Heat Loss 9,281w, Design 45c at -2 - Ecodan 11.2kw R32 - 25L Buffer - 250L Telford Tempest HP DHW - All 16 radiators replaced - Auto Adapt - Mel-Pump app - Octopus Cosy Fixed
10 March 2026 - now 2 x Sigenstor 10 batteries with 8kw Inverter
@richard24738 Perhaps I need to re-visit mine for a closer inspection, thanks. I would not be surprised at all if there were gremlins in the Mitsubishi software.
Mitsubishi Ecodan 8.5kW
4.4kW Solar PV
5.2 kWh Battery Storage
1983 build, 300mm loft insulation, cavity wall insulation (beads)
Posted by: @richard24738it's a Telford Tempest Heat Pump Cylinder and I spoke to them. They were adamant that it's a Mitsubishi software issue.
In future, please try to use email rather than phone calls when pursuing 'issues' with manufacturers, suppliers and installers.
The text in an email is clear evidence, timed and dated.
It can be used in the event of a claim made under the Consumer Rights Act.
On the other hand, you can freely make guesses and incorrect assumptions here on the Forum.
If you get the maths wrong, it doesn't matter because someone else can step in and correct it.
Try to imagine this topic rather like a conversation in a pub, where everyone is able to chip in with what they think.
If I were in your house, I'd be doing a couple of test investigations.
For example:
1: What happens if I disconnect the supply to the immersion heater from the Mitsubishi controller, and instead use a 13A mains socket to power it?
Does it then operate at the specified 3kW rating and heat the water faster?
2: Whilst the mains is off, undo the cover of the immersion heater and have a look at the wiring.
There should be two thermostats in series, one of which is usually adjustable.
The live wire then goes to the heating element.
But what if your particular model has two elements in parallel, each rated 1.5kW?
If only one is functional, then that would account for the symptoms you're reporting here.
Save energy... recycle electrons!
@transparent Thank you for your comments.
Unfortunately what you suggest I do is beyond my technical abilities so I will have to wait for the installer/mitsubishi.
Install 13 April 2024 - 4 Bedroom Brick Detached - Heat Loss 9,281w, Design 45c at -2 - Ecodan 11.2kw R32 - 25L Buffer - 250L Telford Tempest HP DHW - All 16 radiators replaced - Auto Adapt - Mel-Pump app - Octopus Cosy Fixed
10 March 2026 - now 2 x Sigenstor 10 batteries with 8kw Inverter
That's fine @richard24738
We always try to leave technical suggestions like mine in topics.
Others will soon come across this discussion, and some might have the tools and experience to try what I've posted.
This is very much a shared investigation.
Not everyone here can attempt everything; we pool the knowledge.
Perhaps, however, there's a model number on the end of your immersion heater which you could post here.
There are different versions of the Thermowatt.
I can then look it up and see what its specification is.
Save energy... recycle electrons!
Install 13 April 2024 - 4 Bedroom Brick Detached - Heat Loss 9,281w, Design 45c at -2 - Ecodan 11.2kw R32 - 25L Buffer - 250L Telford Tempest HP DHW - All 16 radiators replaced - Auto Adapt - Mel-Pump app - Octopus Cosy Fixed
10 March 2026 - now 2 x Sigenstor 10 batteries with 8kw Inverter
Thanks Richard. That's the detail we need.
Here's what I've found.
RT IH IN1 14 tells us that you have an immersion heater with a 1¾-inch threaded flange.
There's a single heating element within an Incoloy metal outer sleeve.
The sleeve is doubled over to present a length of 14-inches (350mm) within the tank.
The element is rated 3kW for a supply voltage of 240v AC.
If you have only 230v, then it operates at 2.7kW.
The thermostat component is the higher-quality version of the usual RTS.
It is certified to the ErP Standard which requires both the live and neutral to disconnect in the event of over-temperature.
One of the two internal thermostatic disconnectors is adjustable for different temperatures.
Possibly your installer hasn't set that thermostat to at least 60°C.
Thus it could be switching off before reaching the target temperature.
The Mitsubishi software might be able to detect that, but I don't know.
Someone else with an Ecodan is better placed to comment on that.
... and now you see the benefit of posting model numbers here 😀
Save energy... recycle electrons!
I managed to partially keep an eye on mine today for it's cycle (200L tank btw);
13:27 Tank temp 49.5°C ASHP goes off
3kW load in addition to baseline
13:40 Tank temp 52.5°C
13:58 Tank temp 55.5°C
14:20 Tank temp 59.5°C (I was out and unable to manually verify this one, so it's taken from the MEL Cloud app graph which is not great).
Just checked my settings on the controller and the target temperature is 61°C for 5 minutes. Once it hit 59.5°C the element stops drawing power, but I'm pretty sure that the program continues running until 15:00, preventing the heating from coming on.
Not needed today, but when it gets cooler it is annoying, even more so, because surely the heating should be made available anyway as the ASHP is not doing anything when the element in the tank takes over right?
