[Solved] Help needed with Grant Aerona 3 issues
Posted by: @fleurculesIt was sitting at 35 for a bit, now up to 36. Although oddly the rads have just gone from feeling about as warm as they ever do to feeling noticeably colder.
OK well so far as I can see there are now only three possibilities
1. The heat pump is unable to get up to the set temperature because of a fault
2. The heat pump is unable to get up to the set temperature because too much energy is being dissipated even though there is no fault.
3. The heat is unable to get up to the set temperature because something else is stopping it even though there is no fault and its not dissipating a load of energy. However I can see what condition would caused this.
In case (2) then something (eg the house) would be getting pretty warm with perhaps 14kW flowing into it. In case (3) you would at least expect it to cycle.
You could check return temp and flow rate in the UI to calculate how much heat the heat pump is generating, and electrical power consumption to check how that corresponds. This would unequivocally differentiate the cases above.
I would say 95% probability there is a fault with the unit itself. I would do those final checks (when its running obviously), summarise and approach your installer/Grant to fix. Im surprised the A1 error isnt constant unless there is in fact another internal fault as yet unrevealed.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Ok think I'm done tinkering, have gone back to WC mode. Under fixed temp settings the highest it got to was 36, then dropped back to 35/34.
@jamespa thanks for all of your help so far!
Edit: just seen your most recent reply. Energy consumption is pretty much steady at around 2kW whenever it's on (only higher if e.g. the kettle is on, occasionally drops lower).
Posted by: @fleurculesOk think I'm done tinkering, have gone back to WC mode. Under fixed temp settings the highest it got to was 36, then dropped back to 35/34.
@jamespa thanks for all of your help so far!
Edit: just seen your most recent reply. Energy consumption is pretty much steady at around 2kW whenever it's on (only higher if e.g. the kettle is on, occasionally drops lower).
Noted. Its a pity you didnt capture the flow rate and return temp when it was in fixed FT mode, but you could capture it now or just go for the 95% case that there is a fault (unless of course Im missing something!) and get Grant in.
Assuming you do do that don't let the engineer tell you its working until he/she has demonstrated operation at 55C or thereabouts, ie sufficient to heat DHW! Good luck!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
First time posting so bear with me. Some bits that have helped me with my bodged grant install. Note that I haven’t necessarily correlated this with your issues so please pick and choose and YMMV
1. Balance your heating emitters. For my money this does not get spoken about enough, insane how much this can benefit your system for free. This includes any UFH that was running on reactive controls (room thermostats).
2. The unit you have has a pump that has three speeds set by dip switches inside the external unit. This means the oft repeated 5 degree dt does not necessarily apply. The unit can probably modulate to about 25% output. You want roughly 2 degree dt at this point and 8 degree dt when it’s outputting at its max. I note you have seen the flow does not get high enough, I wonder what your dt was at that point. Perhaps a useful experiment might be to set your flow to 45 as before and check your dt when it seems to “stall” if this is above or at 8, maybe up your pump speed.
3. As mentioned before do inflate your thermostat temp way past the desired point, salus thermostats do have TPI by default which means that it will turn itself off and on without you noticing.
4. Advanced, consider running a wire to the modbus ports on the outside unit. I have done this and there is a helpful guide on the web which i will try and find if you are happy to do some tinkering. This, mapped into home assistant, will give you all the data about what your heat pump is doing that you should need.
Sorry about your experience with grant. I’d be minded to get a general heat pump installers opinion as the issue is likely the install and not the unit themselves which are actually quite capable.
The units are rebadged Chofu units from Japan which is a well regarded company shipping to quite a few countries i believe.
@adamp thanks. I've now spoken to someone from Grant and they are going to send someone out to replace the discharge temperature sensor. He seemed confident this would fix my issues and is also likely the cause of the A1 error code. Fingers crossed!!
@fleurcules thats great news. My advice is to make sure he demonstrates high temperature operation and if you can note the cop when he does it (difficult I know for a short run). Then he cant easily leave saying 'its fixed' if, in fact, its something other than the sensor!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Just to update the thread, I now have a new heat pump!! The Grant engineer came last Monday, and found that there wasn't enough gas in the system so likely a leak. I'm away on a work trip but my husband was then left without any heating for a week, but luckily we were able to demonstrate that the previous owners had serviced it so Grant came today and fitted a new one. Hopefully that's the last of the issues!
@fleurcules thanks for posting an update and I’m glad you were able to get to the bottom of it.
