Buying large amp bidirectional RCD and RCBO
@jamespa – fuses and trips must be rated according to the current-carrying capacity of the cable, not calculated on the load(s) you intend to supply.
So if you want to deliver 80A max to the larger CU, then that dictates the cable size and how it can be carried/supported.
Fixing a cable to a solid surface (like a wall) by using clips, will give it a different rating than running the same size cable through conduit.
It affects how much heat can be radiated away into the air.
A professional electrician would look at the building and decide a route and fixing-strategy which has least adverse affect on the current that the cable can carry.
Sometimes he/she will use the 'standard' Twin & Earth cable (6424Y) which is most commonly used in domestic properties,
but there are other circumstances when more current could be passed by running 'singles' (6491X) through a 20mm diameter plastic conduit.
There isn't a 'standard' mains cable size between 16mm² and 25mm².
Let's assume you'd prefer to pay less for the 16mm² cable size:
To achieve 80A capacity using twin&earth it would need to be in free air for its entire length. That would give a rating of 83A.
If 16mm² single-cored wire was pulled through a conduit, then it would be rated 74A – 85A, depending on length and how much free space there was left in the conduit.
So you're asking for something which is close to the limits for that size of copper conductor.
Having an 80A Service Fuse might not be regarded as sufficiently fast protection for that 16mm² cable.
It could still get hot enough to be dangerous without the fuse blowing.
It's likely that an electrician will require a faster-acting MCB to which the cable is connected.
I can't immediately find an 80A MCB on the wholesaler sites I've just looked at.
They may not exist.
But there are 80A RCBOs with 30mA 'earth leakage' protection, with prices around £30.
The transfer switch must be rated at 80A minimum.
In practice you'd probably select one with 100A capability.
The MTS is not going to act as an MCB.
It doesn't 'trip out' if you try to draw more current through it.
Save energy... recycle electrons!
Posted by: @transparent@jamespa – fuses and trips must be rated according to the current-carrying capacity of the cable, not calculated on the load(s) you intend to supply.
So if you want to deliver 80A max to the larger CU, then that dictates the cable size and how it can be carried/supported.
Fixing a cable to a solid surface (like a wall) by using clips, will give it a different rating than running the same size cable through conduit.
It affects how much heat can be radiated away into the air.A professional electrician would look at the building and decide a route and fixing-strategy which has least adverse affect on the current that the cable can carry.
Sometimes he/she will use the 'standard' Twin & Earth cable (6424Y) which is most commonly used in domestic properties,
but there are other circumstances when more current could be passed by running 'singles' (6491X) through a 20mm diameter plastic conduit.There isn't a 'standard' mains cable size between 16mm² and 25mm².
Let's assume you'd prefer to pay less for the 16mm² cable size:
To achieve 80A capacity using twin&earth it would need to be in free air for its entire length. That would give a rating of 83A.
If 16mm² single-cored wire was pulled through a conduit, then it would be rated 74A – 85A, depending on length and how much free space there was left in the conduit.
So you're asking for something which is close to the limits for that size of copper conductor.
Having an 80A Service Fuse might not be regarded as sufficiently fast protection for that 16mm² cable.
It could still get hot enough to be dangerous without the fuse blowing.It's likely that an electrician will require a faster-acting MCB to which the cable is connected.
I can't immediately find an 80A MCB on the wholesaler sites I've just looked at.
They may not exist.But there are 80A RCBOs with 30mA 'earth leakage' protection, with prices around £30.
The transfer switch must be rated at 80A minimum.
In practice you'd probably select one with 100A capability.The MTS is not going to act as an MCB.
It doesn't 'trip out' if you try to draw more current through it.
Thanks, I understand and indeed understood all of that, which is why my original diagram showed thick cable (illustrated by a thick line) from service fuse to MTS and again from MTS to CU, and (at least in my mind) a 100A changeover switch, thus preserving the integrity of the cable and interrupter capacity relative to the (80A service) fuse right up to the point where it enters the CU (diagram reproduced in part below - ignore the question in the call out - that has now been resolved - it is necessary). Your suggestion of a lower rated MTS complicates that relatively simple model, and requires yet another component between the service fuse and what would otherwise be the first point of interruption, in order to preserve the integrity with the lower rated components you suggest using. Its possible of course, but putting another component in the box which must, in practice, be worked on 'live' (I have yet to see an electrician call out the DNO to interrupt the service and reconnect it!) seems like a retrograde step if it can be avoided.
I think the safety parameters are now sufficiently clear (for which many thanks) and the limiting factor is the components that can be purchased from a company that I and the electrician trust, which in the case of a component required to stand 100A, is unlikely to include a one from an unknown Chinese manufacturer advertised on Alibaba or eBay! Given the relatively small choice that I have found so far, that will probably determine the detailed design. There do appear to be 100A transfer switches available from CES or the like, but unfortunately sold in an enclosure that is full already. As the same enclosure ideally needs also to accommodate the two 32A MCBs protecting the inverter, that wont do. I suppose that, in the limit, I could buy the enclosure plus switch and throw away the enclosure, but that feels a bit silly.
Hopefully a more in depth search will turn up a suitable part!
Once I have a final design with available components I will post it again.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaThe main fuse is 80A, I was told to upgrade from 60A before getting an ashp. In retrospect I don't know why. However, given that this is rhe case it seems to me the transfer switch has to be rated at at least 80A as does everything else downstream until MCBs are reached. Of course I could put in 63A MCB immediately prior, but its getting a bit silly tge number of components.
