[Solved] Help needed with Grant Aerona 3 issues
Posted by: @fleurculesIt was sitting at 35 for a bit, now up to 36. Although oddly the rads have just gone from feeling about as warm as they ever do to feeling noticeably colder.
OK well so far as I can see there are now only three possibilities
1. The heat pump is unable to get up to the set temperature because of a fault
2. The heat pump is unable to get up to the set temperature because too much energy is being dissipated even though there is no fault.
3. The heat is unable to get up to the set temperature because something else is stopping it even though there is no fault and its not dissipating a load of energy. However I can see what condition would caused this.
In case (2) then something (eg the house) would be getting pretty warm with perhaps 14kW flowing into it. In case (3) you would at least expect it to cycle.
You could check return temp and flow rate in the UI to calculate how much heat the heat pump is generating, and electrical power consumption to check how that corresponds. This would unequivocally differentiate the cases above.
I would say 95% probability there is a fault with the unit itself. I would do those final checks (when its running obviously), summarise and approach your installer/Grant to fix. Im surprised the A1 error isnt constant unless there is in fact another internal fault as yet unrevealed.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Ok think I'm done tinkering, have gone back to WC mode. Under fixed temp settings the highest it got to was 36, then dropped back to 35/34.
@jamespa thanks for all of your help so far!
Edit: just seen your most recent reply. Energy consumption is pretty much steady at around 2kW whenever it's on (only higher if e.g. the kettle is on, occasionally drops lower).
Posted by: @fleurculesOk think I'm done tinkering, have gone back to WC mode. Under fixed temp settings the highest it got to was 36, then dropped back to 35/34.
@jamespa thanks for all of your help so far!
Edit: just seen your most recent reply. Energy consumption is pretty much steady at around 2kW whenever it's on (only higher if e.g. the kettle is on, occasionally drops lower).
Noted. Its a pity you didnt capture the flow rate and return temp when it was in fixed FT mode, but you could capture it now or just go for the 95% case that there is a fault (unless of course Im missing something!) and get Grant in.
Assuming you do do that don't let the engineer tell you its working until he/she has demonstrated operation at 55C or thereabouts, ie sufficient to heat DHW! Good luck!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
First time posting so bear with me. Some bits that have helped me with my bodged grant install. Note that I haven’t necessarily correlated this with your issues so please pick and choose and YMMV
1. Balance your heating emitters. For my money this does not get spoken about enough, insane how much this can benefit your system for free. This includes any UFH that was running on reactive controls (room thermostats).
2. The unit you have has a pump that has three speeds set by dip switches inside the external unit. This means the oft repeated 5 degree dt does not necessarily apply. The unit can probably modulate to about 25% output. You want roughly 2 degree dt at this point and 8 degree dt when it’s outputting at its max. I note you have seen the flow does not get high enough, I wonder what your dt was at that point. Perhaps a useful experiment might be to set your flow to 45 as before and check your dt when it seems to “stall” if this is above or at 8, maybe up your pump speed.
3. As mentioned before do inflate your thermostat temp way past the desired point, salus thermostats do have TPI by default which means that it will turn itself off and on without you noticing.
4. Advanced, consider running a wire to the modbus ports on the outside unit. I have done this and there is a helpful guide on the web which i will try and find if you are happy to do some tinkering. This, mapped into home assistant, will give you all the data about what your heat pump is doing that you should need.
Sorry about your experience with grant. I’d be minded to get a general heat pump installers opinion as the issue is likely the install and not the unit themselves which are actually quite capable.
The units are rebadged Chofu units from Japan which is a well regarded company shipping to quite a few countries i believe.
@adamp thanks. I've now spoken to someone from Grant and they are going to send someone out to replace the discharge temperature sensor. He seemed confident this would fix my issues and is also likely the cause of the A1 error code. Fingers crossed!!
@fleurcules thats great news. My advice is to make sure he demonstrates high temperature operation and if you can note the cop when he does it (difficult I know for a short run). Then he cant easily leave saying 'its fixed' if, in fact, its something other than the sensor!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Just to update the thread, I now have a new heat pump!! The Grant engineer came last Monday, and found that there wasn't enough gas in the system so likely a leak. I'm away on a work trip but my husband was then left without any heating for a week, but luckily we were able to demonstrate that the previous owners had serviced it so Grant came today and fitted a new one. Hopefully that's the last of the issues!
