@crimson That 50 litres of water in the buffer tank, has this been plumbed as the LLH was? Were it plumbed as a two port volumiser, then the loss of space in your airing cupboard / utility area or whatever might be a sacrifice worth making as it would certainly provide the extra volume of water your system may have lacked. Well insulated, it might be a worthwhile move. Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
Hi @toodles , hope you're keeping well!
It's been plumbed in as a 4 port LLH/volumiser combination. Much to my annoyance when the specialist wanted it to be a 2 port volumiser just on the return to aid with system volume.
However installers stuck with Grant's requirement with their install pack to have a LLH. The installer today said he always uses the 5L/other small ones and never had issues. What's frustrating here is had they actually came and spent time investigating (like I kept asking them to and the builder to) - they may have spotted the pump in the Grant being faulty (and sooner!).
What I'm concerned with now is, a) pump replace - great if that works, but b) now have 50L LLH which could itself cause mixing etc.
@crimson ☹️ I feel it is time the manufacturers came to their senses and listened to sense concerning LLH v Buffer v Volumiser. In the Q&A presentation that @editor put together, the only indication of any LLH or Buffer Tank benefit did not make it to the presentation as not one invitee would speak up in their favour yet manufacturers still appear to be exercising rear-end protection measures by insisting on their use. Regrets, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
Posted by: @crimson@jamespa be very interested to know your thoughts on this.
A 6L LLH replaced with a 50L one…could that cause more issues?
I'll hopefully have the pump on the Grant ASHP replaced tomorrow, he mentioned they should have just hit a 2:30pm cut off that Grant stated for it to be sent out at 3pm and arrive to installers tomorrow.
Turns out I do have a defrost valve by the Grant ASHP too.………(think different people attending from the installers hasn't helped matters).
I think it's unlikely it will make things worse.
The pump issue is yet another example where a buffer not only degrades performance but also obscures faults. Without the buffer and auxiliary pump there would have been no flow at all which is easily detected
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaPosted by: @crimson@jamespa be very interested to know your thoughts on this.
A 6L LLH replaced with a 50L one…could that cause more issues?
I'll hopefully have the pump on the Grant ASHP replaced tomorrow, he mentioned they should have just hit a 2:30pm cut off that Grant stated for it to be sent out at 3pm and arrive to installers tomorrow.
Turns out I do have a defrost valve by the Grant ASHP too.………(think different people attending from the installers hasn't helped matters).
I think it's unlikely it will make things worse.
That's good to hear.
I truly hope this 10 minute replace of the pump will do the job and I can sign off this project and move on!
Posted by: @crimsonI'm off in December, and may invest in some kind of heat gun where it's quick and easy to see deltas across rads, and balance the rads again
Definitely worth getting numbers. It's generally differences that matter so a cheap amazon probe is fine as long as you use tge same one consistently strapped and preferably covered with insulation. You need to measure when something is happening, ie it's heating, preferably when the problem is evident as well as when it isn't.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaPosted by: @crimson@jamespa be very interested to know your thoughts on this.
A 6L LLH replaced with a 50L one…could that cause more issues?
I'll hopefully have the pump on the Grant ASHP replaced tomorrow, he mentioned they should have just hit a 2:30pm cut off that Grant stated for it to be sent out at 3pm and arrive to installers tomorrow.
Turns out I do have a defrost valve by the Grant ASHP too.………(think different people attending from the installers hasn't helped matters).
I think it's unlikely it will make things worse.
The pump issue is yet another example where a buffer not only degrades performance but also obscures faults. Without the buffer and auxiliary pump there would have been no flow at all which is easily detected
Oh completely, he even said without the hydraulic break either a secondary pump would have taken over or it just would have obviously not been running. Just madness.
The manual flow setter being blacked out with gunk I guess also hasn't helped (he said he doesn't like manual ones - so why have one in?!!??).
Shortly installer is coming to replace the offending pump &/or the pcb controller (can't remember the term).
1 living room sitting at 19.8C according to a temp heat miser panel. One of my probes shows 18.7C. On my list once project complete to configure the heatmiser panels to be -1C as I think the power in them gives them a higher temp than actual.
This is at Grant's default WC with max flow down 5C: 40C max at -3C, 30C min at 20C.
Lets see…
…and it's not the water pump, ramped up to 28l/min - 30l/min, then quite soon after dropped to 20l/min.
Thankfully Grant had the sense to also send an entire replacement PCB, which he seems to be on the phone to them to say can he go ahead and replace that as pump not fixed it.
Dying with anticipation to see the heating just sodding well work!
@Crimon, but the Grant Aerona R32 range has fixed speed pumps with 1,2 or 3 configurable speeds? Coupled with the previously blackened flow setter you mentioned, has anyone isolated the outdoor unit, disconnected the flexible primary hoses, checked and reverse flow power flushed the condenser plate heat exchanger and seen if a load of black gunk is blasted out? The primary circulating pumps are not known [in my experience] to give any issues. Grant Technical's blunderbuss default response is often 'replace the entire PCB', usually out of ignorance, lack of technical competency (on site and/or remote), to correctly diagnose root cause issues. A replacement PCB and new pump won't fix a blockage or restriction on the primary hydronic circuit however. The amount of Grant owners who have had new PCBs is remarkable. That said, they may have upgraded firmware or control burned into them, I dunno...
