Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!

Radiator sizing sanity check

50 Posts
3 Users
3 Reactions
15.3 K Views
(@papahuhu)
Honorable Member Member
Joined: 1 year ago
Posts: 444
Topic starter  

@jamespa 

 

The flow temp is a tricky one, because it is on/off constantly the heat pump ramps up and is only operating at max flow temp for a couple of minutes before it stops. So it increases in temp rather rapidly, then stops, this makes correlation with 

In the 5 months it has been installed, I’ve only seen it stop to defrost once. It’s never running long enough to get a build up of ice. Mine stops because the homely says it has reached set point, the node is in the lounge and the temp never deviates  from -0.2C to +0.5C of set point, so in my case it starts heat pump at 17.8 and stops at 18.2 which overheats to 18.5, before decaying for 40min before restarting. In homely defence it gives good economy, my system uses 50% less energy than other identical systems on heat pump monitor. But I have cold bedrooms!

The installers offered to remove the homely free of charge last week. I’d want them to remove it and refund the installation cost. I’m holding fire on this until I’ve sorted out the rads first and potentially downsized the heat pump, depending on the new heat loss.

 

Yes most of Switzerland is dry, but we were in the Rhine valley, which has a wet microclimate. Golf ball sized hail and massive electrical storms every 4 days in the summer, crazy hot and humid. Wish I’d never left now, but at the time and without irony I missed the crapness of the UK, Switzerland was too boring!



   
ReplyQuote
JamesPa
(@jamespa)
Illustrious Member Moderator
Joined: 4 years ago
Posts: 5706
 

Posted by: @papahuhu
↑

The flow temp is a tricky one, because it is on/off constantly the heat pump ramps up and is only operating at max flow temp for a couple of minutes before it stops. So it increases in temp rather rapidly, then stops, this makes correlation with 

That really, really shouldn't happen and suggests that the heat pump may be well oversized or there is some other problem eg a badly set up buffer/LLH (if you have one) or blocked system (cold rads suggest it is blocked/needs bleeding/lsvs have been turned down too much/TRVs are stuck)

 

Posted by: @papahuhu
↑

In homely defence it gives good economy, my system uses 50% less energy than other identical systems on heat pump monitor.

Are you sure that isn't because your heat pump has twice the capacity it needs and the pumps you are comparing with are running closer to capacity?

 

The more you tell me the less certain I am that the rads are too small, although I grant that they may be.  The other system issues need to be sorted first before you can decide the cause, a run time of 2 mins is just crazy.  A heat loss survey wont sort these system issues (although it might point at oversizing) and until they are sorted everything about rad sizing is just speculation.

 

Posted by: @papahuhu
↑

Yes most of Switzerland is dry, but we were in the Rhine valley, which has a wet microclimate. Golf ball sized hail and massive electrical storms every 4 days in the summer, crazy hot and humid. Wish I’d never left now, but at the time and without irony I missed the crapness of the UK, Switzerland was too boring!

Difficult one!

 


This post was modified 11 months ago 2 times by JamesPa

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
(@papahuhu)
Honorable Member Member
Joined: 1 year ago
Posts: 444
Topic starter  

@jamespa 

Thanks, yes. 
it’s even more difficult as only they have access to the homely data.
The installer is coming out next week, a repeat full heat loss survey should sort out whether the unit is oversized and any necessary remediation should follow on from that. I’m considering it as starting the install process afresh, whether they share my perception is yet to be determined. I will get them to put it right though, at their dollar, even if it means ultimately going to the SCC and getting a full re-installation.

All this is complicated by the fact that I moved my very sick and elderly parents in with us during covid. So they are freezing cold at the moment. Heat pumps are not my favourite things at the moment, although I know it is the installer rather than the technology.



   
ReplyQuote
JamesPa
(@jamespa)
Illustrious Member Moderator
Joined: 4 years ago
Posts: 5706
 

Posted by: @papahuhu
↑

Mine stops because the homely says it has reached set point, the node is in the lounge and the temp never deviates  from -0.2C to +0.5C of set point, so in my case it starts heat pump at 17.8 and stops at 18.2 which overheats to 18.

I find it impossible to believe that your house heats by 0.7C, or even 0.2C, in 2 minutes, unless you live in a tent.  IMHO something else is causing the heat pump to shut down unless the Homely is directly over a radiator (in which case move it!) or has been set up with a hysteresis sub .1C

My strong advice to you is to find out whats going on before the installers turn up.  A new heat loss survey is no better than the previous one, just different, so isnt going to give a definitive answer.  Given what you now say there is no evidence so far that the upstairs rads are too small and there is strong evidence of an underlying system problem.

I would recommend you start by whacking up the set temperature on the Homely to say 30C.  If its the Homely causing the heat pump to switch off, this will stop it doing so.  You can then monitor flow temperature and rad temps whilst the house heats for an hour or two.  That will give an insight.  If the heat pump still switches off after a few minutes, then the Homely (unless its seriously misconfigured) isn't the problem, something in the system is blocked (could be as simple as a filter) or the heat pump is grossly oversized.  Simple experiment to start with, which will tell us a lot.

You are right to insist its put right at their expense, but the fact its got to this stage and they swapped out an oversized radiator tells me they haven't a scooby what they are doing so you may well be best off doing a bit of self diagnosis if you dont want this to drag on for years.

