Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Samsung Heat Pump – Can't Activate TW2 Pipe Sensor (for Delta T Control)
So... after 2 frustrating years, with a COP of 2, for a house with underfloor heating and very good insulation, I finally found the issue (or issues)
1- the smallest issue, which generates a delta T of 1 or 2 - the "plumber" mixed the supply and return from the heat pump to the puffer... supply is in the lower part and the return on the higher part, when leaving the puffer they are in the correct place, supply is up and return is down... so... the water is really mixing in the puffer 😀 😀 - this issue i have not fixed yet, it's on my ToDo list
2. the BIG issue - the "engineer" (electropainter - explained below) who made the connections between the outside and inside units of the heat pump, did not do a proper job and was losing refrigerant since the beginning... a proper engineer came by yesterday and it seems i had no more refrigerant... now it's fixed and after 12 hours in cooling mode i have a COP of 6.... I have NEVER seen this COP on my heat pump, NEVER, maximum was 2.5, in the beginning...
I have no words, I don't know if I should laugh or cry...
There are 2 saying in romanian which fit my use case:
- what i learned recently: "I am too poor to be cheap" - i'll never work with cheap people, it will eventually cost you double or triple, better find competent workers which have a higher price
- "electropainter" handyman (in romanian - electrozugrav) - a guy which does something for 1 year, with no proper learning and is now advertising himself as a specialist.... thats with what specimens i worked initially...
I'll come back with an update again, after a few months.
I hope this helps others... don't make the mistakes I did, better pay more for a good worker (regardless for what) than go for the cheap ones and have to repair what they did, it will cost more!
Great news. Lack of refrigerant will certainly degrade cop.
Posted by: @bubuontheweb1- the smallest issue, which generates a delta T of 1 or 2 - the "plumber" mixed the supply and return from the heat pump to the puffer... supply is in the lower part and the return on the higher part, when leaving the puffer they are in the correct place, supply is up and return is down... so... the water is really mixing in the puffer
![]()
- this issue i have not fixed yet, it's on my ToDo list
I assume you mean buffer not puffer. You are correct this will cause even more mixing than a correctly plumbed buffer! Of course better still almost certainly is not to have a buffer at all. I presume there is no way to pursue whoever installed this to take the buffer out or better still turn it into a 2 port volumiser.
If you are replumbing this yourself then there is an arrangement of valves you could add in to allow you to try it as a volumiser not a buffer, but be able to reverse the operation if for some reason it doesn't work. Just saying if you are planning extensive work on plumbing.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa Buffer, yes 😀
Volumiser, you mean to have it linked only to outlet or inlet? Not connecting them both, right?
I plan to do it myself, redo everything, without buffer. However, I plan to add some valves along the route in case removing the buffer does not give a better outcome.
Wondering if someone could share a diagram on how it should look? And what should i share beforehand, as info, for this?
Read on a couple of pages from here
That describes the configs.
With a volumiser you need also to bypass or remove the secondary pump
Alternatively number ports clockwise starting top left.
For a buffer:
Flow in from heat pump = 1
Flow out to emitters =2
Return from emitters (via secondary pump) =3
Return to heat pump =4
Secondary pump can alternatively go between port 2 and emitters.
For a volunteer
Flow in from heat pump = 4
Flow out to emitters =2
No secondary pump
Tank bypassed on return
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa I assume “volunteer” should be volumiser?
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with SCOP >4) open system operating on WC
Posted by: @judith@jamespa I assume “volunteer” should be volumiser?
Autocorrupt seems to be working overtime.
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
- 27 Forums
- 2,800 Topics
- 66.2 K Posts
- 1,453 Online
- 7,206 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: How will removing the standing charge on gas bills benefit heat pumps?
I'm not sure it makes much of a difference to heat-pump...
By Temperature_Gradient , 3 hours ago
-
@editor Ouch, sorry to re start the tick. I had assume...
By DavidB , 4 hours ago
-
RE: Say hello and introduce yourself
@e-a-west as the good Major said, welcome to the forums...
By Mars , 5 hours ago
-
RE: New Build 3 Phase or 1Phase
We are on three phase power because it's an enormous li...
By EtchedPixels , 6 hours ago
-
RE: How much of your renewable and home setup would still work if the internet went down?
Yes I actually have a copy of a tool that whenever a ce...
By EtchedPixels , 14 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
@editor Hi, To resolve this, please tap on the A...
By Indevolt Tech , 22 hours ago
-
RE: Double or Triple Glazed Windows?
Posted by: @singlespeed With 9 years repairing windo...
By Rob of York , 2 days ago
-
@transparent we’re still running a secure version of PH...
By Mars , 2 days ago
-
RE: How quickly would you want/expect heat recovery to take from setback?
Much longer than that here. The heating isn't even on. ...
By bobflux , 2 days ago
-
RE: Passiv Smart Thermostat - Help & Forum Support
Obviously the weather is changeable but there's a defin...
By Singlespeed , 2 days ago
-
RE: The Changing Jet Stream Could Challenge UK Air Source Heat Pumps
@rob-of-york I must admit that when we had a Daikin hea...
By Toodles , 2 days ago
-
RE: Forum updates, announcements & issues
Get the Renewable Heating Hub heads-up on WhatsApp. I...
By Mars , 2 days ago
-
RE: Safety study for plug in batteries out to tender - looks like Q3 2027 at best before legal
@editor I pointed out to the one of the Fuse execs that...
By dansus , 2 days ago
-
RE: 15kw pump for 225m2 1990's house - over kill?
@seaviews As well as loft insulation, there are othe...
By Rob of York , 3 days ago
Members Online
No online members at the moment