With our 8kw inverter we did not need any MCB over 63A (and that was just because Solis required 36.4*1.25 and we had to round up)...
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
Posted by: @batpredPosted by: @jamespaThe main fuse is 80A, I was told to upgrade from 60A before getting an ashp. In retrospect I don't know why. However, given that this is rhe case it seems to me the transfer switch has to be rated at at least 80A as does everything else downstream until MCBs are reached. Of course I could put in 63A MCB immediately prior, but its getting a bit silly tge number of components.
With our 8kw inverter we did not need any MCB over 63A (and that was just because Solis required 36.4*1.25 and we had to round up)...
I am sure I wont need anything bigger for the inverter, but the grid supply is fused at 80A so any components and cable upstream of the first MCB have got to be rated for 80A or above. The thick lines in the diagram I drew were intended to depict that.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @jamespaPosted by: @batpredPosted by: @jamespaThe main fuse is 80A, I was told to upgrade from 60A before getting an ashp. In retrospect I don't know why. However, given that this is rhe case it seems to me the transfer switch has to be rated at at least 80A as does everything else downstream until MCBs are reached. Of course I could put in 63A MCB immediately prior, but its getting a bit silly tge number of components.
With our 8kw inverter we did not need any MCB over 63A (and that was just because Solis required 36.4*1.25 and we had to round up)...
I am sure I wont need anything bigger for the inverter, but the grid supply is fused at 80A so any components and cable upstream of the first MCB have got to be rated for 80A or above. The thick lines in the diagram I drew were intended to depict that.
The approach in my case was as follows:
- supply is 100amp
- tails (I think 25mm) connect to Henley box
- tails connect from Henley box to CU
- CU has a 63Amp MCB for grid port (as 36.4*1.25 is 45.5 and the cable could take more) . But a 50Amp MCB could have been used instead
- 16mm cable to grid port
- the same CU also has a RCBO of 16amp for sockets, connecting to 2.5mm cable.
The goal is, as I am sure you are aware, just to make sure that each section of cable is protected by an MCB of lower rating than the maximum rating of that cable.
It was decided that the maximum required for the house (excluding EV and a small CU) was 36.4A. This was based on the inverter capacity (but it would be 50 with the same inverter if used with an AC coupled inverter on the smart port). So we no longer consider we could have a 100A supply to the house. Does this approach help?
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
- 27 Forums
- 2,475 Topics
- 56.9 K Posts
- 267 Online
- 6,165 Members
Join Us!
Worth Watching
Latest Posts
-
RE: If a heat pump can only heat DHW to 50C then what? Issue with 18KW Heliotherm heat pump
Hi, Nothing yet. I've asked customer to measure flow...
By errmm , 5 hours ago
-
RE: High Temp Heat Pumps for fast warm-up of house
I don't know exactly how long it takes to heat up (and ...
By JamesPa , 7 hours ago
-
RE: Need help maximising COP of 3.5kW Valiant Aerotherm heat pump
OK. What Im seeing looks fairly normal TBH: 1 start ...
By JamesPa , 7 hours ago
-
RE: Vaillant Tech Support Flagged Low DT: UFH Return Cold, Suspected Zero Flow
@editor thanks for the tips which I will try before cal...
By DavidB , 9 hours ago
-
RE: Daikin 6kw setup with Dixell controller
@jamespa Many thanks for your reply, a very detailed an...
By CraigH , 9 hours ago
-
RE: Exploring the role of alternative clean heating solutions - Government Consultation
Despite reservations, I found some time to respond to t...
By Rusty , 9 hours ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@crankplus, nope, still not, and I've followed up with ...
By Mars , 9 hours ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
@agentgeorge Probably, but temperature change at -10 ha...
By AndrewJ , 10 hours ago
-
RE: External wall insulation - your experience
To be clear, my experience was very positive. The journ...
By Batpred , 12 hours ago
-
@foxesfan Re: ‘Servicing’ as @editor has covered in his...
By Toodles , 12 hours ago
-
RE: A Smarter Smart Controller from Homely?
@benson No idea why mine doesn’t work, all I see on ...
By Papahuhu , 13 hours ago
-
RE: Battery sizing - How low can you go!
It seems I am seeing something similar to what you do, ...
By Batpred , 14 hours ago
-
RE: Gaslighting in the heat pump industry – has anyone else experienced this?
Don’t know if this is relevant to this thread, but my A...
By Gruff2001 , 14 hours ago
-
RE: Bosch CS5800i 5kW - Experience So Far
@majordennisbloodnok While getting Home Assistant runni...
By Steelbadger , 1 day ago
-
RE: MCS - BS EN 12831-1:2017 – Heat Loss Survey
Since May 2025 it no longer a requirement in England to...
By JamesPa , 1 day ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Forum Handel @jancold Manufacturer: Daikin Model: E...
By Jancold , 1 day ago
-
RE: Octopus Cosy 12 Heat Pump Regret: Incredibly Loud, Poor Heating & Constant Hum - Help!
@harriworld it was roughly 3am for an hour as that’s ...
By L2jad , 1 day ago
-
RE: Hoped for improvements not being realised on my Mitsubishi heat pump
I have been wondering that myself. The fact is that, ...
By JamesPa , 1 day ago
-
RE: Filtering Tap Water – Share Your Setup for Cleaner, Better-Tasting Water
I remember when I was in my early 20s I was introduced ...
By Majordennisbloodnok , 2 days ago
-
RE: Setback savings - fact or fiction?
But if it is recorded an an integer, which it seems it ...
By cathodeRay , 2 days ago