Ecodan U4 error code

18 Posts
4 Users
4 Reactions
1,777 Views
(@spacebiscuit)
Eminent Member Member
Joined: 10 months ago
Posts: 11
Topic starter  

I've cleaned that solder joint up and resoldered it, looks good now. But today no matter what I've tried the machine will not spin up. I've tried wiggling the wires connectors, thermistors on the pipes but nothing! I'm all out of ideas.


   
ReplyQuote
(@spacebiscuit)
Eminent Member Member
Joined: 10 months ago
Posts: 11
Topic starter  

I discovered that there are some dip switches (SW2) that can be set on the unit's controller board which will indicate the exact thermistor at fault. In my case it was the water inlet thermistor that was showing a wrong resistance which I missed when I was testing each thermistor for general operation not actual readings.

Part ordered and hopefully that will be it fixed!


   
👍
1
ReplyQuote
 Gary
(@gary)
Prominent Member Member
Joined: 2 years ago
Posts: 336
 

@spacebiscuit could you detail what switches you changed maybe useful for someone else in the future thanks


   
ReplyQuote



(@spacebiscuit)
Eminent Member Member
Joined: 10 months ago
Posts: 11
Topic starter  

On SW2 switches 1, 4 and 6 need to be on - this will then return a number corresponding to a thermistor. Although in my case it returned '3' which could be one of two. So I then had to try 3,4,5 on which gives the temperature of the inlet - mine was read '102' which is not achievable and so indicates a bad resistance reading and therefore TH32 being the faulty thermistor - I hope!

See pages 74 and 76 here:

 

This post was modified 10 months ago by spacebiscuit

   
👍
2
ReplyQuote
(@derek-m)
Illustrious Member Member
Joined: 4 years ago
Posts: 4429
 

@spacebiscuit

Page 55 shows the resistance range for TH32, which could be measured if you have a suitable multimeter. You could also test the circuit board by connecting a suitable resistor in place of the thermistor.


   
ReplyQuote
(@spacebiscuit)
Eminent Member Member
Joined: 10 months ago
Posts: 11
Topic starter  

Oh I didn't see that - so I'm getting 300-320 ohms on that thermistor....


   
ReplyQuote
Page 2 / 2



Share:

Join Us!

Trusted Installers

Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.

✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available

👉 Find your installer now!

Latest Posts

x  Powerful Protection for WordPress, from Shield Security
This Site Is Protected By
Shield Security