Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Samsung Heat Pump – Can't Activate TW2 Pipe Sensor (for Delta T Control)
So... after 2 frustrating years, with a COP of 2, for a house with underfloor heating and very good insulation, I finally found the issue (or issues)
1- the smallest issue, which generates a delta T of 1 or 2 - the "plumber" mixed the supply and return from the heat pump to the puffer... supply is in the lower part and the return on the higher part, when leaving the puffer they are in the correct place, supply is up and return is down... so... the water is really mixing in the puffer 😀 😀 - this issue i have not fixed yet, it's on my ToDo list
2. the BIG issue - the "engineer" (electropainter - explained below) who made the connections between the outside and inside units of the heat pump, did not do a proper job and was losing refrigerant since the beginning... a proper engineer came by yesterday and it seems i had no more refrigerant... now it's fixed and after 12 hours in cooling mode i have a COP of 6.... I have NEVER seen this COP on my heat pump, NEVER, maximum was 2.5, in the beginning...
I have no words, I don't know if I should laugh or cry...
There are 2 saying in romanian which fit my use case:
- what i learned recently: "I am too poor to be cheap" - i'll never work with cheap people, it will eventually cost you double or triple, better find competent workers which have a higher price
- "electropainter" handyman (in romanian - electrozugrav) - a guy which does something for 1 year, with no proper learning and is now advertising himself as a specialist.... thats with what specimens i worked initially...
I'll come back with an update again, after a few months.
I hope this helps others... don't make the mistakes I did, better pay more for a good worker (regardless for what) than go for the cheap ones and have to repair what they did, it will cost more!
Great news. Lack of refrigerant will certainly degrade cop.
Posted by: @bubuontheweb1- the smallest issue, which generates a delta T of 1 or 2 - the "plumber" mixed the supply and return from the heat pump to the puffer... supply is in the lower part and the return on the higher part, when leaving the puffer they are in the correct place, supply is up and return is down... so... the water is really mixing in the puffer
![]()
- this issue i have not fixed yet, it's on my ToDo list
I assume you mean buffer not puffer. You are correct this will cause even more mixing than a correctly plumbed buffer! Of course better still almost certainly is not to have a buffer at all. I presume there is no way to pursue whoever installed this to take the buffer out or better still turn it into a 2 port volumiser.
If you are replumbing this yourself then there is an arrangement of valves you could add in to allow you to try it as a volumiser not a buffer, but be able to reverse the operation if for some reason it doesn't work. Just saying if you are planning extensive work on plumbing.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa Buffer, yes 😀
Volumiser, you mean to have it linked only to outlet or inlet? Not connecting them both, right?
I plan to do it myself, redo everything, without buffer. However, I plan to add some valves along the route in case removing the buffer does not give a better outcome.
Wondering if someone could share a diagram on how it should look? And what should i share beforehand, as info, for this?
Read on a couple of pages from here
That describes the configs.
With a volumiser you need also to bypass or remove the secondary pump
Alternatively number ports clockwise starting top left.
For a buffer:
Flow in from heat pump = 1
Flow out to emitters =2
Return from emitters (via secondary pump) =3
Return to heat pump =4
Secondary pump can alternatively go between port 2 and emitters.
For a volunteer
Flow in from heat pump = 4
Flow out to emitters =2
No secondary pump
Tank bypassed on return
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa I assume “volunteer” should be volumiser?
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with SCOP >4) open system operating on WC
Posted by: @judith@jamespa I assume “volunteer” should be volumiser?
Autocorrupt seems to be working overtime.
105 m2 bungalow in South East England
Mitsubishi Ecodan 8.5 kW air source heat pump
18 x 360W solar panels
1 x 6 kW GroWatt battery and SPH5000 inverter
1 x Myenergi Zappi
1 x VW ID3
Raised beds for home-grown veg and chickens for eggs
"Semper in excretia; sumus solum profundum variat"
- 26 Forums
- 2,723 Topics
- 63.8 K Posts
- 2,545 Online
- 7,124 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Jokes and fun posts about heat pumps and renewables
@jamespa Normally, we have rainwater in our water butts...
By Toodles , 7 hours ago
-
RE: Heat Pump Servicing & Maintenance – Good Value or Rip-Off?
@old_scientist if you are going DIY then you may wan...
By Papahuhu , 13 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
After a short while that was followed by the 'power war...
By JamesPa , 13 hours ago
-
RE: Samsung heat pump - data cable issue
That's well done. Cable is the correct type (LIYCY = 2x...
By bobflux , 21 hours ago
-
RE: Electricity price predictions
I agree, we will find out at the next budget whether th...
By Old_Scientist , 1 day ago
-
RE: Missing flow temperature in Heat Geek proposal
@editor I went through HG website, so should be ok for ...
By sttpd1917 , 1 day ago
-
Who did the Freedom Heat Pump cloud server and what did...
By Mars , 1 day ago
-
RE: Who's your electricity provider and what's your tariff?
Reading between the lines of what octopus are doing wit...
By JamesPa , 1 day ago
-
RE: Air to air bus grant installer anywhere
The through wall two hole ones have their place (listed...
By EtchedPixels , 1 day ago
-
I hope it goes ok, Hon can be hard to set up IF the sof...
By Graham Hendra , 1 day ago
-
@clockworks Hi, So there is a big difference between st...
By ASHP-BOBBA , 1 day ago
-
@editor wellvery comprehensive answer. I will get all i...
By Keithb , 2 days ago
-
RE: Advice on my Heat Pump Journey: Old Stone Built Detached Cottage
all good advice I will follow this up
By PaulC , 2 days ago
-
Heat of vaporization of water is 2.25 MJ/kg (0.625 kWh/...
By bobflux , 2 days ago
-
RE: Existing Solar Panel installation - structural roof calculation check
What will also happen is that they see that there is so...
By EtchedPixels , 3 days ago