Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Ecodan U4 error code
I've cleaned that solder joint up and resoldered it, looks good now. But today no matter what I've tried the machine will not spin up. I've tried wiggling the wires connectors, thermistors on the pipes but nothing! I'm all out of ideas.
I discovered that there are some dip switches (SW2) that can be set on the unit's controller board which will indicate the exact thermistor at fault. In my case it was the water inlet thermistor that was showing a wrong resistance which I missed when I was testing each thermistor for general operation not actual readings.
Part ordered and hopefully that will be it fixed!
@spacebiscuit could you detail what switches you changed maybe useful for someone else in the future thanks
On SW2 switches 1, 4 and 6 need to be on - this will then return a number corresponding to a thermistor. Although in my case it returned '3' which could be one of two. So I then had to try 3,4,5 on which gives the temperature of the inlet - mine was read '102' which is not achievable and so indicates a bad resistance reading and therefore TH32 being the faulty thermistor - I hope!
See pages 74 and 76 here:
Page 55 shows the resistance range for TH32, which could be measured if you have a suitable multimeter. You could also test the circuit board by connecting a suitable resistor in place of the thermistor.
Oh I didn't see that - so I'm getting 300-320 ohms on that thermistor....
- 26 Forums
- 2,646 Topics
- 61.8 K Posts
- 740 Online
- 7,045 Members
Join Us!
Latest Posts
-
RE: Heat Pump Overpromising – What Were You Actually Told Before You Bought?
@editor Sorry Mars, I didn’t see a notification about ...
By Toodles , 3 minutes ago
-
RE: Hitachi Heat Pump being replaced with Vaillant
Yes to be configured as a volumiser. The pump is to be...
By trebor12345 , 21 minutes ago
-
RE: Anyone concerned about GivEnergy?
So it seems subscription day has finally arrived for Gi...
By TechnoGeek , 2 hours ago
-
RE: How many people are happy with their ASHP and do you believe them?
I agree, and not. Energy prices are a largely politica...
By JamesPa , 4 hours ago
-
RE: Solar Produced vs Home Consumed
All inverters will use solar power in preference to dra...
By JamesPa , 4 hours ago
-
Yes, you will need to notify them even if the inverter ...
By Old_Scientist , 5 hours ago
-
RE: Heat Pump Manufacturers Recommending Buffer Tanks
@tony-stolz, I think @jamespa has already covered the h...
By Mars , 17 hours ago
-
RE: Heat Pump Operation in Summer - Valliant 7kW
I do the same: cool my large buffer (3000L) to 10C, pum...
By upnorthandpersonal , 1 day ago
-
@editor "The interesting bit is that many modern invert...
By Singlespeed , 1 day ago
-
RE: Ecodan & MelCloud scheduling
With the prospect of warmer weather this week, I brough...
By downfield , 1 day ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
I reached out to MCS directly last week on this and her...
By Mars , 1 day ago
-
RE: Help me keep the faith with my air source heat pump installation
My heating developed a really severe case of noise and ...
By JamesPa , 2 days ago
-
RE: Octopus Cosy 12 Heat Pump Regret: Incredibly Loud, Poor Heating & Constant Hum - Help!
@l2jad I was just thinking all things being equal. Our ...
By AndrewJ , 2 days ago
-
Hi, Does anybody have experience with Heat Geek insta...
By sttpd1917 , 3 days ago