Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Ecodan help with efficiency setup and design - removing manifold mixers, LLH and pumps
thank you that's very good to hear, I will hopefully start the mods at the end of the week all going well.
alongside I plan to rewire so the main FTC display will be the one thermostat its downstairs in the centre of the house and the bedrooms will just act as temperature limiters
@rich I agree with your assessment that your pump is oversized, I have the same unit in a similarly-sized house with a design temp of 50° at -2.5 and I have come to the same conclusion. MCS heat loss assessments are notoriously pessimistic compared to how people find their houses perform, and EPC values are an over-generalised, rushed, stab in the dark. Unfortunately these are the figures that your plumbers supplied to Mitsubishi to get the OK for the system they put in. The SCOP value will assume far more heat is being supplied and probably has no idea of how much baseload all those pumps are drawing.
I slightly disagree with Derek’s statement that running at 33 at 0C is not a matter for concern in that it does show that you don’t need a large heat input at a low OAT but need even less for the vast majority of the time. I certainly find that my 8.5kW unit only runs continuously at 3°C or below, above that it cycles as it can’t modulate down far enough, and it cycled more frequently under WC than it does with AA. Rather than have the lowest flow temp but have pumps running circulating the heat 24 hrs a day, perhaps shorter defined on/off sessions charging the slabs at a higher temperature would work better for you. There are those who only run their HP during low-cost power periods but get enough heat in to last a whole day.
I suppose I should just point out that altering the pipework might well invalidate the Mitsubishi guarantee, if that is important to you. It is probably worth talking to them anyway whatever you do as they do seem to be quite customer friendly.
Mitsubishi EcoDan 8.5 kW ASHP - radiators on a single loop
210l Mitsubishi solar tank
Solar thermal
3.94kW of PV
Thanks for the reply I haven't yet altered the pipework as decided the coldest part of the year is not the best time if anything was to go wrong,
I have to agree with you about the low flow temperatures not working out for efficient running mine suffers terribly and is cycled far to much at anything from about +2c you can see the flow and return temperatures raising as the UFH can not give away any more heat and the heat pump is as low as it can go.
I think moving off weather compensation and having longer off times will work out more cost effective the issue I have at the moment is most of the pumps are not controlled via the FTC removing the pumps and turning the 3 remaining stats for temperature limiters leaving the main FTC as the one main stat goes hand it hand. Trying to rewire the pumps to do that will unfortunately be quite extensive.
In regards to the warranty this is not something I am really bothered about keeping I'm more keen on just having the simplest most efficient design
Time for an update
I had some time the last few days and with the warmer weather decided its now or never.
I'm no plumber but for a first go I am fairly happy, 4 pumps and the low loss header have now been removed.
I have had the system running for a few hours and am please to report monitoring the manifold l/min flow gauges before and after the mods there has been no loss in flow 😀
I did then have to shut the system down as I have a leak that I will have to fix on Friday
moving the dip switches to set up the new one zone I discovered several more errors like the PWM for the pump just being unplugged
going forward I will look at balancing the system (upstairs return is much hotter) and changing my running style to auto adaption.
I've added some pictures
Nice work - my system is almost identical to yours, I look forward to seeing if you get any efficiency benefits.
@rich congratulations. For doing this, and also on having the confidence in yourself to do this in winter. albeit you did check the forecast 😉
My octopus signup link https://share.octopus.energy/ebony-deer-230
210m2 house, Samsung 16kw Gen6 ASHP Self installed: Single circulation loop , PWM modulating pump.
My public ASHP stats: https://heatpumpmonitor.org/system/view?id=45
11.9kWp of PV
41kWh of Battery storage (3x Powerwall 2)
2x BEVs
@rich that is admirable. We’ll done. Looking forward to seeing how the system performs once you’ve balanced the rads.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
morning all,
The system has now been running 24/7 since Friday in weather compensation mode and the house is sat at 21c downstairs 20c upstairs.
so far we seem to have big electric savings I would put most of this down to the removal of all the extra pumps and control rather than heat pump as this still needs better control to get the most out of it.
I have slowed the upstairs flows to match the Delta T of downstairs as you can see the temperatures have become a lot better compared to the original. I am going to aliexpress some more cheap thermometer so I can better balance the system.
