Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!

Ecodan UD 0-0 error

14 Posts
4 Users
2 Reactions
2,177 Views
 Gary
(@gary)
Reputable Member Member
Joined: 3 years ago
Posts: 350
Topic starter  

Hi all

Anyone ever had a UD0-0 error on a Mitsubishi Ecodan.  Google wasn’t very helpful.  It’s doing it intermittently and shutting off the heat pump.



   
Quote
SUNandAIR
(@sunandair)
Honorable Member Member
Joined: 3 years ago
Posts: 568
 

Hi Gary, haven’t seen full numbers on your error code but UD appears to be an overheat protection code. 

You could also do an Info request… like the flow rate enquiry. or, in this case, an error history enquiry. 

Enq code 103 is last error

Enq code 104 is second to last error

Enq code 105 is third to last error 

I don’t know how these enquiries would be displayed.

but hope this helps


This post was modified 10 months ago by SUNandAIR

   
ReplyQuote
 Gary
(@gary)
Reputable Member Member
Joined: 3 years ago
Posts: 350
Topic starter  

Thanks it doesn’t provide anymore info just says UD-0



   
ReplyQuote



Mars
 Mars
(@editor)
Illustrious Member Admin
Joined: 5 years ago
Posts: 4357
 

@gary I’ll ask Mitsubishi for some insights, and hopefully they can provide some clarification. Have you called their support line?


This post was modified 10 months ago by Mars

Get a copy of The Ultimate Guide to Heat Pumps

Subscribe and follow our YouTube channel!


   
ReplyQuote
 Gary
(@gary)
Reputable Member Member
Joined: 3 years ago
Posts: 350
Topic starter  

@editor thanks Mars just waiting for support to open at 8am



   
👍
1
ReplyQuote
Mars
 Mars
(@editor)
Illustrious Member Admin
Joined: 5 years ago
Posts: 4357
 

@gary after a quick document scan the UD0-0 error suggests a communication error between the outdoor and indoor units, or sometimes between components like the controller and the main PCB. Will be interesting to see if that’s correct and what Mitsubishi have to say.

Agreed that a Google search offers nothing, with this thread being the first search result 😂


Get a copy of The Ultimate Guide to Heat Pumps

Subscribe and follow our YouTube channel!


   
ReplyQuote



 Gary
(@gary)
Reputable Member Member
Joined: 3 years ago
Posts: 350
Topic starter  

@editor I found some info in the service manual it could be a bad condensing temperature or pressure sensor.

It shuts down the heat pump if condensing temperature is over 70C.

Does anyone know what typical condensing temperatures should be?



   
ReplyQuote
Mars
 Mars
(@editor)
Illustrious Member Admin
Joined: 5 years ago
Posts: 4357
 

@gary my Mitsubishi contact recommended you call the support line, and sent me this.

1746541381526

Get a copy of The Ultimate Guide to Heat Pumps

Subscribe and follow our YouTube channel!


   
ReplyQuote
Mars
 Mars
(@editor)
Illustrious Member Admin
Joined: 5 years ago
Posts: 4357
 

As far as I know (and I stand to be corrected) in normal operation, typical condensing temperatures on an ASHP are usually in the 40–60C range, depending on flow temps, load and outdoor conditions. Hitting 70C is high and usually a sign of something going wrong like a faulty sensor, blocked heat exchanger, poor flow or even a stuck valve. 


Get a copy of The Ultimate Guide to Heat Pumps

Subscribe and follow our YouTube channel!


   
ReplyQuote



 Gary
(@gary)
Reputable Member Member
Joined: 3 years ago
Posts: 350
Topic starter  

@editor thanks Mars that’s the same table I found in the service manual it’s does feel like it’s the sensor that’s at fault.  When it stopped it was reading 74C.

I managed to get the heat pump running this morning  at 32C flow temp but the condenser temp was reading 65C so if you are correct this also points to a faulty sensor.

The heat pump has now been off for 3 hours and it’s reading 68C which doesn’t seem likely.



   
👍
1
ReplyQuote
 Gary
(@gary)
Reputable Member Member
Joined: 3 years ago
Posts: 350
Topic starter  

£400 later and it’s fixed it was the T3 sensor that measures the condensed refrigerant temp it should read single figures was reading 65C and occasionally above 70C which is when it trips the error.



   
ReplyQuote
Abernyte
(@abernyte)
Reputable Member Member
Joined: 3 years ago
Posts: 257
 

Gary, might I enquire how old the Ecodan unit is? I am just trying to get a measure on the economics of the Mitsubishi service package, which includes all parts, and the random failure costs. £400 for a fairly minor sensor helps focus the mind!



   