Ecodan U4 error code
I've cleaned that solder joint up and resoldered it, looks good now. But today no matter what I've tried the machine will not spin up. I've tried wiggling the wires connectors, thermistors on the pipes but nothing! I'm all out of ideas.
I discovered that there are some dip switches (SW2) that can be set on the unit's controller board which will indicate the exact thermistor at fault. In my case it was the water inlet thermistor that was showing a wrong resistance which I missed when I was testing each thermistor for general operation not actual readings.
Part ordered and hopefully that will be it fixed!
@spacebiscuit could you detail what switches you changed maybe useful for someone else in the future thanks
On SW2 switches 1, 4 and 6 need to be on - this will then return a number corresponding to a thermistor. Although in my case it returned '3' which could be one of two. So I then had to try 3,4,5 on which gives the temperature of the inlet - mine was read '102' which is not achievable and so indicates a bad resistance reading and therefore TH32 being the faulty thermistor - I hope!
See pages 74 and 76 here:
Page 55 shows the resistance range for TH32, which could be measured if you have a suitable multimeter. You could also test the circuit board by connecting a suitable resistor in place of the thermistor.
Oh I didn't see that - so I'm getting 300-320 ohms on that thermistor....
- 22 Forums
- 2,057 Topics
- 44.9 K Posts
- 62 Online
- 3,299 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Is Your 6kW Air Source Heat Pump Really a 6kW?
There are various ways to look at things related to CoP...
By Johnmo , 3 hours ago
-
RE: IVT Greenline high pressure switch and electrical cassette errors
@abbote thanks for that advice.There was a bit of air i...
By tdudgeon , 3 hours ago
-
RE: Heat Pump Manufacturers Recommending Buffer Tanks
One manufacturer Viessmann has to have their buffer, as...
By Johnmo , 5 hours ago
-
RE: How To Balance Radiators & the Role of the Lockshield Valve: A Homeowner's Guide
Good luck, I hope it all works out!
By JamesPa , 23 hours ago
-
@johnd it's a difficult one, because we've seen instanc...
By Mars , 1 day ago
-
RE: Is your heat pump insured?
@johnmo sorry it comes across like that. The post is au...
By KevinPotts , 1 day ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
@johnmo Perhaps a little detail might explain my reason...
By Toodles , 1 day ago
-
Win a 6-panel PV courtesy of egg and Renewable Heating Hub
Our epic giveaway just went live! Want to win a 6-pan...
By Mars , 2 days ago
-
RE: Yes, the "zoning with ASHP" topic again...
James, thanks again for your thoughtful and persistent ...
By HarryRea , 2 days ago
-
RE: Is this normal? Click of the DHW returning to space heating
So the Lone Ranger returned today! Even though we thoro...
By Grantmethestrength , 2 days ago
-
RE: Vaillant & OVO partner up to offer Heat Pump Plus
Hopefully iv done the right thing today by signing up t...
By Westkent , 2 days ago
-
RE: Battery sizing - How low can you go!
My own experience with connecting four batteries to thr...
By Transparent , 2 days ago
-
RE: Plate heat exchanger considerations
Work on 2-3 percent per degree. This is a reasonable e...
By JamesPa , 3 days ago
-
RE: Advice for ground source heat pump in new build with PV and batteries
The useful bit is the bit that specifies the heat loss ...
By JamesPa , 3 days ago
-
RE: Volumisers in Heat Pump Systems: Does Placement Matter?
You’re absolutely right that during defrost the refrige...
By Mars , 3 days ago
-
@editor thanks Mars that’s the same table I found in th...
By Gary , 3 days ago
-
RE: Tariff and charging strategy advice please
They haven't asked me to prove that I have an EV (I do)...
By JamesPa , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
Took a while to find on the OFGEN site: ”The FIT sche...
By AgentGeorge , 3 days ago
-
RE: why solar diverters for HW instead of the heat pump?
For me there are few factors why you may want to heat w...
By Johnmo , 3 days ago