Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Water Hammer After Heat Pump Install
Evening everyone
I have a very long story but to cut it short:
we have a Vailant Ecotherm ASHP that was installed 14 months ago.
From the start we have had issues with water hammer that our installer has tried and failed to rectify with arrestors. In the past few months it has got worse and is driving me crazy.
Our property shares water supply with a farm and another house. This is historic and goes back to when the 3 properties were part of the same estate. When they were sold on as separate dwellings, the water supply was not altered.
I have no technical expertise and frankly don’t know where to begin to get this problem sorted. Do I need to find a plumber who has specialist knowledge of ASHPs?
I’d be very grateful for any suggestions.
Thank you.
As far as I know this occurs when a valve/ tap closes very quickly. Can you narrow it down to a particular valve or tap? I assume it occurs on the Hot water piping as the ASHP is a closed system. Since you mention the supply perhaps I am wrong and it occurs on the cold supply side?
Daikin 6Kw ASHP.
MG4 EV, Solis 8KW inverter, 32KWh battery
1926 Semi with loft and wall cavity insulation, all radiator.
I agree with@jancood and incidentally it is unlikely to be anything to do with the ashp so unlikely an ashp specialist can help any more than any other plumber. It could however be a result of upgrading from a low pressure water system to a high pressure one, which may well have been done when the ashp was installed, which is normal practice.
If you can provide more details when it occurs/what triggers it and anything else at all that you observe it may be possible to tie down the likely cause or suggest some tests which allow it to be tied down. Also did you previously have a low pressure hot and or cold water system (with a tank eg in the loft).
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
I have a LG heat pump. Installed in 2020.
After installation, it was very noisy at times. After call back with installers they installed a bypass on the hot water heating:
- Controlled by a manual valve which by trial & error is probably closed approx 20%
- that pushes part of the flow directly back to return (rather than via the hot water tank). The heat is not wasted therefore (maybe a slight efficiency loss only)
Possibly the pump on the heat pump is too powerful vs the pipe runs & tank? Other heat pumps may have better controllable pump speeds.
In our controls we can reduce pump speed but afaik that would reduce it for the heating as well as hot water.
So the bypass seems a better solution in our case. Might it help you?
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
Posted by: @tim441I have a LG heat pump. Installed in 2020.
After installation, it was very noisy at times. After call back with installers they installed a bypass on the hot water heating:
From OPs description I had the impression (quite possibly wrongly) that the water hammer is associated with the domestic hot/cold water not the heating water.
OP needs to clarify this by telling us more about his/her observations!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Thanks everyone for your replies.
Initially the hammer occurred only when the farm was drawing water for their barns - 8am ish and 4pm ish. It would last for approx 3-10 mins. Whilst it was happening the water pressure would drop right down. However, if we turned our cold taps on, the noise would stop, so it was bearable.
For the past few months we’ve had an issue with much louder hammer that occurs when our next door neighbour (not the farmer) uses their shower, which we understand to be a power shower. This can happen at any time they wish to shower (which is perfectly reasonable) and can go on for as long as 25 minutes. The hammer is much louder than when water is being used by the farm. And the noise isn’t reduced by us turning on the cold taps.
Before the new system was installed we had a cold water tank in the loft.
@jaynieq ahhhh... so sounds like its not really a heat pump issue .. more associated with the pressurised system which is "live" connected. Whereas the old system was effectively disconnected via the tank in roof.
HHopefully a plumber on this forum can advise e.g. if it needs an extra valve... or something
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
Posted by: @jaynieqThanks everyone for your replies.
Initially the hammer occurred only when the farm was drawing water for their barns - 8am ish and 4pm ish. It would last for approx 3-10 mins. Whilst it was happening the water pressure would drop right down. However, if we turned our cold taps on, the noise would stop, so it was bearable.
For the past few months we’ve had an issue with much louder hammer that occurs when our next door neighbour (not the farmer) uses their shower, which we understand to be a power shower. This can happen at any time they wish to shower (which is perfectly reasonable) and can go on for as long as 25 minutes. The hammer is much louder than when water is being used by the farm. And the noise isn’t reduced by us turning on the cold taps.
Before the new system was installed we had a cold water tank in the loft.
That's really helpful.
Yor last sentence confirms it's not to do with the ashp as such. When your ashp was installed you were also upgraded from an unpressurised (indirect) system to pressurised (direct) dhw and pressurised cold water throughout. This is a normal thing to do and brings your water system up to date with modern practice. It also means you get higher pressure water at taps and it's all potable. Generally this is regarded as positive.
Unfortunately, whilst previously most of your water system was isolated from your neighbours by the tank, now it isn't and it's causing you a problem.
It's absolutely nothing to do with the ashp so you don't need an ashp specialist, what you need is a plumber who is good at tracking down and solving water hammer problems in older properties.
Maybe it's worth having a chat with the neighbours and seeing if there are any obvious bits of pipework between the properties that could be the cause, or whether replacing some with mdpe (plastic) might help.
Sorry but I don't think I'm going to be more helpful than that, but hopefully it enables you to ask the right questions to find the right type of plumber to fix it.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jaynieq I wish you luck with this one. I think the main thing I am telling you is to focus (when discussing with any plumber) on the water hammer and the fact that you went from an indirect system to a direct system. That's the trigger, not the ASHP. The latter is irrelevant so probably best not even to bring it up. If your neighbour also experiences the noises they may have an incentive to help.
Probably a good idea to nail down the triggers if you havent already and be sure you are able to cause the hammer if anyone visits. Also consider making a recording for them. Its nigh on impossible to fix a problem if you cant experience/reproduce it!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 26 Forums
- 2,631 Topics
- 61.5 K Posts
- 892 Online
- 7,027 Members
Join Us!
Latest Posts
-
RE: Estimating true heat loss from twelve months of consumption data
Hi @ian33a you could do your own heat loss calculation ...
By Judith , 7 hours ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
@djh ah, I have never seen this before, interesting ide...
By ASHP-BOBBA , 7 hours ago
-
RE: Anyone concerned about GivEnergy?
@sunnyskies I agree with Downfield trying to ask the GE...
By Judith , 8 hours ago
-
RE: Setback savings - fact or fiction?
@jamespa — this version may be marginally better: &nb...
By cathodeRay , 9 hours ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
All going according to plan, mid July we get that 7kW a...
By Batpred , 10 hours ago
-
Current metrics - DHW target set to 47c
By TaffontheTaff , 15 hours ago
-
RE: My Grant R290 9kW Heat Pump Installation
@petch I'm very sorry that I have not picked up your po...
By GrahamF , 17 hours ago
-
RE: Samsung gen 7 HP 12kw - auto control issue and water law
Suggest you have a trial with Havenwise app. I have th...
By Broadsman , 19 hours ago
-
RE: New Solar, Batteries, Air Source and Under Floor Heating advice please
You’re right: UFH works best with high-conductivity fin...
By bafab , 22 hours ago
-
RE: DIY or Don’t Touch? Solarman Smart Meter Install
That was my understanding also.
By JamesPa , 22 hours ago
-
RE: Grant Aeona 3 R32 cycling with weather compensation.
That would be abnormal but I cant see from your charts ...
By JamesPa , 22 hours ago
-
RE: Vaillant Sensocomfort Time
Oh I remember this from when I set mine up 2 years ago,...
By JamesPa , 1 day ago
-
Heat geek have already stated that the pro is in fact c...
By JamesPa , 1 day ago
-
RE: The Myth of the MCS Performance Guarantee
@editor I know. As if MCS wasn't bad enough, it's now e...
By Deltona , 1 day ago