Solis inverters S6-EH1P: pros and cons and battery options

73 Posts
9 Users
4 Reactions
2,897 Views
Transparent
(@transparent)
Illustrious Member Moderator
Joined: 4 years ago
Posts: 2907
 

Posted by: @batpred

Essentially you probably have a shared neutral and three live cables going onto the inverter. Perhaps the inverter produces power evenly on the three phases? 

 

But I think the meter will offset, it so your supplier will charge you 0? So the electrical considerations may not impact the cost side 

 

I am curious if your CT clamp covers three live cables and so three readings of imports are considered?

A domestic 3ph Smart Meter operates in Vector Sum Mode.

If a home with a single-phase solar inverter exports on one phase and imports on the other two, then you are only charged for the difference between the phases.

 

A 3ph Inverter would need to have CT clamps on all 3 phases in order to export to the grid at the levels configured.

However, demand on the phases at the inverter won't be even because it's supplying single-phase in-home appliances.

 

A G98 certified 3ph inverter should import evenly across the three phases.
(I wish that was programmable because I'd like to trial one that has asymmetric current demand!)

 


This post was modified 1 hour ago by Transparent

Save energy... recycle electrons!


   
ReplyQuote