Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
@robs Wow. That’s quite a difference!
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@robs Oops. Thanks for that. I've run it with a more accurate pipe sizing. Initially over 5m of pipe it looks like 0.054 bar for the corrugated and 0.013 bar for 28mm copper. So yes 4 times the pressure drop. I'll do a bit of measuring and see what Samsung have to say.
Measured pipe runs etc. The length of the Kaiflex pipe is 17.256m. Pressure drop at a flow rate of 15lpm is 0.066bar. Flow and return - so the pressure drop is 0.132 bar. If it was 28mm copper it would be 0.05bar. However estimating the length of the heating pipes (22mm and 15mm) the pressur drop is about 1.2 bar. At higher flow rates it gets a lot worse. Yes 28mm copper would be better however it's the rest of the heating circuit that's critical.
Delta T. Now it's between 4 and 5 at a flow temperature of 28 degrees C. The flow rate has dropped from 19 lpm to 15 lpm. How - I started trying to balance the rads. You get into a doom loop of adjust one and the others change. In the end I just set 9 of the 11 to '90 degrees on' from shut i.e. open the Lock Shield by a quater turn from shut. Most of the L/S are 'low authority' - half a turn and there are fully open. Will try again when it gets colder (and when I've got the hang of the IR camera).
Finally - anyone know what 'Eco Level4/5' is on the control panel?
@mike-h Got this reply from Samsung support:
The Eco level is there is an indication as to how the system is running at that given time, from Eco 1 where the immersion is operating only to Eco 5 where you have solar operating only. You should normally see this around the 3- 4 mark.
I have seen 2/5 - clear as mud.
HavenWise now have control of my system. Will report when I have more data (or any ...).
@raiph Looking forward to hearing what you experience. My heat pump should (hopefully, after a 2 year battle with my planning authority) be in within the next month or two and Havenwise was the direction I was thinking of going.
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa Ok. Can someone settle an argument I've been having with myself. If I balance the radiators to get a better Delta T then the flow rate will decrease. Does this mean that the pump pressure will increase? Is a higher flow rate better as far as efficiency goes?
As for HavenWise - half way through me trying to balance the rads they change the Water Outlet temperature. Confused me. I've tried two methods - dual channel thermostats with K thermocouples and an infrared camera attachment on my phone. For the thermocouples - use a bit of tape to fix them to the front panel of the rads - top left/bottom right. Don't use the pipework. Switch off the lockshield valve and wait for it to cool down. When it is cold slowly open the L/S 15 degrees at a time until the flow face of the panel reaches the Water outlet temperature. Then check the return. Wait for 10 - 15mins and adjust until you get near to a Delta T of 5. As for the Infrared camera - it does match the thermocouple readings and also gives an indication of the heat flow across the rad. Be realistic Delta T or 4 to 6 should be OK.
Does anyone know the power consumption of a Samsung at various Water Outlet temperatures and flow rates. Saturday night 3 degrees outside and HavenWise set the WO temperaure to 27.5. 'Instantaneous power' was 900W. Bit high? The house didn't make it past 19 degrees.
I'll log the heating flow and return temperatures over a couple of days to try and get an idea what the HP is doing and also how HavenWise are controlling it.
Posted by: @raiph. If I balance the radiators to get a better Delta T then the flow rate will decrease. Does this mean that the pump pressure will increase? Is a higher flow rate better as far as efficiency goes?
I'm not sure what you mean by better. As a general principle you should be fully opening the valve on the radiator furthest away/last to heat up and then adjusting others down. You don't want to restrict the flow rate more than you need to to get equal delta t across all radiators (or if you are balancing for room temperature which is arguably better but more difficult, equal room temperature). However you do this at least one radiator valve should be fully open when balanced. If the resulting flow rate is too high then turn the pump down a notch or better still allow the Samsung itself to control it, which it can assuming this is a regular set up. It's not so much higher flow rate that is better, you need sufficient to carry the heat to the radiators and any more is wasteful. If you balance the rads with at least one valve fully open when balanced, that's the best you can do.
@toodles has, I believe, a balancing 'script', perhaps he cam post it again.
