My Powerwall 3 Consumes 3-4 kWh/Day in Self-Consumption: Is This Normal?
I had solar panels & Powerwall 3 installed in August 2025 & have been shocked to discover that the battery is self-consuming between 3 & 4 kWh of energy per day. I understand that some of this is ‘round trip’ losses due to conversion losses but I was completely unaware that batteries also have standby / parasitic losses which, in my case amounts to about 2kWh per day.
I have also discovered that the Tesla App adds these battery losses to home use instead of battery so, unless you have separate monitoring, you would be either be completely unaware of the losses or spend an eternity trying to work out why your heat pump is using more energy than previously.
Has anyone else noticed similar losses? If so, were you aware of this ‘running cost’ before you decided to purchase? I was completely unaware (possibly due to stupidity on my part) but feel that it’s an important consideration because it’s a fixed running cost that affects calculations of savings and ROI.
I see that Mars has changed the post title. Not a problem, Mars, but I would like to confirm that Tesla have advised me that the self-consumption I’m experiencing is completely ‘normal’ and is not a fault with my system.
I’m interested to find out whether this self-consumption is typical of all batteries / inverters (Tesla assure me that it is) and also how widespread knowledge of this self-consumption is. I can find no information on data sheets & installers appear unaware or in denial. Food for thought and discussion ……….
Posted by: @caronI see that Mars has changed the post title. Not a problem, Mars, but I would like to confirm that Tesla have advised me that the self-consumption I’m experiencing is completely ‘normal’ and is not a fault with my system.
I’m interested to find out whether this self-consumption is typical of all batteries / inverters (Tesla assure me that it is) and also how widespread knowledge of this self-consumption is. I can find no information on data sheets & installers appear unaware or in denial. Food for thought and discussion ……….
My 3yo 9.5kWh GivEnergy battery imports 9.3kWh from empty and fully discharges 8kWh
Ecodan 6kW, 5.4 kW PV array, 9.6 kWh GivEnergy battery, Bosch induction hob, Zappi 7kW charger, electric car and electric motorbike
@caron, I'm looking into this for you... from my own personal vantage points, 3-4kWh would seem high, but I don't know much about batteries.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
I have done some investigation into this previously, I have 3 data sources - Tesla measurements (instantanious), Tesla App History and also some high level independent monitoring.
Noting that the powerwall 3 datasheet has a reported round-trip efficiency of 89% @ 25C ambient.
If you take my history in the Tesla App battery tab for this month, its reporting 96% efficiency - however in my testing, the "instant" figures within the App and the historical graphs don't align.
For example, the "fast" Charge rate shown at the CT Clamps as "instant" consumption report 5.0kW but compared to the historical data it's only showing 4.8kW.
So based on my independent monitoring i see a round trip of 86% at around 6C ambient.
Battery Discharge was closely aligned in my testing, but it didn't match historical Home Load
Similar to you, i saw "over consumption" reported by the Tesla App history, but not instant.
Over the month of November, Tesla history reported 10% more consumption than actual
In summary, i think the Tesla App is making it look worse in some places (home load) and better in others (charge/discharge) - but i don't think in reality it's as bad as your quoting.
Hope this is helpful towards your own observations
@f1p Might be normal
my numbers 3+ year old powerwall 2, last 12 months:
3.24MWh in, 2.85Mwh out, ~0.88% round efficiency trip, around ~1.07kWh per day
efficiency depends on the rate of charge and discharge, for example 3.3kW charge rate should be the most efficient (based on what Tesla was telling everyone 3 years ago). but now tesla uses 5kW for charging almost all the time.
Running costs is kind of fine, main issue for me with Tesla Powerwall is control, Tesla regularly changes firmware to introduce unpredictable behaviour which will change what you can and can't do and which tariff to use.
I have a magic boiler
@caron, I heard back from @saenergy (a top battery installer and expert) and here's what he said:
"It’s not uncommon but there’s factors to consider. The inverter and BMS will use power to keep alive. Depending on charge state and reserve, it should take this from solar or battery, sometimes from grid.
RTE is a thing so there’s always less out than in.
The other thing, and the most likely cause, will be thermal effect on the battery packs.
As capacity is, at a very basic level, a function of voltage, as temp changes, so does the resistance of the cells and the voltage moves.
