Brief update on weather compensation (AI). I have a LG 16kw unit installed 2020 - so 5 full years usage.
First 2 years ran on fixed flow as setup by installer. We have a meter on the heat pump as RHI grant - so know usage. Those years both circa 8050kWh pa (not exactly recorded).
After that moved to AI due to high costs and recorded monthly usage. Monthly varies a lot from year to year with different weather. But annual usage incredibly close - so seems to even out.
2025: 5756kWh
2024: 5741
2023: 5782
Saving nearly 30% vs fixed flow.
Main rooms heated to 21deg.
Bedrooms etc cooler - suits us.
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
@morgan i should have made clear ... LG call their version of weather compensation "AI"
Listed Grade 2 building with large modern extension.
LG Therma V 16kw ASHP
Underfloor heating + Rads
8kw pv solar
3 x 8.2kw GivEnergy batteries
1 x GivEnergy Gen1 hybrid 5.0kw inverter
Manual changeover EPS
MG4 EV
Posted by: @tim441@morgan i should have made clear ... LG call their version of weather compensation "AI"
I had no idea LG called their weather compensation AI... not confusing at all 🤣
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
As good a place as any to drop this video:
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
Increasing weather curve during winter?
We are now in the dead of winter, the lake is starting to freeze over, nights have been well sub zero and solar has been very little. I've notice that the internal house temp has been hovering lower and lower the past few days (reducing from set point of 20 to 19C) so I've bumped up the WC from 0.7 to 0.75 and might need to go to 0.8. I do have the aerotherm set to active so would have thought active would be enough to compat the loss alone.
Perhaps the persistent cold has robbed the walls of final heat and with solar being poor (we are south facing at 1000m in Spain so get very good solar) the increase in the WC is to offset this drop is solar.
I'm going to assume this is normal? Do others experience this? Our house is 80-100cm stone walls and very little insulation.
Typing this out makes it clear this is quite logical and reasonable explanation and outcome.
Posted by: @jameshIncreasing weather curve during winter?
We are now in the dead of winter, the lake is starting to freeze over, nights have been well sub zero and solar has been very little. I've notice that the internal house temp has been hovering lower and lower the past few days (reducing from set point of 20 to 19C) so I've bumped up the WC from 0.7 to 0.75 and might need to go to 0.8. I do have the aerotherm set to active so would have thought active would be enough to compat the loss alone.
Perhaps the persistent cold has robbed the walls of final heat and with solar being poor (we are south facing at 1000m in Spain so get very good solar) the increase in the WC is to offset this drop is solar.
I'm going to assume this is normal? Do others experience this? Our house is 80-100cm stone walls and very little insulation.
Typing this out makes it clear this is quite logical and reasonable explanation and outcome.
This is normal. I’m a fiddler and vary the heat curve slope up and down according to to season. The Vaillant algorithm used on active (and inactive will be worse) does not have enough gain in the control system to set the room temperature constant. Yes you could leave the heat curve to the highest setting and allow it to cycle more in shoulder season but that reduces your COP and increases your bills (at least a bit).
Mick Wall has done a lot of monitoring of his Vaillant and concluded that Havenwise does a better job for house comfort and he explains it more fully than I can. Havenwise isn’t essential if you are willing to to fiddle as the season changes.
https://energy-stats.uk/sensocomfort-room-temp-mod-inactive-active-or-expanded/
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with SCOP 4.7) open system operating on WC
Posted by: @jameshI'm going to assume this is normal? Do others experience this? Our house is 80-100cm stone walls and very little insulation.
Here in the south of the UK I don't find the need to vary the weather curve but I do switch from 'no room influence' to 'expanded' mode (which acts as a limiter) at either extreme of the season, when solar gain can easily dominate house loss during the day.
For most of the season 'no room influence' keeps the house much more stable than I could ever achieve with a boiler/thermostatic control.
Our house is tolerably insulated with a mixture of 200mm solid brick walls + internal wall insulation, 200mm solid brick walls + no internal insulation and 200mm lightweight block. 7kW @-2 for 200sq m.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Okay thanks both.
Yes the house is very nice and has sat at the desired temperature untill now, so it works great and I'm very happy.
I'm not interested in have wise, quite happy to push a few buttons now and again.
Interestingly we've been well under 0 for a few days now and dipping to -9C overnight. I've actually had to reduce the weather curve (0.8 to 0.7) as it was overheating, even with active enabled (active is not strong enough for it's job imo). It seems when it's really cold my house is fine. The issue is mild temps 2-7C and higher humidity, low solar where the algorithm falls down for heat required.
