Mitsibushi Ecodan U4 error code: thermistor values
Hi All
Have had the pleasure of a trouble free air source heat pump for 8 years.
Came on today with a U4 error code and tripped the RCCB. The manual states that the error refers to one of the thermistors in the outdoor unit (TH32,TH33,TH6,TH7 or TH8).
The Heat pump is a Mitsibushi Ecodan PUHZ-W85VHA2R1-BS UK
Would anyone know where I can get the resistance values for the thermistors to check which one is faulty?
Thanks in advance.
Welcome to the forums @hughes674 – the resistance values you're looking for are available in the ME Engineer app.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
@editor Hi
Thank you. Appreciated.
Bad news checked all the thermistors apart from TH8 as cant get to it and they all are within range.
Got a feeling its gonna be expensive.
And here's a suggestion from Mitsubishi's Technical Trainer. This video shows how to use the Main Remote Controller to look at thermistor readings, which can help narrow down which thermistor needs testing.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
@editor Thank you.
All the thermistor temperature readings look right but not displaying anything for TH8.
Is there a way of the controller telling me which thermistor is faulty?
@hughes674 so the technical trainer has informed me that if have melcloud installed you can call the technical help desk and they will be able to access the system remotely and provide further guidance. If not, it’s a case of getting an engineer out unfortunately.
Buy Bodge Buster – Homeowner Air Source Heat Pump Installation Guide: https://amzn.to/3NVndlU
From Zero to Heat Pump Hero: https://amzn.to/4bWkPFb
Subscribe and follow our Homeowners’ Q&A heat pump podcast
Hi All
Mitsubishi Ecodan PUHZ-W85VHA2R1-BS UK
Following on from a U4 fault on my heat pump I have now finally received the TH8 thermistor from Mitsubishi.
Issue I have is the power board needs removing to replace it but cannot get the power board off. released the rubber clips but the board is still firmly attached somehow.
Has anyone had any experience removing these?
- 21 Forums
- 1,822 Topics
- 39.3 K Posts
- 54 Online
- 2,136 Members
Join Us!
Latest Posts
-
RE: Heat Pump starting current
Hi @cathodeRay , aren't all of the cycles in your chart...
By s_gatorator , 51 minutes ago
-
RE: ASHP for small garage and workshop
OK here the data for 0600-0659 in the chart I posted e...
By cathodeRay , 2 hours ago
-
RE: hum/whine from Wilo circulation pump
@richard24738 Tricky Devils those LLH’s! Befor you try ...
By Toodles , 3 hours ago
-
RE: Ripped Off: How UK Homeowners Are Paying Gas Prices for Wind Energy
Beacause an admin has edited the post we have lost the ...
By Jeff , 5 hours ago
-
RE: Vaillant Arotherm ASHP gets noisier when it gets colder outside
Please thank @judith who posted this initially!
By JamesPa , 10 hours ago
-
RE: Adding data centre electricity costs to domestic energy bills?
I don't see how the total costs which will be applied t...
By Transparent , 10 hours ago
-
RE: Samsung ASHP owners what have you set your weather compensation to?
Currently resetting Flow temps as per my thread adjusti...
By Alfapat , 12 hours ago
-
RE: What to Expect During Your First Winter with a Heat Pump
Vaillant have this comment about de-icing "The de-icing...
By JohnR , 1 day ago
-
RE: Mitsubishi Ecodan 8.5kW Monobloc (FTC5) Defrost Mode
Perhaps. My 200 sw m 1930s retrofit with fabric upgrad...
By JamesPa , 1 day ago
-
@transparent Thanks for the info, i will try to get EDF...
By MikeF , 1 day ago
-
RE: Investment or not Solar/Battery instllation
@abernyte I can send the quote , if you can understand ...
By Alfapat , 1 day ago
-
RE: How to make me regret installing a heat pump
@lucia I’ve started reading the work of Dieter Helms a ...
By Judith , 1 day ago
-
Coincidentally, I had an introductory visit from a very...
By IanMK13 , 1 day ago
-
RE: Best temperature wave form for best economy and efficiency .
@ivanhoew - yes, I agree, still a work in progress on t...
By cathodeRay , 1 day ago
-
RE: Controversial opinions - pure weather compensation, buffer tank, heat loss, oversized heat pumps
I realise that maybe the case for your customers now bu...
By JamesPa , 1 day ago
-
RE: Solar thermal with combi boiler
Running a ULV immersion heater avoids the losses incurr...
By Transparent , 1 day ago
-
RE: ASHP and how it should run and potential kw consumption?
@judith I thought no one saw my tears
By jeegnesh , 2 days ago
-
I've recently topped up by adding a few litres at the t...
By ecodan-efficiency , 2 days ago
-
RE: Running my new Nibe ASHP efficiently
@lizzie Thank you Lizzie, you are most welcome! As the ...
By Toodles , 2 days ago
Latest Topics
-
By s_gatorator 1 day ago
-
Investment or not Solar/Battery instllation
By Alfapat 1 day ago
-
By Jancold 2 days ago
-
By MikeF 3 days ago
-
Running my new Nibe ASHP efficiently
By jamieheatpumpnew 3 days ago
-
How do the settings on my Gen 5 Samsung ASHP sound?
By cyrusir 4 days ago
-
By Potatoman 4 days ago