Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Where heat loss surveys seem to go against practical reality
We have a reasonably large, old house, improved significantly by the previous owner, with reasonable insulation (but some old stone and cob walls retained), with UFH and decent double glazing.
It's been a walk through treacle to get installers to come out and quote, but I finally have two to compare against. I also have a figure from a third (no report) and a stupidly high quote which we rejected. I also did my own heat loss survey using HeatPunk.
So, in order of size
Installer A : 14.7KW - Tape measure and HeatPunk - rejected on grounds of price
Installer B : 13.7KW - Lidar and Spruce
Myself : 12.3KW - Tape measure and HeatPunk
Installer C : 10.7KW - Lidar and Spruce
I've done a load of cross referencing (with much help from knowledgeable people on this forum, thank you once again) of my annual oil usage and wood stove : ~ 11.3 KW
Installer B is adamant that many of our rooms will be too cold unless we have a flow temperature of over 50 degrees and a 15KW Grant heat pump. He also says that our main bedroom is too cold and will need an additional radiator. That we currently run the UFH in that room, and most rooms, at about 45 and it is toasty in the winter makes no sense to us. He keeps saying that MCS requirements are very different to what we may find acceptable. This same installer is advocating ACH figures of between 0.7 and 1.7 (average 1.03), seems rather high? The house old, yes, but it not draughty. This is a third party doing the heat loss before passing it to a chosen installer to do the work - the installer will take overall responsibility from the point that the contract is signed, the heat loss surveyor walks away. Heat Pump offered is the 15KW Grant.
Installer C is in agreement with us that if the rooms are remaining warm enough in the winter with reasonable flow temperatures, then we are probably fine. His ACH figures range between 0.5 and 0.9, with an average of 0.55. This is an installer who will be doing the work through his own company using dedicated subcontractors. He was a heating engineer, is Heat Geek trained but doesn't operate through them anymore. Heat pump offered is the 12KW Vaillant mk 2. Flow temperature is designed for 45.
Fabric losses vary between B and C , 9,800 with B, 8,300 with C.
Ventilation losses : B is 3850 and C is 2370.
So the combination of fabric and ventilation losses combine to give the 27% difference between each proposal.
My gut feeling suggests to me that Installer C is the more practical (although I wonder if the figures are trimmed to meet the Vaillant spec) and that installer B is protecting himself and the installer that he passes the work on to.
I don't have the appetite to get another installer out, even if they agreed to come, it would be Christmas before we get to an installation point.
If you were betting on the right choice, assuming I have given enough information here, where would you put your money?
thanks
@ian33a — a tricky one. Any or all of your hunches may be correct. Can you get the raw data Installers B and C used for their fabric heat losses, and look for discrepancies there? The air change differences are already explained, and I favour Installer C assessment.
I would also ask both installers B and C if they can explain the difference in results given they used the same method, and then scrutinise their explanations for anomalies.
How confident are you in your 11.3 kW loss based on your past oil boiler and wood burner use? Which way are any errors likely to have pushed the result?
Of course getting the heat loss estimate as accurate as possible is very important, but installer character and style also matters. You need someone you can work with. On the basis of the information given, on that basis perhaps Installer C is a better bet? But the final choice has to be yours, we can only suggest things to consider.
Midea 14kW (for now...) ASHP heating both building and DHW
You probably know this, but when going with a Heat Geek trained installer that is not operating through them, you could end up taking the risk of a not correctly sized pump.
With Heat Geek they give you a SCOP guarantee for heating and hot water (hot water being a very small share of energy use). So if your figure is below their guarantee (exact figure depends on what they calculate your typical flow temperature will be), they will swap the pump at their own cost.
If you have rads undersized in a room you care about, you will probably end up turning the temp up. Ultimately, the pump will end up operating at a higher temperature to keep it comfortable and so run with a lower efficiency..
We made sure we increased rad output on the rooms that were a bit low so that the whole thing will run more efficiently. So I would look at the specific advice they give in terms of upgrades (based on loss calculations, ideally very close to room level detail). They should calculate a flow design temperature at -2C external temp (for SE, less depending where you are in the country). This is what MCS requires them to do before they complete a proposal. I know many just get data from your epc (like spruce does) and give you an estimate. But after this, they ask for £250-500 for a proper heat loss report. For a detailed heat loss report, I found it money well spent.
8kW Solis S6-EH1P8K-L-PLUS hybrid inverter; G99: 8kW export; 16kWh Seplos Fogstar battery; Ohme Home Pro EV charger; Vaillant Arotherm Pro 7kW; 100Amp head, HA lab on mini PC
Currently viewing this topic 3 users ( JamesPa, cathodeRay, ian33a ) and 3 guests.
Recently viewed by users: Batpred 9 minutes ago.
- 27 Forums
- 2,758 Topics
- 64.9 K Posts
- 1,649 Online
- 7,161 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Where heat loss surveys seem to go against practical reality
You probably know this, but when going with a Heat Geek...
By Batpred , 12 minutes ago
-
RE: Vaillant Arotherm – Using Heating
@trebor12345 the space saver on the Pro is just a funny...
By Batpred , 29 minutes ago
-
RE: Glass lined Cylinder for private water supply
Thank you, once again, for your replies. Yes...
By ian33a , 2 hours ago
-
RE: Surface mount or bury primaries for heat pump installation?
It's all in and running!
By tomasmcguinness , 2 hours ago
-
It’s been out a few days and Amazon has already attache...
By Mars , 3 hours ago
-
RE: 7kW EV Charger Options Advice
Not much to add to Majors comments. Personally, the dis...
By Batpred , 7 hours ago
-
RE: Missing flow temperature in Heat Geek proposal
Yes, and this is another point I agree. We did find a f...
By Batpred , 7 hours ago
-
RE: Problems with sizing a replacement for a Viessmann Vitocal 200-S
A very good point. In effect, the DHW pipework is an em...
By cathodeRay , 11 hours ago
-
RE: Being screwed over by Volkswagen Audi Group
No worries, I can't really argue with your logic and I ...
By Old_Scientist , 1 day ago
-
RE: Next steps on my ASHP journey: Radiators and Pipework
Flow rate is set by pressure created by the circulator ...
By bobflux , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@tim441 Here are those same three month periods for 202...
By Toodles , 2 days ago
-
RE: Adding additional Solar Panels to a DC coupled battery system
@transparent thank you for your reply above. As alway...
By Old_Scientist , 3 days ago
-
RE: How Accurate Is My DIY Heat Loss Calculation?
@kilgorexv definitely a larger inverter will help and m...
By AndrewJ , 5 days ago
-
RE: Adventures in heat loss calculations
@rob-of-york — thanks for posting this, all very useful...
By cathodeRay , 5 days ago