Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Ecodan U4 error code
I've cleaned that solder joint up and resoldered it, looks good now. But today no matter what I've tried the machine will not spin up. I've tried wiggling the wires connectors, thermistors on the pipes but nothing! I'm all out of ideas.
I discovered that there are some dip switches (SW2) that can be set on the unit's controller board which will indicate the exact thermistor at fault. In my case it was the water inlet thermistor that was showing a wrong resistance which I missed when I was testing each thermistor for general operation not actual readings.
Part ordered and hopefully that will be it fixed!
@spacebiscuit could you detail what switches you changed maybe useful for someone else in the future thanks
On SW2 switches 1, 4 and 6 need to be on - this will then return a number corresponding to a thermistor. Although in my case it returned '3' which could be one of two. So I then had to try 3,4,5 on which gives the temperature of the inlet - mine was read '102' which is not achievable and so indicates a bad resistance reading and therefore TH32 being the faulty thermistor - I hope!
See pages 74 and 76 here:
Page 55 shows the resistance range for TH32, which could be measured if you have a suitable multimeter. You could also test the circuit board by connecting a suitable resistor in place of the thermistor.
Oh I didn't see that - so I'm getting 300-320 ohms on that thermistor....
- 26 Forums
- 2,706 Topics
- 63.5 K Posts
- 1,121 Online
- 7,111 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Electricity price predictions
What time are they discharging - during the peak to sup...
By Old_Scientist , 21 minutes ago
-
RE: Indevolt Batteries UK Support & Info Thread
All understood, but if you want it installed 'professio...
By JamesPa , 23 minutes ago
-
If Reform were to win, I suspect that many of the AR7/8...
By Old_Scientist , 29 minutes ago
-
RE: Renewables & Heat Pumps in the News
the Derril Water solar plant? I will cross-post. &n...
By JamesPa , 16 hours ago
-
RE: HeatPump maintenance in Swindon area?
Sorry I can't but ... it sounds like a job any half dec...
By JamesPa , 20 hours ago
-
My contribution is to wonder how your radiators are plu...
By springswood , 1 day ago
-
RE: Powerwall 3 tripping RCDs in powercut
If I were to write a remote diagnostics chart for the P...
By Transparent , 2 days ago
-
RE: GivEnergy inverter tripping due to over-voltage?
possibly interesting to note the latest spreadsheet S...
By Tim441 , 2 days ago
-
RE: Summer heat is becoming the new winter cold in the UK. What are you doing about it?
Our ashp service is booked for a couple of weeks from n...
By Judith , 3 days ago
-
RE: Air Conditioning in Cars - What is this doing for the Climate?
In fairness, my EV has a heat pump in it which is theor...
By Majordennisbloodnok , 3 days ago
-
RE: Can DNO change a G99 export allowance once approved?
Fair enough and mea culpa. I was responding to a comme...
By JamesPa , 3 days ago
-
RE: Two heating zones to one zone
In your case, converting it to a single zone sounds lik...
By sarahstrachan , 4 days ago
-
RE: Consultation on reform of Consumer Protection in the retrofit market
I agree with much of that, but that's a much wider refo...
By JamesPa , 5 days ago