Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Heat pump size advice – is 16kW overkill for this property?
Im looking for some second opinions to confirm what I think about a Thermal Earth installation in a neighbours house. I just want to be sure that the mainstream of thinking is the same as mine.
Thermal Earth did a heat loss report (not shared with owner) which predicted a 5835W loss. The owner then told them she might at some point in the future convert a garage space of 30 m2. They have subsequently fitted a 16kW Acond heat pump.
Their argument was that the extra heating requirement tipped it over their original choice so they went for the next one up.They havent said yet what their original choice of unit was, but it would have been an Acond. I estimate that the 30m2 space built to regs would add at most an extra 1200W giving a total of 7035W loss.
Does anyone else think that it is outrageous and inappropriate to fit a 16 kW model? Her usage for the last week was 255 kWh and she prefers her house cool.
Thanks in advance
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
What's the square footage of your neighbour's house?
The other alarm bell is why the heat loss report wasn't shared with the homeowner. If they've hired and paid them, they're entitled to that report. They should demand it.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
@editor Sometimes, things can be even better; Octopus Energy’s Plumber and their Electrician spent three hours each assessing our property for a heat pump installation and shared their thoughts, reservations, suggestions on how to maximise siting and routing of pipes etc., provided us with the Heat Loss Calculation (verbally anyway) without any charge whatsoever, (They are our energy suppliers but there was no obligation involved for this survey). As it happened at that time, as they were the new boys on the block (early 2022), they were unable to provide an installation matching our desires due to using a narrow set of formulations and they did say that in due course, they would be widening the scope of installations. Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
Here is the report size. I made her ask for it once I got involved, they said they usually provide it after installation!
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@kev-m well I guess it would be nearer to 120m2 after the possible extension, but by my calculation still twice what is required.
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody holy ***t batman, yes! 16kw unit for a 5.8kw heat loss? even with a bit of growth room for an extension, thats bonkers.
I just had a look at the Acond range, there are two units. The N is rated at 1.5-7 kw. The R is rated at 3-16. Don't know at what temps, or how accurate the "plate rating" numbers are, not found that level of detail yet.
If the installer really felt that that brands "small" wasn't enough then surely the professionally appropriate thing to do would be to look at and discuss with customer alternative brands that have a more "medium" unit? Not just stick in the "large" because they have a deal with that brand?
Additional thought whilst getting coffee - we have "design conditions" weather right now. If the system is installed and running, it should be possible by looking at the systems stats to derive the house's actual heat loss in design conditions.
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
@iancalderbank That mirrors my feelings Ian. Unfortunately the owner has not been given a manual yet or even instructed how to turn off the heating. Its costing her £10-15 a day at the moment compared to my £5-7 a day in a similar sized worse insulated property just down the road, and I like it a lot warmer than she does.
The company want her internet installed to monitor it from there end but this is proving problematic in her property. I haven't been able to get an answer as to whether it can be controlled just from the controller unit or if it is an internet function via an app.
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Posted by: @bontwoody@kev-m well I guess it would be nearer to 120m2 after the possible extension, but by my calculation still twice what is required.
do you think excessive enough to hit the not fit for purpose clause in the sale of goods act?
I'm not sure about the relevant consumer law. It might be hard to prove it's not fit for purpose if it's able to heat the property and especially if it can modulate down to 3kW. An undersized system would be easier to prove. Also, if it complies with MCS I would think it would be deemed fit for purpose.
However, I don't think a twice oversized ASHP need cost twice as much to deliver the same amount of heat as the correctly sized one (as suggested by your own figures) so maybe it's the way it is set up and used?
Posted by: @bontwoody@iancalderbank That mirrors my feelings Ian. Unfortunately the owner has not been given a manual yet or even instructed how to turn off the heating. Its costing her £10-15 a day at the moment compared to my £5-7 a day in a similar sized worse insulated property just down the road, and I like it a lot warmer than she does.
The company want her internet installed to monitor it from there end but this is proving problematic in her property. I haven't been able to get an answer as to whether it can be controlled just from the controller unit or if it is an internet function via an app.
Has the controller been correctly optimised?
I always find posts and cases like this very disconcerting. Our floorspace is around 380m2 and we have an 18kW ASHP which is probably the right size for the entire property. This nonsense about heat pumps scaling down is such mumbo jumbo in my opinion, because there have been times when I've shut off half the house (UFH and rads) and there's very no drop off in electricity consumption.
