Grant 13kW Aerona3 - issues getting zones to temp

507 Posts
14 Users
85 Reactions
58.2 K Views
(@crimson)
Honorable Member Member
Joined: 2 years ago
Posts: 273
Topic starter  

In a way I’m glad the water heating shows this up. As least then its not something beyond the plant room, but perhaps having a bigger LLH further exaggerates what was going on before.

Builder said the installer has been radio silent though said he was monitoring house temps over the weekend. Am sure them going down didn’t give him opportunity to say he’d fixed it lol.

Another odd thing. I still get the metallic bang in one of the living rooms on an Eskimo rad. And thats happened during a hot water cycle when the zone is shut. I know that would seem a smaller issue amongst all this, but any ideas what it could be? I think its the non TRV side of the rad…



   
ReplyQuote
(@jamespa)
Illustrious Member Moderator
Joined: 3 years ago
Posts: 3343
 

Posted by: @crimson

Also realised hot water tank was sitting at 35C…

I do run that to the bare min, 1 cycle a day for an hour. If no one has a shower etc, it will sit lowest 44C, so fine for using.

 

probes show 45C on pipework flow into plant room from ASHP into LLH, 34C top left of LLH and 34c just before 2 port valves - heating/water tank.

so no wonder thats struggled.

would seem secondary pump is now buggered

With that drop its clear that very little hot water is getting from the primary into the secondary so either pump problem or piping problem.  Has he plumbed the LLH back to front eg with primary and secondary going in opposite directions.  That would cause all sorts of interesting effects none of which are good. 

It beggars belief that the installer didn't check this before he left.  Id be tempted to lock the door next time!

 

 


This post was modified 1 hour ago by JamesPa

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
(@crimson)
Honorable Member Member
Joined: 2 years ago
Posts: 273
Topic starter  
IMG 1279

Posted by: @jamespa

Posted by: @crimson

Also realised hot water tank was sitting at 35C…

I do run that to the bare min, 1 cycle a day for an hour. If no one has a shower etc, it will sit lowest 44C, so fine for using.

 

probes show 45C on pipework flow into plant room from ASHP into LLH, 34C top left of LLH and 34c just before 2 port valves - heating/water tank.

so no wonder thats struggled.

would seem secondary pump is now buggered

With that drop its clear that very little hot water is getting from the primary into the secondary so either pump problem or piping problem.  Has he plumbed the LLH back to front eg with primary and secondary going in opposite directions.  That would cause all sorts of interesting effects none of which are good. 

It beggars belief that the installer didn't check this before he left.  Id be tempted to lock the door next time!

 

 

 

This is what the specialist thought but looked at the specs of the tank and it has no baffles which he said would mean you can’t really pipe it wrong. All the labels are on the front, no arrows this time. I tried to get my phone round the back but couldn’t see anything.

I was shocked he left so quickly. Either he realised it was buggered so rather than be there any longer thought he’d chip off or something has ramped down after he left.

He did place the flow probe and probe thats just before the heating zones next to each other. I wonder if he thought the one just before zones was actually the return and was happy that there was a lovely delta and not however something  completely wrong lol. I thought I was going a bit mad when saw them next to each other but theyre definately on the pipe work that runs above the 3 zone valves and just under the hot water valve so they can’t be a return.

Let me know if I am bonkers though have attached a photo. However the black probe temp is very close in temp to another that’s top left of the LLH (so the flow after the LLW).

 

 

 

 

 


This post was modified 47 minutes ago by Crimson

   
ReplyQuote