In a battery, when it charges and discharges, it will generate heat. Remember the RTE, well losses come out in the form of heat.
As the electronics attempt to compensate for that, using cell temps, sometimes per cell, sometimes in groups, it kind of loses track.
This is because the system measures kWh in an out, uses that to adjust alongside the volts, temp changes and a really complex charge curve equation.
It’s inevitable as we use electronics to manage a variable chemical reaction. It’s not a truly closed loop signal.
This is why calibration cycles exist. They ignore a lot of the adjustments and equations and just drive the volts right down to minimum, then charge to max volts.
Most batteries do this every now and then automatically. Call it cell balancing or calibration, whatever, it’s doing the same job.
I do this manually on my van for example. As the fully charged range drops off, usually to around 165miles, I’ll run the van to basically dead, then slow charge it to full. Hey presto, range back up to 185miles.
The only way to truly know the in/out energy on the battery is to meter it, log it and compare. Best to do when you can fully charge/discharge it."
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
@gruff2001 Our Growatt 13 kWh system charges about 11.7 kWh (from 10% to full) and then discharges about 10.4 kWh back to 10%. Given that the HP is on 24 hours, it invariably gets to that 10% and starts using the grid by early evening. I was doing some research as to why and this seems to be fairly normal. Good to see that others with different battery systems observe similar patterns, and not just a Growatt thing.
16 * 435 watts PV
13 kWh Growatt battery
1 EV - Mercedes EQB
6 kW Aira Heat Pump
I suspect a good chunk of the "losses" are power consumption of the inverter itself.
Our Solis inverter consumes somewhere between 50-100w depending on the load, so over a 24hr period that's going to add up.
As the inverter is built into the Powerwall, I suspect this appears as a "hidden" drain on the battery capacity.
I wonder if the loss is similar for one Powerwall and Powerwalls with the extended capacity?
@editor Thank you so much for looking into this for me and to everyone else that’s replied.
i’m sorry I’ve gone quiet since posting. I have a lot to say about this subject but I’ve realised that I’m completely burnt out after spending almost 4 months chasing Tesla and disappearing down a rabbit hole of data collection & analysis.
I need to consolidate my findings into some kind of report/review but, at the moment, my brain has turned to mush so I’m going to concentrate on enjoying real life for the next week or so.
@caron I can confirm that the power usage of the PW3 is quite high, and I was initially quite shocked at how high. Others have noted similar in discussions around the internet.
The weeks before our July installation, our average daily usage was fairly constant at around 9kWh per day. The weeks immediately after installation, daily consumption came in at the 11-14kWh range, so a definite increase of around 2-3kWh per day was immediately noticeable (and it's a lot more more obvious in summer where our usage is fairly low and stable versus winter where it's all over the place and would probably just go under the radar)
Previously we had a basic solar inverter, which was self powered by the connected solar (it didn't switch on until there was solar), so we never saw any 'consumption' from the grid. The PW3 has an inverter plus other electronics that are powered continuously so it's not unreasonable to attribute maybe 50-100W to that (1.2-2.4kWh/day). Then there's the thermal management of the battery - cooling in summer and heating in winter, which again uses power. That's before we consider any round trip conversion losses.
I'm not sure how/where the Tesla app records various usage/losses. I keep a spreadsheet where daily 'usage' = 'grid import' + 'solar generation' - 'solar export' (i.e, everything in minus everything out). Grid import and solar export come from the smart meter, and solar generation is from the Tesla app as I have no independent solar metering.
I will be interested to read any further details you have managed to discern.
Samsung 12kW gen6 ASHP with 50L volumiser and all new large radiators. 7.2kWp solar (south facing), Tesla PW3 (13.5kW)
Solar generation completely offsets ASHP usage annually. We no longer burn ~1600L of kerosene annually.
@old_scientist Thanks for your reply. My initial observations were similar to yours. I had solar & PW3 installed in mid-August when my consumption had been low & consistent so it was very apparent that there was an increase of about 30%. If it had been a month later, I would have blamed the heat pump & been frantically trying to work out why it was consuming an extra 3 to 4 kWh per day.