@bontwoody, I don't think there's much of a case for it hitting any thresholds under the "fit for purpose clause in the sale of goods act?". I've looked into this when we ran into issues with our Samsung fridge (which is 10000% not fit for purpose), there's an awful lot of subjectivity involved in the definition of what is and isn't "fit". I have, however, been researching the complaints process of badly installed heat pumps and will now be adding incorrectly sized heat pumps to my research.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
- 26 Forums
- 2,607 Topics
- 60.8 K Posts
- 82 Online
- 6,967 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Renewables & Heat Pumps in the News
@editor, I hear that too. I can confirm that out of ...
By ASHP-BOBBA , 54 minutes ago
-
End-of-Life Heat Pumps: How Do You Dispose of an ASHP in the UK?
As many of you know, our Global Energy Systems heat pum...
By Mars , 1 hour ago
-
@derbygraham fully agree with James, and it’d be good t...
By Mars , 1 hour ago
-
RE: Indevolt Batteries UK Support & Info Thread
Finally got around to installing and setting up the Sol...
By Mars , 1 hour ago
-
Unfortunately its a function of the physics. Max heat ...
By JamesPa , 3 hours ago
-
RE: Microbore heat pump installs
In principle you are almost certainly right, but in pra...
By JamesPa , 3 hours ago
-
RE: Electricity price predictions
@old_scientist We are a low mileage home, so bulk of ou...
By ChandyKris , 4 hours ago
-
There are just too many unknowns for me to comment on p...
By Transparent , 6 hours ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
@toodles I keep an eye on wholesale prices and energy m...
By ChandyKris , 6 hours ago
-
RE: Brand and installer questions for ASHP
Strange, perhaps it doesnt use modbus which the third p...
By JamesPa , 8 hours ago
-
RE: Upgrading my system, how far do I go?
For comparison, my PW3 with 11.04kW inverter, will char...
By Old_Scientist , 11 hours ago
-
RE: Changes to Tesla Powerwall Charging Regime?
Elon gate - legendary! I take my hat off to you @toodle...
By Old_Scientist , 14 hours ago
-
RE: Mitsubishi Ecodan not good enough ?
Thanks @goody, appreciate the feedback and sorry you ha...
By marcexec , 1 day ago
-
RE: Minimum and Zero Disrupt Heat Pump Installations
True (first sentence) Thats the reason to consider th...
By JamesPa , 1 day ago
-
RE: High air source heat pump running costs – Vaillant AroTherm Plus
Quite right. I was using a rough guesstimate of doublin...
By Majordennisbloodnok , 2 days ago
-
RE: My Grant R290 9kW Heat Pump Installation
Again, really don't know how accurate this is! &nb...
By petch , 2 days ago
-
RE: MCS Quality Audit – Has Anyone Had One? Did It Lead to Remediation?
@toodles The whole scheme is a shocking waste of money....
By Papahuhu , 2 days ago
-
RE: Anyone concerned about GivEnergy?
Many thanks for your, and the subsequent, answers tk qu...
By KevH , 2 days ago
-
RE: DIY or Don’t Touch? Solarman Smart Meter Install
Yes, and these guys would probably be my preferred inst...
By Batpred , 2 days ago
-
RE: Hot water tank lose heat rapidly on random days
@jamespa Hopefully their reasons are well intended! ...
By Bash , 2 days ago
-
RE: Ecoflow UK Support & Info Thread
As mentioned above, we’ve got our full review of the Ec...
By Mars , 3 days ago
-
RE: Say hello and introduce yourself
@sonosppp welcome to the forums. I see you've posted in...
By Mars , 3 days ago
-
RE: Guidance with installing a new heating system
@bobflux Great, thanks for the advice. The pipe has an ...
By Hamilton , 4 days ago
-
RE: Daikin Altherma 3 LT compressor longevity question
@optimistic-optimiser I have has a Daikin for a few yea...
By madsid , 4 days ago
-
RE: UK DIY Battery: SEPLOS 48V 200Ah x2 + Sunsynk 8K – Safe Installation for Garage Conversion
The rule of thumb is to ensure that you can isolate any...
By Transparent , 4 days ago