Posted by: @jameshInterestingly we've been well under 0 for a few days now and dipping to -9C overnight. I've actually had to reduce the weather curve (0.8 to 0.7) as it was overheating, even with active enabled (active is not strong enough for it's job imo). It seems when it's really cold my house is fine. The issue is mild temps 2-7C and higher humidity, low solar where the algorithm falls down for heat required.
Thats quite plausible particularly with radiators.
Radiator output is not a linear function of surface temperature unfortunately, its (usually) proportional to temperature^1.3 (there is a range of aluminium radiators claiming a much lower exponent - ie closer to linear). This means that, if the WC curve is linear, the rads will output more in relation to the loss at lower OATs and less in relation to the loss at higher OATs. Depending on how exactly the curve is set up the discrepancy, a degree or so, may manifest itself more or less anywhere in the range, but most likely at middle OATs.
As a further complication, if your heat pump modulates its water pump speed to keep a constant DT (some do) then the discrepancy between a linear FT variation and the ideal for radiators is greater than for heat pumps that keep their water pump speed constant.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
Interesting thanks. I do wish the vaillant app would let me build my own weather curve. There is a lot of scope for improved user functionality - though I respect they don't want plebs messing with stuff.
-
Bosch CS5800i 7kW replacing Greenstar Junior 28i
2 weeks ago
-
Rodents! A word of warning for heat pump owners
1 month ago
-
Ecodan Pump Issues… Circulation pump turns off when heat pump compressor turns off
2 months ago
-
Running my new Nibe ASHP efficiently
2 months ago
-
Where has Watson gone?
2 months ago
- 27 Forums
- 2,520 Topics
- 58.6 K Posts
- 727 Online
- 6,800 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Daikin Altherma 3 LT compressor longevity question
This mess is intriguing: I wonder if this represent...
By bobflux , 20 minutes ago
-
RE: Say hello and introduce yourself
Hi. I'm Mike. Thank you for letting me join. My partn...
By Fretless6 , 2 hours ago
-
RE: Connecting Growatt SPH5000 over wired ethernet rather than wireless
The simplest wired option is usually the Growatt Ethern...
By Jonatan , 5 hours ago
-
RE: Peak Energy Products V therm 16kW unit heat pump not reaching flow temperature
ASHPs do have a minimum compressor speed. The minimum h...
By bobflux , 11 hours ago
-
RE: Electricity price predictions
@jamespa And it seems some of the nasty public cloud...
By Batpred , 12 hours ago
-
RE: Tell us about your Solar (PV) setup
Location: near Lyon, France 12kWp on the roof, 2x Sol...
By bobflux , 12 hours ago
-
RE: Jokes and fun posts about heat pumps and renewables
Technology is rapidly advancing. BBC News reported th...
By Transparent , 15 hours ago
-
What matters for flow and pressure drop is internal dia...
By bobflux , 16 hours ago
-
RE: Do Fridges and Freezers have COP ratings?
@editor Thank you all for your replies and submitted in...
By Toodles , 18 hours ago
-
I know and yes. The secondary deltaT wont necessaril...
By JamesPa , 22 hours ago
-
RE: Designing heating system with air to water heat pump in France, near Lyon
Just love the way you put it! 🤣
By Batpred , 2 days ago
-
RE: Safety update; RCBOs supplying inverters or storage batteries
Thank you for sharing. So it seems that your Schneid...
By Batpred , 2 days ago
-
RE: Forum updates, announcements & issues
@upnorthandpersonal thanks for the thoughtful, consider...
By Mars , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@mk4 All 21 panels have their own Enphase IQ7a microinv...
By Toodles , 2 days ago
-
RE: Setback savings - fact or fiction?
Great, so you have proven that MELCloud is consistently...
By RobS , 3 days ago
-
RE: Mitsu PUHZ120Y 'Outdoor Temp 'error?
Thanks David & James It almos...
By DavidAlgarve , 3 days ago
-
RE: Surge protection devices SPDs
@trebor12345 - your original Topic about the right type...
By Transparent , 3 days ago
-
RE: Help needed with Samsung AE120RXYDEG
@tomf I’ve been sent this from a service engineer at Sa...
By Mars , 3 days ago
-
RE: Buying large amp bidirectional RCD and RCBO
Yes... I went through this particular headache and ende...
By bobflux , 4 days ago
-
O-oh! Let's take this as an opportunity to 'pass the ...
By Transparent , 4 days ago
-
RE: Homely setup on daikin heat pump
@craigh I refer to our somewhat elevated temperature of...
By Toodles , 4 days ago
-
RE: Air source heat pump roll call – what heat pump brand and model do you have?
My turn, this describes the future installation, only t...
By bobflux , 4 days ago