I briefly tried Auto adaption but this raised the flow temperature a lot, s this due to my heat pump constantly running around its lowest frequency (possibly oversized) I have used 540 code to see that I am getting a flow rate of 15 this seems ok but possibly a bit low for my heat pump?
today with it 5C outside I am still getting cycling so I am considering trying to schedule stops letting the slab cool slightly before adding more energy in what do you think?
please seen the before and after pictures of temps and flows
Looks good so far. The cycling may be the low flow temps rather than the energy (although they are of course related). Ecodans seem to struggle to maintain LWTs in the low 30s. When I'm running on WC I raise the LWT a bit more than is necessary and let the external stats limit the room temp, which does stop the ASHP periodically.
Thanks yeah I am using the FTC controller as the stat so I am just trailing Advanced Auto Adaption however I have noticed this raises the LWT significantly
Posted by: @richThanks yeah I am using the FTC controller as the stat so I am just trailing Advanced Auto Adaption however I have noticed this raises the LWT significantly
I think auto adaption is best suited to fast response emitters, like rads or fan coils. It is essentially load compensation.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
-
Struggling to get CoP above 3 with 6 kw Ecodan ASHP
1 week ago
-
Mitsubishi Ecodan circulation pump running.
2 weeks ago
-
Ecodan Auto Adapt Options
2 weeks ago
-
Ecodan heat pump leak
3 weeks ago
-
Interpreting MelPump data / cycling?
1 month ago
- 26 Forums
- 2,590 Topics
- 60.3 K Posts
- 288 Online
- 6,922 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
Our Cosy 9 has been in hush mode for three days. So far...
By KevH , 2 hours ago
-
RE: Rate the quality of your heat pump design and installation
I had a Worcester Bosch compress 2000 fitted March 2026...
By Josejo , 3 hours ago
-
RE: Air-to-air heat pumps - best models and installers
Are you creating a whole new category for A2A?
By ASHP-BOBBA , 6 hours ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
There isn’t as far as I know, @djh, but you’re welcome ...
By Majordennisbloodnok , 19 hours ago
-
RE: Can anyone explain the following behaviour with a Grant Aerona 3 R30 / Smart Controller?
Final Update. Yesterday, I was going through the moti...
By Unsure , 20 hours ago
-
RE: How much can an east/west solar solar system be oversized?
Best performance occurs with PV string near inverter no...
By bobflux , 20 hours ago
-
RE: Forum updates, announcements & issues
Thank you Mars for all your dedication to improvements;...
By Toodles , 23 hours ago
-
RE: Who do I complain to about a poor ECO4 installation, can anyone advise?
Take it one step at a time. If you can get the dhw and...
By JamesPa , 1 day ago
-
RE: Selling 2 x Kensa Shoebox 7kw GSHP (New)
Hi Jain, we’ve got an ashp so I’m afraid we won’t be yo...
By Judith , 1 day ago
-
No buffer or low loss header Grant controller in sens...
By JamesPa , 2 days ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
That's an amazing job to get all that in there! A truly...
By Batpred , 2 days ago
-
RE: Anyone concerned about GivEnergy?
Thanks for your advice - I'll keep trying with the inst...
By JohnDwyer , 2 days ago
-
RE: Plug and play solar. Thoughts?
I am also yet to find a case where an installation that...
By Batpred , 2 days ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
This is what I got from OVO. At least it was quick.. ...
By Batpred , 2 days ago
-
RE: IVT greenline HT Plus E - Circulation Pump Constantly On
Welcome to the forums. Irrespective of which brand yo...
By Mars , 3 days ago
-
RE: 7.5kW Heat Loss, But Quoted a 10kW Midea. No Re-Pipe, No Buffer Tank. Does This Add Up?
Oh, how I love these old scientists!I'm in with your 5 ...
By LeJamaisContent , 3 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@jamespa Someone who is not easily phased I suppose.
By Toodles , 3 days ago
-
@downfield Once OE had removed our gas meter and capped...
By Toodles , 3 days ago
-
Living with a Low Loss Header (Or Measure For Measure, it’s All About the Pump)
I know, low loss headers (LLHs) aren’t necessarily ‘low...
By Toodles , 3 days ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
After seeing umpteen negative price slots again today, ...
By ChandyKris , 3 days ago
-
RE: The Reality Behind a Failed Heat Pump Installation – and an IWA Insurance Rejection
@ian-w Getting back to the problem in hand, what do yo...
By JamesPa , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@papahuhu Generally, I leave Homely to take care of mat...
By Toodles , 4 days ago