Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Does legionella cycle also heats up radiators?
Hello. Beginner's question:
I have a system with a ASHP and a hot water tank.
When the legionella cycle (Friday 1pm for 1 hour) kicks in my radiators also heat up. Is this supposed to happen?
I am suspecting the valve that controls where the hot water from the pump goes (diverting to DHW or Heating) is not working well, and DHW is leaking to the radiators.
Welcome to the forums @bbmorales
No, that shouldn’t be happening. It sounds like you’re on the right track with your diagnosis though. During the legionella cycle, only your hot water tank should be heating up, not the radiators. This suggests that the diverter valve may be faulty and allowing hot water to flow into the heating circuit. A photo of the diverter valve would be helpful.
The other question this poses is that I assume your heating is off at the moment and you’re only using your heat pump for hot water production. So why is your system coming on at all and distributing heat to your rads. Does your circulation pump come on when the legionella cycles starts?
🔥 Britain’s Heat Pump Shitshow
How Installing a Heating System Became a National Nervous Breakdown
Free UK shipping.
📗 Heat Pumps Explained
A Jargon-Free Guide for Homeowners
Rewritten and updated for 2027
📘 From Zero to Heat Pump Hero
🛠️ Bodge Buster
New to heat pumps?
Take the Heat Pump Fundamentals course and use INTRO50 at checkout for 50% off.
Hi @editor Mars, many thanks.
Regarding the images, I've uploaded two, hopefully this gives you an idea of the system.
Regarding your other question
"Does your circulation pump come on when the legionella cycles starts? "
Apologies for the question, but where is this pump and how to I verify this?
I have not disabled completely the heating, but I can try doing so next Friday (disable completely the heating, leaving on only DHW).
Thanks for your help!
@bbmorales let's backtrack a little bit. Can you please share more information about the system you have (brand and model of heat pump would be a good starting point)? We'll need to ascertain whether your heating is in fact off.
🔥 Britain’s Heat Pump Shitshow
How Installing a Heating System Became a National Nervous Breakdown
Free UK shipping.
📗 Heat Pumps Explained
A Jargon-Free Guide for Homeowners
Rewritten and updated for 2027
📘 From Zero to Heat Pump Hero
🛠️ Bodge Buster
New to heat pumps?
Take the Heat Pump Fundamentals course and use INTRO50 at checkout for 50% off.
There is no need, imo, to run a legionella cycle as often and it would be better run during the night on cheaper rate electricity. The ASHP heats to 50c and the immersion takes over to 60c. Expensive on day time rate on a weekly basis. Needn’t be for as long as an hour either so far as I know.
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
Faulty 3 port diverter….
Easiest fix is to disable the legionella program.
Off grid on the isle of purbeck
2.4kW solar, 15kWh Seplos Mason, Outback power systems 3kW inverter/charger, solid fuel heating with air/air for shoulder months, 10 acres of heathland/woods.
My wife’s house: 1946 3 bed end of terrace in Somerset, ASHP with rads + UFH, triple glazed, retrofit IWI in troublesome rooms, small rear extension.
@bbmorales it's a personal preference and depends on the likelihood of bacteria proliferating in your tank. We run a Legionella cycle every two weeks. Since we work from home and use hot water frequently, the water in our cylinder is constantly being drained and replaced, preventing stagnation. This routine works for us. However, some homeowners choose to turn it off completely.
🔥 Britain’s Heat Pump Shitshow
How Installing a Heating System Became a National Nervous Breakdown
Free UK shipping.
📗 Heat Pumps Explained
A Jargon-Free Guide for Homeowners
Rewritten and updated for 2027
📘 From Zero to Heat Pump Hero
🛠️ Bodge Buster
New to heat pumps?
Take the Heat Pump Fundamentals course and use INTRO50 at checkout for 50% off.
- 27 Forums
- 2,781 Topics
- 65.6 K Posts
- 1,792 Online
- 7,187 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Tesla Powerwall (2) Calibration Cycles
@toodles when you mentioned there had been an improveme...
By Papahuhu , 11 minutes ago
-
RE: Replacing Storage Heaters with a Heat Pump in a Stone Cottage
That sounds like a better approach (being able to see a...
By cathodeRay , 19 hours ago
-
RE: DIY Heat Pump Installations: Navigating Legal and Regulatory Hurdles
Thanks for the reference @jamespa I can't see any te...
By Transparent , 20 hours ago
-
RE: battery storage without solar
Indeed, current on the grid input = current used for ch...
By bobflux , 21 hours ago
-
RE: Who's your electricity provider and what's your tariff?
@papahuhu @papahuhu A lot of tears and sweat went into ...
By Andris , 24 hours ago
-
RE: Getting closer to a finished Haier system
Very nice! Congratulations. Big MLC looks neat whe...
By bobflux , 1 day ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
We have the same problem, 12 mature trees clip the morn...
By Papahuhu , 2 days ago
-
RE: Solis inverters S6-EH1P: pros and cons and battery options
I had a battery and inverter installed a while ago, my ...
By Batpred , 2 days ago
-
RE: Is This Initial Free Quote From Octopus Trusted Partner Reasonable?
@ltron2 The EPC on our house is A-92, however that i...
By Rob of York , 2 days ago
-
RE: Heat pump branding. Clever, contemporary… or a bit too much?
The layout is confusing - much better like this: We b...
By downfield , 3 days ago
-
RE: Is it just me, or does tradesperson timekeeping and communication drive you absolutely mad?
My experience, backed up by opinions from various frien...
By Majordennisbloodnok , 3 days ago
-
RE: Analysis of the economics of switching to an A2W ASHP compared to other heat sources
I had a meeting today with a company based out of Swede...
By Mars , 4 days ago
-
RE: Review your electricity provider
We were with Octopus in our old house and it was fault...
By ian33a , 4 days ago
-
RE: Estimating true heat loss from twelve months of consumption data
I did, indeed, go with the 12 KW Vaillant unit.  ...
By ian33a , 4 days ago