Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Ecodan U4 error code
I've cleaned that solder joint up and resoldered it, looks good now. But today no matter what I've tried the machine will not spin up. I've tried wiggling the wires connectors, thermistors on the pipes but nothing! I'm all out of ideas.
I discovered that there are some dip switches (SW2) that can be set on the unit's controller board which will indicate the exact thermistor at fault. In my case it was the water inlet thermistor that was showing a wrong resistance which I missed when I was testing each thermistor for general operation not actual readings.
Part ordered and hopefully that will be it fixed!
@spacebiscuit could you detail what switches you changed maybe useful for someone else in the future thanks
On SW2 switches 1, 4 and 6 need to be on - this will then return a number corresponding to a thermistor. Although in my case it returned '3' which could be one of two. So I then had to try 3,4,5 on which gives the temperature of the inlet - mine was read '102' which is not achievable and so indicates a bad resistance reading and therefore TH32 being the faulty thermistor - I hope!
See pages 74 and 76 here:
Page 55 shows the resistance range for TH32, which could be measured if you have a suitable multimeter. You could also test the circuit board by connecting a suitable resistor in place of the thermistor.
Oh I didn't see that - so I'm getting 300-320 ohms on that thermistor....
- 27 Forums
- 2,792 Topics
- 65.9 K Posts
- 2,624 Online
- 7,195 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: tepeo ZEB UK Support & Info Thread
Sorry you are correct, I was remembering figures from t...
By JamesPa , 9 minutes ago
-
RE: battery storage without solar
Thanks. The qualifications are multiple, it seems. M...
By Batpred , 2 hours ago
-
Do You Need a Buffer Tank or Low Loss Header for Underfloor Heating in a Large Property?
I have come across someone on another forum who lives i...
By GrahamF , 3 hours ago
-
Fair enough, still worth checking, I suspect muck gets ...
By JamesPa , 7 hours ago
-
RE: Passiv Smart Thermostat - Help & Forum Support
@singlespeed No problem. Here is a list of the tariffs ...
By Will H , 8 hours ago
-
RE: Renewable Heating Hub Homeowners' Q&A Podcast
Our episode with George Clarke and ScottishPower’s Rob ...
By Mars , 8 hours ago
-
RE: Heat Pumps Without Grants: Would You Have Installed One & Will You Now?
I installed during the era of RHI, not BUS so it doesn'...
By Abernyte , 8 hours ago
-
RE: Review your electricity provider
@singlespeed I seem to remember that when I signed up f...
By Toodles , 8 hours ago
-
RE: [Update] Indevolt PowerFlex 3000: UK ENA Listing Status
Hi everyone, We’ve seen a few discussions and inqui...
By Indevolt Tech , 13 hours ago
-
RE: Cooling/heating with one unit
Long term, it may be more cost effective to get an A2A ...
By Rob of York , 16 hours ago
-
RE: Renewables & Heat Pumps in the News
Posted by: @editor I think we should make that approa...
By Rob of York , 2 days ago
-
RE: Does anyone have experience of a smart water meter?
My neighbour received an email from Anglian Water sayin...
By AndrewJ , 2 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
Well the military is well known for going green, isn't ...
By Majordennisbloodnok , 2 days ago
-
RE: Why are ASHP installs so expensive?
I've ripped out over 11kw of storage and panel heaters ...
By Singlespeed , 2 days ago