@fleurcules thanks for posting an update and I’m glad you were able to get to the bottom of it.
On a semi-related note, I’ve been genuinely surprised by the number of comments we’ve had on our YouTube channel (and a few on the forums as well) this winter from homeowners reporting heat pump failures that, on investigation, turned out to be refrigerant loss. That’s interesting, because both installers and manufacturers consistently tell me that refrigerant leaks are extremely rare.
It does rather underline why the industry is pushing towards refrigerants like R290 with a much lower global warming potential… if leaks do happen, the consequences are at least far less severe.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
@editor We come across about 4 leaks per year on sealed heat pump systems out of about 200 we see. This is why the service must be carried out by an F Gas engineer so it can be leak checked. As for R290 if installed poorly without adequate ventilation the damage caused to the environment is zero until it maybe it ignites, then it could be catastrophic. Generally though leaks are rare and nothing that escapes would ever compare to the damage by air travel or another rocket to the moon!
-
New Installation - Grant Aerona 3 + 210L Hot Water Cylinder
2 years ago
-
Another ASHP Performance Thread - 13kW Grant Aerona
2 years ago
-
Grant Aerona 3 Help programing
2 years ago
- 27 Forums
- 2,520 Topics
- 58.6 K Posts
- 565 Online
- 6,800 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Peak Energy Products V therm 16kW unit heat pump not reaching flow temperature
ASHPs do have a minimum compressor speed. The minimum h...
By bobflux , 9 hours ago
-
RE: Electricity price predictions
@jamespa And it seems some of the nasty public cloud...
By Batpred , 9 hours ago
-
@bobflux My apologies, they somehow were removed in ...
By Ubert767 , 9 hours ago
-
RE: Tell us about your Solar (PV) setup
Location: near Lyon, France 12kWp on the roof, 2x Sol...
By bobflux , 9 hours ago
-
RE: Jokes and fun posts about heat pumps and renewables
Technology is rapidly advancing. BBC News reported th...
By Transparent , 12 hours ago
-
What matters for flow and pressure drop is internal dia...
By bobflux , 13 hours ago
-
RE: Do Fridges and Freezers have COP ratings?
@editor Thank you all for your replies and submitted in...
By Toodles , 15 hours ago
-
I know and yes. The secondary deltaT wont necessaril...
By JamesPa , 19 hours ago
-
RE: Designing heating system with air to water heat pump in France, near Lyon
Just love the way you put it! 🤣
By Batpred , 1 day ago
-
RE: Safety update; RCBOs supplying inverters or storage batteries
Thank you for sharing. So it seems that your Schneid...
By Batpred , 1 day ago
-
RE: Forum updates, announcements & issues
@upnorthandpersonal thanks for the thoughtful, consider...
By Mars , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@mk4 All 21 panels have their own Enphase IQ7a microinv...
By Toodles , 2 days ago
-
RE: Setback savings - fact or fiction?
Great, so you have proven that MELCloud is consistently...
By RobS , 2 days ago
-
RE: Mitsu PUHZ120Y 'Outdoor Temp 'error?
Thanks David & James It almos...
By DavidAlgarve , 3 days ago
-
RE: Surge protection devices SPDs
@trebor12345 - your original Topic about the right type...
By Transparent , 3 days ago
-
RE: Help needed with Samsung AE120RXYDEG
@tomf I’ve been sent this from a service engineer at Sa...
By Mars , 3 days ago
-
RE: Buying large amp bidirectional RCD and RCBO
Yes... I went through this particular headache and ende...
By bobflux , 3 days ago
-
O-oh! Let's take this as an opportunity to 'pass the ...
By Transparent , 4 days ago
-
RE: Homely setup on daikin heat pump
@craigh I refer to our somewhat elevated temperature of...
By Toodles , 4 days ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
My turn, this describes the future installation, only t...
By bobflux , 4 days ago
-
RE: Say hello and introduce yourself
@liam-dr, I’d like to echo James’ welcome, and we look ...
By Mars , 4 days ago
-
RE: The Hidden Secret to a Successful Heat Pump: Pipe Size Matters
@falesh Hi Falesh, If I were designing your syste...
By Liam DR , 4 days ago