6 Red Flags to Avoi...
 
Notifications
Clear all

6 Red Flags to Avoid When Considering a Heat Pump Installation

40 Posts
14 Users
28 Reactions
1,683 Views
 GT22
(@gt22)
New Member Member
63 kWhs
Joined: 2 months ago
Posts: 5
 

@johnmo Thank you for providing that clarification.

This post was modified 2 months ago by Mars

   
ReplyQuote
 GT22
(@gt22)
New Member Member
63 kWhs
Joined: 2 months ago
Posts: 5
 

@editor  As requested a couple of photos. Many thanks for the information. It is so helpful to get that sort of clear information.

Sanyo display 20240924 174119


Sanyo landing unit 20240924 174046

 

This post was modified 2 months ago 3 times by Mars

   
👍
1
ReplyQuote
 GT22
(@gt22)
New Member Member
63 kWhs
Joined: 2 months ago
Posts: 5
 

If I had a new ASHP installed I would still have to have a hot water cylinder. I watched the relevant video on this site. But I don't need any buffer unit. 

Can I get clarification on this point. 

Can the ASHP External unit, supply heat for Central Heating radiators or UFH at one temperature and one set of F&R pipes and do that supply directly? Bypassing the cylinder?

Or have I got that completely wrong and need to go away and do some serious reading? 🤔 

This post was modified 2 months ago by GT22

   
ReplyQuote



(@benson)
Estimable Member Member
545 kWhs
Joined: 8 months ago
Posts: 56
 

Nothing like a government grant to bring out the bandits for sure. An absolute minefield and as per my other post our current installation is hardly going smoothly. The company we went with however were one of the few who didn't want a massive amount of money (in effect the whole cost of the job minus the grant) up front, so at least I have some leverage to try and ensure it is completed to a decent standard.
As for optimus heating, came across as knowing their onions but I booked an initial home survey after a fair bit of back and forth communications (mainly telling me how good they were) and after all that they didn't turn up or contact me to tell me they weren't coming. Red flag #7?

This post was modified 2 months ago by Mars

   
👍
1
ReplyQuote
Mars
 Mars
(@editor)
Illustrious Member Admin
22695 kWhs
Veteran
Joined: 4 years ago
Posts: 2722
 

@benson Optimus didn't turn up?

Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb

Subscribe and follow our Homeowners’ Q&A heat pump podcast


   
ReplyQuote
(@benson)
Estimable Member Member
545 kWhs
Joined: 8 months ago
Posts: 56
 

@editor Nope. Made a firm appointment, and they didn't turn up or make any contact. I was slightly miffed.

This post was modified 2 months ago by Mars

   
ReplyQuote
Mars
 Mars
(@editor)
Illustrious Member Admin
22695 kWhs
Veteran
Joined: 4 years ago
Posts: 2722
 

@benson that's very disappointing indeed.

Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb

Subscribe and follow our Homeowners’ Q&A heat pump podcast


   
ReplyQuote
(@jamespa)
Famed Member Moderator
7533 kWhs
Joined: 2 years ago
Posts: 1297
 

Posted by: @gt22

Can the ASHP External unit, supply heat for Central Heating radiators or UFH at one temperature and one set of F&R pipes and do that supply directly? Bypassing the cylinder?

Or have I got that completely wrong and need to go away and do some serious reading? 🤔

ASHPs (and fossil boilers running at a low flow temperature or with weather compensation - rare in UK, common in more enlightened countries) supply at one flow temperature at any one time and thus the installation will invariably include a three way diverter valve (or two two way valves) so that space heating or dhw can be fed, but not at the same time.  The unit switches flow temperature and the diverter valve according to whether space of dhw heating is required.

If you need, in addition, two flow temperatures for space heating you must supply the space heating at the higher temperature and mix down for the lower.  Again same for boilers and ASHPs.  The ASHP COP will be determined by the higher, because that is the temperature it is required to produce.

Hope that clears matters up.


   
👍
1
ReplyQuote
 GT22
(@gt22)
New Member Member
63 kWhs
Joined: 2 months ago
Posts: 5
 

@jamespa Many thanks. You are adding to my education on the current ASHP approach. So different from my 2009 Sanyo configuration, hence my questions.

This post was modified 2 months ago by Mars

   
ReplyQuote



(@jamespa)
Famed Member Moderator
7533 kWhs
Joined: 2 years ago
Posts: 1297
 

Posted by: @gt22

@jamespa Many thanks. You are adding to my education on the current ASHP approach. So different from my 2009 Sanyo configuration, hence my questions.

My ashp journey is only 3 years old and in that time it's clear that thinking has matured quite significantly, albeit by no means universally.  I can only imagine how much change there might have been since 2009.
Please continue to ask questions, people here are very willing to help and no question is silly.
 

This post was modified 2 months ago by Mars

   
👍
1
ReplyQuote
(@Erik Verne)
New Member
Joined: 2 days ago
Posts: 1
 

Great article! You've highlighted essential red flags to watch out for when considering a heat pump installation. One innovative idea would be to include tips on how to verify the credentials of installers, ensuring both quality and reliability in the installation process. Keep up the informative work!

This post was modified 9 hours ago by Mars

   
💥
1
ReplyQuote
(@jamespa)
Famed Member Moderator
7533 kWhs
Joined: 2 years ago
Posts: 1297
 

One innovative idea would be to include tips on how to verify the credentials of installers, ensuring both quality and reliability in the installation process. Keep up the informative work!

@mars That could be a whole discussion in itself.  I don't personally think its simple!

 


   
👍
1
ReplyQuote
Page 3 / 4



Share:

Join Us!

Latest Posts

x  Powerful Protection for WordPress, from Shield Security
This Site Is Protected By
Shield Security