Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Yutaki M (RHUE-3AVHN) + XEK23232A System Controller — DHW reheat randomly fails to start, no fault code, fixed only by power-cycling controller
Hi all,
Hoping someone here has hit this before, because I've run out of things to check against the manual.
Setup:
- Heat pump: Hitachi Yutaki M, RHUE-3AVHN, mono-valent (CONF = 1)
- System Controller: XEK23232A
- DHW via diverting valve (P1 = 1) — relay on the controller's DHW output closes an external motorized valve to isolate radiators during DHW loading
- All original Hitachi parts (heat pump, controller, room controller, RF unit, sensors), bought ~2 months ago as an unused/uninstalled unit. Self-installed (DIY).
- No timer input, no DHW electric heater fitted.
Current parameters: CONF 1, P1 1, P2 0, P3 5, P4 2.0, P5 15, P6 55, P7 1.0, P10 45, P11 5, P12 10, P21 20, P22 2, P23 20, P24 0, P25 0, P26 OFF, P27 4.0, P30 1, P31 3, P34 45
DHW works fine for a while (heats to 45°C, reheats correctly when it drops a few degrees), then randomly just... stops trying. TDHW will be sitting way below the P10‑P11 (40°C) reheat threshold — I've seen it stuck at 19°C — with SDHW = 0, relay de-energized, heat pump in standby, and FAUL = 0 the entire time. No fault, no error, it just doesn't register any DHW demand at all.
The only fix I've found is a full power-cycle of the System Controller — the moment it comes back up, it immediately starts heating the tank correctly (confirmed via power consumption monitoring). It's not slow to respond either — I measured a 19°C → 34°C rise in 21 minutes after a restart, so a full recovery clearly finishes well under an hour. That rules out the "Maximum DHW Loading Time" (P27) safety timeout as the cause, since there's no way a normal reheat cycle is running anywhere near that long.
What I've already ruled out / fixed along the way:
- P26 (Summer Switch-Off) was blocking all heating in summer — fixed, set to OFF.
- P30 (No-Load Function) was disabled, causing pointless cold-water circulation with zero demand — fixed, set to 1.
- Wiring/relay confirmed correct (on the DHW output, not the heating output).
- No parameter changes between a successful reheat cycle and the next failed one — it just silently stopped registering demand.
Question:
Has anyone seen the System Controller silently stop registering DHW demand (SDHW stuck at 0) despite TDHW being clearly below the reheat threshold, with no fault code, that only clears on a power-cycle? Is there some internal state/timer not covered in the SMGB0066 service manual that could cause this? Any pointers on how to monitor or reset it without a full restart?
Thanks in advance!
- 27 Forums
- 2,760 Topics
- 64.9 K Posts
- 2,179 Online
- 7,167 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Next steps on my ASHP journey: Radiators and Pipework
I think trying to deduce flow rate from an instantaneou...
By JamesPa , 25 seconds ago
-
RE: Where heat loss surveys seem to go against practical reality
OK, here is the IAT - OAT (degree-hours because the int...
By cathodeRay , 1 hour ago
-
RE: 7kW EV Charger Options Advice
I’ve had an EV with wall charger for over 3 years and t...
By AndrewJ , 1 hour ago
-
My Adapt is finally installed and running! Almost a yea...
By tomasmcguinness , 2 hours ago
-
Hi all, Hoping someone here has hit this before, beca...
By rgabor , 18 hours ago
-
-
RE: Being screwed over by Volkswagen Audi Group
Thanks, @batpred. That integration is the one I have in...
By Majordennisbloodnok , 3 days ago
-
RE: How Accurate Is My DIY Heat Loss Calculation?
@batpred I suspect it will be more this year. I had 9 ...
By AndrewJ , 3 days ago
-
RE: Surface mount or bury primaries for heat pump installation?
@jamespa It's rusting 🙂
By tomasmcguinness , 3 days ago
-
RE: Glass lined Cylinder for private water supply
Thank you, once again, for your replies. Yes...
By ian33a , 3 days ago
-
It’s been out a few days and Amazon has already attache...
By Mars , 3 days ago
-
RE: Missing flow temperature in Heat Geek proposal
Yes, and this is another point I agree. We did find a f...
By Batpred , 3 days ago
-
RE: Problems with sizing a replacement for a Viessmann Vitocal 200-S
A very good point. In effect, the DHW pipework is an em...
By cathodeRay , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@tim441 Here are those same three month periods for 202...
By Toodles , 5 days ago