 


This post was modified 11 months ago 5 times by JamesPa

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote

(@papahuhu)
Honorable Member Member
Joined: 1 year ago
Posts: 444
Topic starter  

It’s not 2 minutes, it heats up for 40-50 minutes, at nearly full blast, then stops completely as the homely registers a downstairs temp above target. This is the output from the radiator upstairs, on until just before it peaks and then off. Start 50 mins, stop 40 mins, start 50 mins, stop 40 mins, 24 hours a day. It doesn’t modulate.

image

Maybe the better way to visualise it is my house electrical demand. Ramps right up to full or nearly full heat pump output, then stops dead. 

image

This post was modified 11 months ago by Papahuhu

   
ReplyQuote
JamesPa
(@jamespa)
Illustrious Member Moderator
Joined: 4 years ago
Posts: 5706
 

@papahuhu sorry - confusing info in previous posts

Anyway upstairs rads aren't getting to anything like the flow temp it seems so that needs to be fixed before any conclusions can be drawn about rad sizing. 


4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
(@papahuhu)
Honorable Member Member
Joined: 1 year ago
Posts: 444
Topic starter  

@jamespa 

Thanks, yes. I think there are multiple hardware and control system issues. 
Just as a hammer has a primary purpose of inserting nails, the primary purpose of any heating system is to heat the house. Until it’s doing that, everything else is superfluous. 



   
ReplyQuote
JamesPa
(@jamespa)
Illustrious Member Moderator
Joined: 4 years ago
Posts: 5706
 

Posted by: @papahuhu
↑

@jamespa 

Thanks, yes. I think there are multiple hardware and control system issues. 
Just as a hammer has a primary purpose of inserting nails, the primary purpose of any heating system is to heat the house. Until it’s doing that, everything else is superfluous. 

Agree.  I think I have given you several pointers to help track it down, its now up to you whether to pursue any or hope your installer will diagnose, which I frankly doubt based on what you have said whilst at the same time hoping I'm wrong!

There is no point in pursuing the radiators further so far as I can see, until the system issues are sorted

 


This post was modified 11 months ago by JamesPa

4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote

(@papahuhu)
Honorable Member Member
Joined: 1 year ago
Posts: 444
Topic starter  

@jamespa 

Do appreciate your assistance, without the run data we are both blind.

I’ll let you know how it goes next week, I live in my false hope that the smoking gun will emerge. I’ll have a look at the supply contract and workmanship warranty too, but I doubt it’s there to provide consumer protections. I didn’t mention it before for simplicity, but my installer is actually a national SME but acting as a sub contractor, and happened to terminate all heat pump installations and lay off all the plumbing staff (bar one, my contact) a week after they “finished” mine. It gets better and better 😀 



   
ReplyQuote
JamesPa
(@jamespa)
Illustrious Member Moderator
Joined: 4 years ago
Posts: 5706
 

Posted by: @papahuhu
↑

I’ll have a look at the supply contract and workmanship warranty too, but I doubt it’s there to provide consumer protections.

No chance!

Posted by: @papahuhu
↑

Do appreciate your assistance, without the run data we are both blind.

Largely, hence my suggestion to do some experimenting with the Homely set temp set to 30C, thus taking that element of control out of the equation for a while at least.

 

Good luck next week.


4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote
(@papahuhu)
Honorable Member Member
Joined: 1 year ago
Posts: 444
Topic starter  

The heat pump unit I have, Samsung gen6 16kW mono, single phase. The manual states the nominal flow rate as 46.7 l/min, when I go and check my actual flow rate it is 29.7l/min. 
Seems to me to be a large discrepancy, that’s a problem right? I’m not sure what the manufacturer really means by nominal, is it minimum or target. The pump is running and there are no low flow alarms/errors.

ta. 



   
ReplyQuote
JamesPa
(@jamespa)
Illustrious Member Moderator
Joined: 4 years ago
Posts: 5706
 

Posted by: @papahuhu
↑

The heat pump unit I have, Samsung gen6 16kW mono, single phase. The manual states the nominal flow rate as 46.7 l/min, when I go and check my actual flow rate it is 29.7l/min. 
Seems to me to be a large discrepancy, that’s a problem right? I’m not sure what the manufacturer really means by nominal, is it minimum or target. The pump is running and there are no low flow alarms/errors.

ta. 

The nominal will be the flow rate for rad dt5 at full output.  Ideally you should be looking to achieve this but.. your 16kW heat pump is likely well oversized so in practice it may not matter.  

 

I have looked back through the thread and there are some key inconsistencies in the observations you report in relation to radiator temperature, flow temperature and how long the heat pump operates for.  Also your plot seems to show rad temps around 25-30 whereas the design ft is 50.  Given these inconsistencies I'm struggling to provide coherent advice on things you might check to help with diagnosis, and I'm also not sure, from what you have said, that you want to do so. 

If you are interested in trying to diagnose and fix then you will need to resolve the apparently inconsistent observations.  For sure, however, a new heat loss survey, whilst it may be useful, will not alone be sufficient and may only serve to delay fixing the actual problem.   If this were my house I would want to focus first on getting it warm, but of course it isn't so that's your decision not mine!

 


4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.


   
ReplyQuote