Probably best to balance before invoking havenwise. I don't know if you can disconnect them temporarily
4kW peak of solar PV since 2011; EV and a 1930s house which has been partially renovated to improve its efficiency. 7kW Vaillant heat pump.
@jamespa Here is the link to my guide:
https://renewableheatinghub.co.uk/how-to-balance-radiators-the-role-of-the-lockshield-valve
Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
Are you all saying that the Delta T across the radiators is irrelevant?
- 26 Forums
- 2,607 Topics
- 60.8 K Posts
- 264 Online
- 6,967 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Renewables & Heat Pumps in the News
@editor, I hear that too. I can confirm that out of ...
By ASHP-BOBBA , 5 hours ago
-
End-of-Life Heat Pumps: How Do You Dispose of an ASHP in the UK?
As many of you know, our Global Energy Systems heat pum...
By Mars , 5 hours ago
-
@derbygraham fully agree with James, and it’d be good t...
By Mars , 6 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
Finally got around to installing and setting up the Sol...
By Mars , 6 hours ago
-
Unfortunately its a function of the physics. Max heat ...
By JamesPa , 7 hours ago
-
RE: Microbore heat pump installs
In principle you are almost certainly right, but in pra...
By JamesPa , 7 hours ago
-
RE: Electricity price predictions
@old_scientist We are a low mileage home, so bulk of ou...
By ChandyKris , 8 hours ago
-
There are just too many unknowns for me to comment on p...
By Transparent , 10 hours ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
@toodles I keep an eye on wholesale prices and energy m...
By ChandyKris , 11 hours ago
-
RE: Brand and installer questions for ASHP
Strange, perhaps it doesnt use modbus which the third p...
By JamesPa , 12 hours ago
-
RE: Upgrading my system, how far do I go?
For comparison, my PW3 with 11.04kW inverter, will char...
By Old_Scientist , 15 hours ago
-
RE: Changes to Tesla Powerwall Charging Regime?
Elon gate - legendary! I take my hat off to you @toodle...
By Old_Scientist , 18 hours ago
-
RE: Mitsubishi Ecodan not good enough ?
Thanks @goody, appreciate the feedback and sorry you ha...
By marcexec , 1 day ago
-
RE: Minimum and Zero Disrupt Heat Pump Installations
True (first sentence) Thats the reason to consider th...
By JamesPa , 2 days ago
-
RE: High air source heat pump running costs – Vaillant AroTherm Plus
Quite right. I was using a rough guesstimate of doublin...
By Majordennisbloodnok , 2 days ago
-
RE: My Grant R290 9kW Heat Pump Installation
Again, really don't know how accurate this is! &nb...
By petch , 2 days ago
-
RE: MCS Quality Audit – Has Anyone Had One? Did It Lead to Remediation?
@toodles The whole scheme is a shocking waste of money....
By Papahuhu , 2 days ago
-
RE: Anyone concerned about GivEnergy?
Many thanks for your, and the subsequent, answers tk qu...
By KevH , 2 days ago
-
RE: DIY or Don’t Touch? Solarman Smart Meter Install
Yes, and these guys would probably be my preferred inst...
By Batpred , 3 days ago
-
RE: Hot water tank lose heat rapidly on random days
@jamespa Hopefully their reasons are well intended! ...
By Bash , 3 days ago
-
RE: Ecoflow UK Support & Info Thread
As mentioned above, we’ve got our full review of the Ec...
By Mars , 3 days ago
-
RE: Say hello and introduce yourself
@sonosppp welcome to the forums. I see you've posted in...
By Mars , 3 days ago
-
RE: Guidance with installing a new heating system
@bobflux Great, thanks for the advice. The pipe has an ...
By Hamilton , 4 days ago
-
RE: Daikin Altherma 3 LT compressor longevity question
@optimistic-optimiser I have has a Daikin for a few yea...
By madsid , 4 days ago
-
RE: UK DIY Battery: SEPLOS 48V 200Ah x2 + Sunsynk 8K – Safe Installation for Garage Conversion
The rule of thumb is to ensure that you can isolate any...
By Transparent , 4 days ago