On a semi-related note, I’ve been genuinely surprised by the number of comments we’ve had on our YouTube channel (and a few on the forums as well) this winter from homeowners reporting heat pump failures that, on investigation, turned out to be refrigerant loss. That’s interesting, because both installers and manufacturers consistently tell me that refrigerant leaks are extremely rare.
It does rather underline why the industry is pushing towards refrigerants like R290 with a much lower global warming potential… if leaks do happen, the consequences are at least far less severe.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
@editor We come across about 4 leaks per year on sealed heat pump systems out of about 200 we see. This is why the service must be carried out by an F Gas engineer so it can be leak checked. As for R290 if installed poorly without adequate ventilation the damage caused to the environment is zero until it maybe it ignites, then it could be catastrophic. Generally though leaks are rare and nothing that escapes would ever compare to the damage by air travel or another rocket to the moon!
-
New Installation - Grant Aerona 3 + 210L Hot Water Cylinder
2 years ago
-
Another ASHP Performance Thread - 13kW Grant Aerona
2 years ago
-
Grant Aerona 3 Help programing
2 years ago
- 27 Forums
- 2,484 Topics
- 57.3 K Posts
- 2,256 Online
- 6,196 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Need help maximising COP of 3.5kW Valiant Aerotherm heat pump
I get the question and what you are trying to do, I wil...
By JamesPa , 7 hours ago
-
@ch_18 downfield is completely correct but you should i...
By Judith , 7 hours ago
-
RE: Vaillant app under reporting flow temperature
No idea then, it's inconceivable that the app and live ...
By JamesPa , 8 hours ago
-
RE: Setback savings - fact or fiction?
That too is true of course, but sometimes we also need ...
By cathodeRay , 9 hours ago
-
RE: Rate the quality of your heat pump design and installation
Pretty awful had new heat pump dead on arrival followed...
By Keithb , 11 hours ago
-
Importance of choosing right installer
I had issues with my Bosch 2000awf installation from da...
By Keithb , 11 hours ago
-
RE: Hoped for improvements not being realised on my Mitsubishi heat pump
@smsm1 Thanks for your interest. At the time that I l...
By DavidAlgarve , 12 hours ago
-
RE: The Hidden Secret to a Successful Heat Pump: Pipe Size Matters
Dear Mars, Thanks for writing this postI'm trying to g...
By Alex , 13 hours ago
-
RE: Help…my NIBE heat pump has faulted again!
Thanks for the pictures, they tell quite a story but no...
By JamesPa , 13 hours ago
-
@majordennisbloodnok Thanks very much, that's cleared t...
By Boycey , 13 hours ago
-
RE: Brine pump error message on Thermia 8kW ground source heat pump system
@schanna I've DM'd you the details. Please click in the...
By Mars , 14 hours ago
-
If you want to find your own activity on the forums, re...
By Mars , 14 hours ago
-
RE: Warranty Repairs- An Un Eddi fying experience!
@bornagain Those staff redundancies were possibly linke...
By Toodles , 18 hours ago
-
RE: Midea ASHP – how to set weather compensation
Happily reporting back after 2+ weeks of operation: com...
By MK4 , 19 hours ago
-
RE: Help needed to adjust weather compensation on Vaillant air source heat pump
The micro climate effect is only going to matter if, as...
By JamesPa , 19 hours ago
-
RE: Tell us about your Solar (PV) setup
@upnorthandpersonal thank you for sharing details of yo...
By Old_Scientist , 20 hours ago
-
RE: Passiv Smart Thermostat - Help & Forum Support
@petch I’ve not come across anyone yet that’s used thes...
By Mars , 1 day ago
-
RE: A Smarter Smart Controller from Homely?
Yep- already done that....nothing novel as such but som...
By benson , 2 days ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
@swwils Similar here, though it has been very mild. I...
By KevH , 2 days ago
-
RE: Home energy storage & battery register
@toodles thankfully we have a range of tariffs to meet ...
By TechnoGeek , 2 days ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@editor thanks Mars! I'll contact them.
By kevinmc1970 , 2 days ago
-
RE: Noisy Grant Aerona 3 13kW ASHP question
@heymikey thanks for the update and sorry to hear that ...
By Mars , 2 days ago
-
RE: Heat loss calculations and how they work in conjunction with heat pump sizing
@jamiejones85mespa your comments are spot on with my th...
By AgentGeorge , 2 days ago
-
RE: The good, the bad and the not that great – my heat pump installation
Must of knocked a load of crud through when they added ...
By Burtis , 2 days ago
-
@mkz, yes I have other installers... can you please sen...
By Mars , 3 days ago