Mitsubishi Ecodan 8.5kW
4.4kW Solar PV
5.2 kWh Battery Storage
1983 build, 300mm loft insulation, cavity wall insulation (beads)
@trbob Very interesting.
It took round about an hour for your immersion to get from 49.5 to 59.5. Probably acceptable
It looks like the Mitsi software switched the immersion off at 59.5 instead of going on to your set 61 degrees for 5 minutes and simply waited to time out at 2 hours.
Yes, annoying as it doesn't release back to heating and I think a bit more worrying in that you haven't really been running your full legionnaire cycle at all!
Something is definately wrong with the software. It's not just my Ecodan.
Thanks for following up.
Install 13 April 2024 - 4 Bedroom Brick Detached - Heat Loss 9,281w, Design 45c at -2 - Ecodan 11.2kw R32 - 25L Buffer - 250L Telford Tempest HP DHW - All 16 radiators replaced - Auto Adapt - Mel-Pump app - Octopus Cosy Fixed
10 March 2026 - now 2 x Sigenstor 10 batteries with 8kw Inverter
- 26 Forums
- 2,607 Topics
- 60.8 K Posts
- 548 Online
- 6,967 Members
Join Us!
Worth Watching
Latest Posts
-
@batpred frost protection £632 ??? That is taking t...
By MartinRobinson , 21 minutes ago
-
RE: Indevolt Batteries UK Support & Info Thread
@editor Interesting questions. If the answer to either ...
By ChandyKris , 33 minutes ago
-
RE: Renewables & Heat Pumps in the News
@editor, I hear that too. I can confirm that out of ...
By ASHP-BOBBA , 8 hours ago
-
End-of-Life Heat Pumps: How Do You Dispose of an ASHP in the UK?
As many of you know, our Global Energy Systems heat pum...
By Mars , 8 hours ago
-
@derbygraham fully agree with James, and it’d be good t...
By Mars , 9 hours ago
-
RE: Microbore heat pump installs
In principle you are almost certainly right, but in pra...
By JamesPa , 10 hours ago
-
RE: Electricity price predictions
@old_scientist We are a low mileage home, so bulk of ou...
By ChandyKris , 11 hours ago
-
There are just too many unknowns for me to comment on p...
By Transparent , 13 hours ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
@toodles I keep an eye on wholesale prices and energy m...
By ChandyKris , 13 hours ago
-
RE: Brand and installer questions for ASHP
Strange, perhaps it doesnt use modbus which the third p...
By JamesPa , 15 hours ago
-
RE: Upgrading my system, how far do I go?
For comparison, my PW3 with 11.04kW inverter, will char...
By Old_Scientist , 18 hours ago
-
RE: Changes to Tesla Powerwall Charging Regime?
Elon gate - legendary! I take my hat off to you @toodle...
By Old_Scientist , 21 hours ago
-
RE: Mitsubishi Ecodan not good enough ?
Thanks @goody, appreciate the feedback and sorry you ha...
By marcexec , 1 day ago
-
RE: Minimum and Zero Disrupt Heat Pump Installations
True (first sentence) Thats the reason to consider th...
By JamesPa , 2 days ago
-
RE: High air source heat pump running costs – Vaillant AroTherm Plus
Quite right. I was using a rough guesstimate of doublin...
By Majordennisbloodnok , 2 days ago
-
RE: My Grant R290 9kW Heat Pump Installation
Again, really don't know how accurate this is! &nb...
By petch , 2 days ago
-
RE: MCS Quality Audit – Has Anyone Had One? Did It Lead to Remediation?
@toodles The whole scheme is a shocking waste of money....
By Papahuhu , 2 days ago
-
RE: Anyone concerned about GivEnergy?
Many thanks for your, and the subsequent, answers tk qu...
By KevH , 3 days ago
-
RE: DIY or Don’t Touch? Solarman Smart Meter Install
Yes, and these guys would probably be my preferred inst...
By Batpred , 3 days ago
-
RE: Hot water tank lose heat rapidly on random days
@jamespa Hopefully their reasons are well intended! ...
By Bash , 3 days ago
-
RE: Ecoflow UK Support & Info Thread
As mentioned above, we’ve got our full review of the Ec...
By Mars , 3 days ago
-
RE: Say hello and introduce yourself
@sonosppp welcome to the forums. I see you've posted in...
By Mars , 4 days ago
-
RE: Guidance with installing a new heating system
@bobflux Great, thanks for the advice. The pipe has an ...
By Hamilton , 4 days ago
-
RE: Daikin Altherma 3 LT compressor longevity question
@optimistic-optimiser I have has a Daikin for a few yea...
By madsid , 4 days ago
-
RE: UK DIY Battery: SEPLOS 48V 200Ah x2 + Sunsynk 8K – Safe Installation for Garage Conversion
The rule of thumb is to ensure that you can isolate any...
By Transparent , 4 days ago