Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Ecodan U4 error code
I've cleaned that solder joint up and resoldered it, looks good now. But today no matter what I've tried the machine will not spin up. I've tried wiggling the wires connectors, thermistors on the pipes but nothing! I'm all out of ideas.
I discovered that there are some dip switches (SW2) that can be set on the unit's controller board which will indicate the exact thermistor at fault. In my case it was the water inlet thermistor that was showing a wrong resistance which I missed when I was testing each thermistor for general operation not actual readings.
Part ordered and hopefully that will be it fixed!
@spacebiscuit could you detail what switches you changed maybe useful for someone else in the future thanks
On SW2 switches 1, 4 and 6 need to be on - this will then return a number corresponding to a thermistor. Although in my case it returned '3' which could be one of two. So I then had to try 3,4,5 on which gives the temperature of the inlet - mine was read '102' which is not achievable and so indicates a bad resistance reading and therefore TH32 being the faulty thermistor - I hope!
See pages 74 and 76 here:
Page 55 shows the resistance range for TH32, which could be measured if you have a suitable multimeter. You could also test the circuit board by connecting a suitable resistor in place of the thermistor.
Oh I didn't see that - so I'm getting 300-320 ohms on that thermistor....
- 27 Forums
- 2,772 Topics
- 65.3 K Posts
- 2,325 Online
- 7,174 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Next steps on my ASHP journey: Radiators and Pipework
@jamespa since going back to bed and reading again this...
By Singlespeed , 6 hours ago
-
RE: Recommendations in Ely (Cambs) area for Full setup checks on Nibe HP setup for House.
If they can't don't give up. Heat pumps are, in reali...
By JamesPa , 22 hours ago
-
RE: Starting Our Heat Pump Journey: 1962 build 3 bed detached house
@ian-s I wouldn't be too concerned about the design ...
By Rob of York , 23 hours ago
-
RE: Missing flow temperature in Heat Geek proposal
Yes that's what would happen by turning down the lsv to...
By JamesPa , 23 hours ago
-
RE: Grant R290 DHW Cycle Interuption
It looks like some sort of short pre-run. The question...
By JamesPa , 1 day ago
-
RE: Cascade System or larger single unit
@renewables345 I would say if it a new build it’s no mo...
By Aventus Eco , 1 day ago
-
RE: Why are ASHP installs so expensive?
Posted by: @batpred There´s another aspect that coul...
By Rob of York , 1 day ago
-
RE: Say hello and introduce yourself
@gz00, welcome to the forums. There’s a huge amount of ...
By Mars , 2 days ago
-
RE: Home energy storage & battery register
1 fox ess lv5200 batteries, plus 2 more waiting to be i...
By Jimcub , 2 days ago
-
RE: Heat Pump deployment statistics: June 2026
@l8again Unfortunately the government is, I suspect,...
By JamesPa , 2 days ago
-
My feed of random industrial auctions turned up this au...
By Prunus , 2 days ago
-
Thank you @majordennisbloodnok – that means a lot, part...
By Mars , 3 days ago
-
We’ve just passed 20 million forum views! 🎉
It's official. The Renewable Heating Hub forums have of...
By Mars , 3 days ago
-
RE: Who's your electricity provider and what's your tariff?
@batpred When the raw material input has increased in c...
By Papahuhu , 5 days ago