Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Knock on effective of balancing radiators
Posted by: @bashWhat is the rough amount of flow that I'll get from the first quarter turn, would it be around half?
It's very dependent on the lsv, heat geek did a series of experiments (search for 'valve authority') and found the control range varied from 0.25 turns to 2 turns depending on model.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Posted by: @bashI was starting to come to the conclusion that that FRVs whilst useful, could end up being the best part of £1000 to fit and I don't really want to pay that
We’ve covered some of this over DM, but for everyone else following along, there’s potentially a “smart” alternative to FRVs due to hit the market later this year. Different manufacturer, different approach. I’ve signed an NDA so can’t share specifics, but the key point is that it dynamically balances the system in response to real heating demand rather than relying on static pre-set flow limits.
On conventional FRVs, our experience has been mixed. In principle, they’re a tidy solution. Do the room-by-room heat loss, calculate the required litres per minute, set the valve accordingly and they should hold that flow rate regardless of pressure fluctuations elsewhere in the system. In practice, they did a reasonable job for us at “normal” flows.
Where it became problematic was at very low flow rates. When we tried throttling certain radiators down to around or under 0.5 L/min, the valve didn’t appear to modulate… instead it effectively shut the radiator off. We saw this repeatedly at settings below roughly 1 L/min across five rads. The radiator would go stone cold, forcing us to increase the setting to over 1 L/min, which was more than that emitter actually required from a design perspective.
So while FRVs can be useful, particularly in systems with pressure variability, I don’t think they’re a silver bullet.
🔥 Britain’s Heat Pump Shitshow
How Installing a Heating System Became a National Nervous Breakdown
Free UK shipping.
📗 Heat Pumps Explained
A Jargon-Free Guide for Homeowners
Rewritten and updated for 2027
📘 From Zero to Heat Pump Hero
🛠️ Bodge Buster
New to heat pumps?
Take the Heat Pump Fundamentals course and use INTRO50 at checkout for 50% off.
I find it quite ironic that most of this heating/plumbing business is about controlling flow and pressure, without actually measuring flow and pressure! Strange rules for a game, when you think about it...
Now a ultrasonic heat meter costs 20€ in medium quantity on alibaba... Motorized ball valve costs 10€... Pressure sensors are also quite cheap... The call of over engineering is too hard to resist 🤣
Posted by: @bobfluxI find it quite ironic that most of this heating/plumbing business is about controlling flow and pressure, without actually measuring flow and pressure! Strange rules for a game, when you think about it...
Thats a very astute observation. Its like an electrician working without any test equipment!
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
I'm looking for a cap to replace the TRV. Whilst all of mine downstairs are fully open, I'm given to understand that there is still pressure on the valve that constricts the flow. I want to remove the TRV but not leave the valve exposed. All I see are decorator caps that achieve the opposite by completely closing the valve. Ideas please.
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
Posted by: @morganI'm looking for a cap to replace the TRV. Whilst all of mine downstairs are fully open, I'm given to understand that there is still pressure on the valve that constricts the flow. I want to remove the TRV but not leave the valve exposed. All I see are decorator caps that achieve the opposite by completely closing the valve. Ideas please.
Decorators caps, not screwed down (they can actually be used to adjust the flow) or the original head just balanced on top. I do the second of these but if you have children or dogs they will get knocked off so perhaps in this case the first is better.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
- 27 Forums
- 2,792 Topics
- 66 K Posts
- 3,528 Online
- 7,197 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Heat pump branding. Clever, contemporary… or a bit too much?
I think Heat Geek have done an amazing job on their bra...
By Tomtheheatingengineer , 7 hours ago
-
RE: HeatGeek vs Octopus surveys: puzzling disparity - any ideas why?
I have just had 3 heat loss surveys, one by heat geek o...
By David , 7 hours ago
-
RE: Heat Geek Zero Disrupt: Are We Sleepwalking Into Another Race to the Bottom?
I think that's the key question. After all inverter uni...
By Prunus , 8 hours ago
-
RE: battery storage without solar
As of October 1st they need specific qualifications to ...
By EtchedPixels , 9 hours ago
-
RE: How should the Boiler Upgrade Scheme be reformed?
A unit which uses water to transfer the heat/chill from...
By Temperature_Gradient , 10 hours ago
-
RE: Renewables & Heat Pumps in the News
With regards to the BUS grant raid, I gave it more thou...
By ASHP-BOBBA , 10 hours ago
-
RE: Why are ASHP installs so expensive?
The whole system seems to work on the basis of...
By ian33a , 10 hours ago
-
RE: Missing flow temperature in Heat Geek proposal
Good plan. If you can get half hourly meter readings a...
By JamesPa , 15 hours ago
-
RE: Heat Pumps Without Grants: Would You Have Installed One & Will You Now?
@editor Most certainly. The heat pump was an ideal s...
By Abernyte , 15 hours ago
-
Although regulations may well vary from country to coun...
By Majordennisbloodnok , 16 hours ago
-
RE: Does anyone have experience of a smart water meter?
Yep I caught our slow leak from a £100 bill rise 8)
By EtchedPixels , 16 hours ago
-
RE: Do You Need a Buffer Tank or Low Loss Header for Underfloor Heating in a Large Property?
@jamespa in some cases, failing the Turing test might b...
By GrahamF , 19 hours ago
-
RE: Passiv Smart Thermostat - Help & Forum Support
@energystoragetech The heat capacity of some...
By JamesPa , 21 hours ago
-
RE: tepeo ZEB UK Support & Info Thread
Sorry you are correct, I was remembering figures from t...
By JamesPa , 1 day ago
Members Online
No online members at the moment