Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
What Air-to-Air (Air conditioning) system do you have and how efficient is it on heating and cooling
We have two single-split Daikin Comfora A2A systems these are a 2.5 kW unit upstairs in the main bedroom and 3.5 kW unit downstairs in the lounge. The house is a 4-bed 1970's detached, about 150 sqm ,with a lot of retrofit insulation.
The A2A units have been in place for just over 1 year now. Over the heating season, we used the downstairs unit to add heat on cheap rate overnight electricity and both units on the "indoor quiet" setting to add some extra heat during the day, mainly running our solar PV output. This was enough on its own on many autumn and spring days, and was supplemented by our gas boiler in the depths of winter, when we only used the A2A overnight.
Overall efficiency on heating was 5800 kWh of heat delivered for 1110 kWh of electricity consumed for an efficiency of 5.2.
On cooling over the 5 heat waves so far in 2026, we got 600 kWh of cooling (heat ejected from the house) for 64 kWh of electricity used for a efficiency of 9.3
On heating our average cost per kWh of heat delivered was under 2p, so far cheaper than gas. (Note this includes both cheap rate overnight electricity consumed from the grid and lost solar PV export at 12p per unit).
Overall, we are very pleased with our A2A system. The two units do a very good job of cooling both upstairs and downstairs, with an extra fan employed occasionally to push cool air around to other rooms. It is very nice to have the house at 24C when it is 34C for hours on end outside! The excellent efficiency on heating was an added bonus, but has turned out to be when we make the most use of the system.
Rob
@rob-of-york welcome to the forums.
Solid numbers. A seasonal heating figure of 5.2 is impressive enough, but what I like is that you’re not pretending the system exists in isolation. You’re using cheap rate electricity, solar when it’s there and the gas boiler when conditions make that sensible.
The cooling side is interesting too. 64kWh of electricity across five heatwaves to keep the house around 24C when it’s 34 outside sounds like a very small price to pay for the comfort.
What I’d be interested to know is how evenly those two units heat the house in winter. With one upstairs and one downstairs do the more remote rooms still stay reasonably comfortable, or are you mainly heating the core of the house and letting the boiler pick up the rest?
Also, how are you measuring the 5,800kWh of heat delivered? Is that coming from the Daikin app?
Really useful first post.
🔥 Britain’s Heat Pump Shitshow
How Installing a Heating System Became a National Nervous Breakdown
Free UK shipping.
Rewritten and updated for 2027
📘 From Zero to Heat Pump Hero
🛠️ Bodge Buster
New to heat pumps?
Take the Heat Pump Fundamentals course and use INTRO50 at checkout for 50% off.
@Mars Good questions!
The downstairs unit did the majority of the heating in winter, as this was overnight taking advantage of cheap rate electricity, and we didn't want to run the upstairs unit in our bedroom while sleeping. So 4800 kWh from the downstairs unit and 1000 kWh from the upstairs one. The heat dispersed reasonably well with the downstairs doors all open and also the upstairs ones to rooms not in use.
The situation was reversed in summer, with the downstairs unit contributing 220 kWh of cooling and the upstairs one 380 kWh. They were typically both run at the same time during the day, but of course heat rises, so the upstairs unit had more work to do.
In autumn and spring, there was enough heat transfer around the house to even out temperatures well enough to not need to use the gas central heating at all. However, on cold days in winter, this wasn't the case and we needed to switch to using gas central heating during the day. The drop in room temperatures was a lot better though than when we had no supplementary heating overnight and the boiler switched off.
Measures of heat delivered and electricity used are from the Daikin app, so subject to the vagaries that may entail.
Rob
- 27 Forums
- 2,767 Topics
- 65.2 K Posts
- 1,766 Online
- 7,169 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Who's your electricity provider and what's your tariff?
Switch to Cosy 12 month fixed initiated - just waiting ...
By Old_Scientist , 5 hours ago
-
RE: Next steps on my ASHP journey: Radiators and Pipework
If you have a flowmeter and two temperature probes, the...
By bobflux , 6 hours ago
-
RE: Is it the house or the equipment?
@springswood Gas connection / disconnection is the re...
By Rob of York , 7 hours ago
-
RE: Starting Our Heat Pump Journey: 1962 build 3 bed detached house
@ian-s One interesting difference between your two q...
By Rob of York , 11 hours ago
-
RE: Siting of the external sensor on a heatpump
@jamespa Absolutely. Even if the same mistake was mad...
By Batpred , 13 hours ago
-
-
RE: Recommendations in Ely (Cambs) area for Full setup checks on Nibe HP setup for House.
In fairness all heating has cost a lot to run in recent...
By JamesPa , 1 day ago
-
RE: Navigating the World of Refrigerants In Heat Pumps: A Guide for Homeowners
Indeed we are invvestigating AC at present and are havi...
By Toodles , 3 days ago
-
No, but the heat pump must be capable of delivering a S...
By JamesPa , 3 days ago
-
RE: Daikin ESPAltherma and Home Assistant installation
It's laziness lol The PV system is very chatty, meter...
By bobflux , 3 days ago
-
RE: Problems with sizing a replacement for a Viessmann Vitocal 200-S
R (The R Project for Statistical Computing, I use it wi...
By cathodeRay , 3 days ago
-
RE: Vaillant Arotherm Plus 7KW need a service on it
booked it with Vaillant. will use them until i can find...
By AdamK , 4 days ago
-
RE: Adventures in heat loss calculations
I have seen it stated that the declared calorific value...
By JamesPa , 4 days ago
-
RE: Two heating zones to one zone
@transparent Many thanks. The garage is fairly well ...
By Profzarkov , 5 days ago