I have now been monitoring my Powerwall 3 for almost 5 months and ascertained that the Tesla App falsely adds battery losses to 'home use' instead of 'battery'. This results in the battery appearing super-efficient and makes impossible to check actual battery performance without additional energy metering equipment. My installer came & fitted a standalone meter after I noticed the increase in home consumption and this has enabled me to see the following:
- battery losses average 3.8 kWh/day
- energy consumption has increased by an average of 18% due to battery losses (ranging from 32% at low use to 14% at high use)
- average battery efficiency is 71% (ranging from 58% at low use to 80% at high use)
- there is a constant parasitic loss of 2.4 kWh in addition to anticipated round trip losses of 11%
- battery losses are applied during battery discharge so the usable capacity is not 13.5 kWh
- actual usable battery is relative to discharge period due to constant parasitic loss
- usable battery capacity is only 12.2 kWh over 6 hour discharge period & 11.4 kWh over a 15 hour discharge period
I'm really not sure what to do next. The Powerwall 3 is marketed as 89% efficiency (solar to battery to home/grid), 97.5% efficiency (solar to home/grid), 13.5 kWh usable battery & comprehensive App for control & monitoring. That's why I chose it. My battery is obviously failing on all points but am I completely misunderstanding the data or am I just expecting too much?
- 27 Forums
- 2,475 Topics
- 56.9 K Posts
- 273 Online
- 6,165 Members
Join Us!
Worth Watching
Latest Posts
-
RE: If a heat pump can only heat DHW to 50C then what? Issue with 18KW Heliotherm heat pump
Hi, Nothing yet. I've asked customer to measure flow...
By errmm , 5 hours ago
-
RE: High Temp Heat Pumps for fast warm-up of house
I don't know exactly how long it takes to heat up (and ...
By JamesPa , 7 hours ago
-
RE: Need help maximising COP of 3.5kW Valiant Aerotherm heat pump
OK. What Im seeing looks fairly normal TBH: 1 start ...
By JamesPa , 7 hours ago
-
RE: Vaillant Tech Support Flagged Low DT: UFH Return Cold, Suspected Zero Flow
@editor thanks for the tips which I will try before cal...
By DavidB , 9 hours ago
-
RE: Daikin 6kw setup with Dixell controller
@jamespa Many thanks for your reply, a very detailed an...
By CraigH , 9 hours ago
-
RE: Exploring the role of alternative clean heating solutions - Government Consultation
Despite reservations, I found some time to respond to t...
By Rusty , 9 hours ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@crankplus, nope, still not, and I've followed up with ...
By Mars , 9 hours ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
@agentgeorge Probably, but temperature change at -10 ha...
By AndrewJ , 10 hours ago
-
RE: External wall insulation - your experience
To be clear, my experience was very positive. The journ...
By Batpred , 12 hours ago
-
@foxesfan Re: ‘Servicing’ as @editor has covered in his...
By Toodles , 12 hours ago
-
RE: A Smarter Smart Controller from Homely?
@benson No idea why mine doesn’t work, all I see on ...
By Papahuhu , 13 hours ago
-
RE: Battery sizing - How low can you go!
It seems I am seeing something similar to what you do, ...
By Batpred , 14 hours ago
-
RE: Gaslighting in the heat pump industry – has anyone else experienced this?
Don’t know if this is relevant to this thread, but my A...
By Gruff2001 , 14 hours ago
-
RE: Bosch CS5800i 5kW - Experience So Far
@majordennisbloodnok While getting Home Assistant runni...
By Steelbadger , 1 day ago
-
RE: MCS - BS EN 12831-1:2017 – Heat Loss Survey
Since May 2025 it no longer a requirement in England to...
By JamesPa , 1 day ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Forum Handel @jancold Manufacturer: Daikin Model: E...
By Jancold , 1 day ago
-
RE: Octopus Cosy 12 Heat Pump Regret: Incredibly Loud, Poor Heating & Constant Hum - Help!
@harriworld it was roughly 3am for an hour as that’s ...
By L2jad , 1 day ago
-
RE: Hoped for improvements not being realised on my Mitsubishi heat pump
I have been wondering that myself. The fact is that, ...
By JamesPa , 1 day ago
-
RE: Filtering Tap Water – Share Your Setup for Cleaner, Better-Tasting Water
I remember when I was in my early 20s I was introduced ...
By Majordennisbloodnok , 2 days ago
-
RE: Setback savings - fact or fiction?
But if it is recorded an an integer, which it seems it ...
By cathodeRay , 2 days ago