Posted by: @allyfish@Crimon, but the Grant Aerona R32 range has fixed speed pumps with 1,2 or 3 configurable speeds? Coupled with the previously blackened flow setter you mentioned, has anyone isolated the outdoor unit, disconnected the flexible primary hoses, checked and reverse flow power flushed the condenser plate heat exchanger and seen if a load of black gunk is blasted out? The primary circulating pumps are not known [in my experience] to give any issues. Grant Technical's blunderbuss default response is often 'replace the entire PCB', usually out of ignorance, lack of technical competency (on site and/or remote), to correctly diagnose root cause issues. A replacement PCB and new pump won't fix a blockage or restriction on the primary hydronic circuit however. The amount of Grant owners who have had new PCBs is remarkable. That said, they may have upgraded firmware or control burned into them, I dunno...
No idea, they may have done that when did the 50L install, but didn't mention it.
He was saying the primary circulating pump (one bottom right?) - the new one is definitely working better as could barely hear the other one with the panel off and the flow would never get up for long, showed me photos of flow setting not getting past 20l/min. Bizarrely Grant supplied one with too short a lead, so had to swap that too to the old one (seriously wish didn't have a Grant…).
So now he's telling me the replacement pump has in fact worked. He's seen it stick to 30l/min on a heating cycle and not seen a short cycle. Mind you he arrived 1:45, and left at 3pm, so not sure how accurate this is…
…and is "happy" everything should be fine. So didn't need to do the PCB replacement. I believe he called Grant and they changed some settings, confirmed Grant pump 2/3 speed and plant room 2/3 speed (flow temps haven't been touched I can see).
To be reconvened in a week or so (colder snap) coming up.
Never know what to think, but will see the proof of the pudding if the room that's always stuck colder hits a decent temp.
At the moment the ASHP I'm having to run hot water for an hour as other half of course has decided needs a shower ASAP (when knew this was happening today). So I won't really know until 5pm the effect of this.
Am away tonight until Sunday night. Sunday night I'll go through all the Grant settings to check everything bar the flow being 40 instead of 45C, matches the defaults case he's tried adjusting the delta cut off or something random to mask stuff…
- 27 Forums
- 2,475 Topics
- 56.9 K Posts
- 238 Online
- 6,165 Members
Join Us!
Worth Watching
Latest Posts
-
RE: If a heat pump can only heat DHW to 50C then what? Issue with 18KW Heliotherm heat pump
Hi, Nothing yet. I've asked customer to measure flow...
By errmm , 4 hours ago
-
RE: High Temp Heat Pumps for fast warm-up of house
I don't know exactly how long it takes to heat up (and ...
By JamesPa , 5 hours ago
-
RE: Need help maximising COP of 3.5kW Valiant Aerotherm heat pump
OK. What Im seeing looks fairly normal TBH: 1 start ...
By JamesPa , 6 hours ago
-
RE: Vaillant Tech Support Flagged Low DT: UFH Return Cold, Suspected Zero Flow
@editor thanks for the tips which I will try before cal...
By DavidB , 8 hours ago
-
RE: Daikin 6kw setup with Dixell controller
@jamespa Many thanks for your reply, a very detailed an...
By CraigH , 8 hours ago
-
RE: Exploring the role of alternative clean heating solutions - Government Consultation
Despite reservations, I found some time to respond to t...
By Rusty , 8 hours ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@crankplus, nope, still not, and I've followed up with ...
By Mars , 8 hours ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
@agentgeorge Probably, but temperature change at -10 ha...
By AndrewJ , 9 hours ago
-
RE: External wall insulation - your experience
To be clear, my experience was very positive. The journ...
By Batpred , 11 hours ago
-
@foxesfan Re: ‘Servicing’ as @editor has covered in his...
By Toodles , 11 hours ago
-
RE: A Smarter Smart Controller from Homely?
@benson No idea why mine doesn’t work, all I see on ...
By Papahuhu , 12 hours ago
-
RE: Battery sizing - How low can you go!
It seems I am seeing something similar to what you do, ...
By Batpred , 13 hours ago
-
RE: Gaslighting in the heat pump industry – has anyone else experienced this?
Don’t know if this is relevant to this thread, but my A...
By Gruff2001 , 13 hours ago
-
RE: Bosch CS5800i 5kW - Experience So Far
@majordennisbloodnok While getting Home Assistant runni...
By Steelbadger , 1 day ago
-
RE: MCS - BS EN 12831-1:2017 – Heat Loss Survey
Since May 2025 it no longer a requirement in England to...
By JamesPa , 1 day ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Forum Handel @jancold Manufacturer: Daikin Model: E...
By Jancold , 1 day ago
-
RE: Octopus Cosy 12 Heat Pump Regret: Incredibly Loud, Poor Heating & Constant Hum - Help!
@harriworld it was roughly 3am for an hour as that’s ...
By L2jad , 1 day ago
-
RE: Hoped for improvements not being realised on my Mitsubishi heat pump
I have been wondering that myself. The fact is that, ...
By JamesPa , 1 day ago
-
RE: Filtering Tap Water – Share Your Setup for Cleaner, Better-Tasting Water
I remember when I was in my early 20s I was introduced ...
By Majordennisbloodnok , 1 day ago
-
RE: Setback savings - fact or fiction?
But if it is recorded an an integer, which it seems it ...
By cathodeRay , 2 days ago