Proposed grid voltage changes
The Energy Networks Association intends changing the Electricity Safety Quality and Continuity Regulations (section 27) to widen the permitted voltage range in GB.
The Announcement is here on the ENA site.
Here's the present version of that Regulation:
The engineer who brought this to my attention also observed that DNOs might actually reduce the LV levels closer to 230v instead of 240v as at present.
That wouldn't require a change to the regulations because 230v is already the 'designated voltage'.
The change could be effected by reducing the 11kV output from Primary Substations over a longish period of time.
It has implications for grid upgrades.
An EV charger or Heat-Pump requiring 4kW at a given moment in time would draw 4.3% more current at 230v than at 240v.
Consequently, a greater proportion of the Distribution Grid would suffer thermal overload, and require upgrading.
DNOs would expect Ofgem to approve such recabling, the costs of which would be met by higher electricity bills in that Region.
Save energy... recycle electrons!
Bold move by Ireland. I wonder what their installation standards and quality is like.
https://renewableheatinghub.co.uk/ireland-doubles-heat-pump-grants-to-e12500/
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
GB could achieve the same as Ireland if DESNZ understood the problems better.
Instead of increasing the grant from £5k to £7500, we should've put the additional £2500 into an inspection regime run by the local Building Control office.
Whilst on-site the surveyors would also have been able to check related works which might've been part of an ECO4 package.
We've really missed a chance to raise the standards.
Save energy... recycle electrons!
Posted by: @editorThis was sent to me last week. More quality ECO4 work.
Someone's got their wires crossed there or it's deliberately fake. There is no way on this earth that is a new Eco4 install.
If it's anything to do with one then it's what they found when they started the job and had to take it out. That's a DIY job in the pics.
@deltona, are you speaking out of authority based on demonstrable fact or expressing an opinion based on not feeling able to believe the claim?
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
Crazy if they were getting away with DIY standards. Could the installer have recruited in-loco? 😀
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kw export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; 100Amp head, HA lab on mini PC
- 27 Forums
- 2,475 Topics
- 56.9 K Posts
- 242 Online
- 6,165 Members
Join Us!
Worth Watching
Latest Posts
-
RE: If a heat pump can only heat DHW to 50C then what? Issue with 18KW Heliotherm heat pump
Hi, Nothing yet. I've asked customer to measure flow...
By errmm , 4 hours ago
-
RE: High Temp Heat Pumps for fast warm-up of house
I don't know exactly how long it takes to heat up (and ...
By JamesPa , 5 hours ago
-
RE: Need help maximising COP of 3.5kW Valiant Aerotherm heat pump
OK. What Im seeing looks fairly normal TBH: 1 start ...
By JamesPa , 6 hours ago
-
RE: Vaillant Tech Support Flagged Low DT: UFH Return Cold, Suspected Zero Flow
@editor thanks for the tips which I will try before cal...
By DavidB , 8 hours ago
-
RE: Daikin 6kw setup with Dixell controller
@jamespa Many thanks for your reply, a very detailed an...
By CraigH , 8 hours ago
-
RE: Exploring the role of alternative clean heating solutions - Government Consultation
Despite reservations, I found some time to respond to t...
By Rusty , 8 hours ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
@crankplus, nope, still not, and I've followed up with ...
By Mars , 8 hours ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
@agentgeorge Probably, but temperature change at -10 ha...
By AndrewJ , 9 hours ago
-
RE: External wall insulation - your experience
To be clear, my experience was very positive. The journ...
By Batpred , 11 hours ago
-
@foxesfan Re: ‘Servicing’ as @editor has covered in his...
By Toodles , 11 hours ago
-
RE: A Smarter Smart Controller from Homely?
@benson No idea why mine doesn’t work, all I see on ...
By Papahuhu , 12 hours ago
-
RE: Battery sizing - How low can you go!
It seems I am seeing something similar to what you do, ...
By Batpred , 13 hours ago
-
RE: Gaslighting in the heat pump industry – has anyone else experienced this?
Don’t know if this is relevant to this thread, but my A...
By Gruff2001 , 13 hours ago
-
RE: Bosch CS5800i 5kW - Experience So Far
@majordennisbloodnok While getting Home Assistant runni...
By Steelbadger , 1 day ago
-
RE: MCS - BS EN 12831-1:2017 – Heat Loss Survey
Since May 2025 it no longer a requirement in England to...
By JamesPa , 1 day ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
Forum Handel @jancold Manufacturer: Daikin Model: E...
By Jancold , 1 day ago
-
RE: Octopus Cosy 12 Heat Pump Regret: Incredibly Loud, Poor Heating & Constant Hum - Help!
@harriworld it was roughly 3am for an hour as that’s ...
By L2jad , 1 day ago
-
RE: Hoped for improvements not being realised on my Mitsubishi heat pump
I have been wondering that myself. The fact is that, ...
By JamesPa , 1 day ago
-
RE: Filtering Tap Water – Share Your Setup for Cleaner, Better-Tasting Water
I remember when I was in my early 20s I was introduced ...
By Majordennisbloodnok , 1 day ago
-
RE: Setback savings - fact or fiction?
But if it is recorded an an integer, which it seems it ...
By cathodeRay , 2 days ago