Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
OK - changed Water Law to 32 & 45 degrees. At the moment I'm having wierd HW problems - the cylder temp drops by about 10 degrees before it fires up again. Over the weekend the cylider dropped to 30 - had to heat it back up to 52 with Eddi. Three port valve problem?
Is there an Error Log somewhere? I'v found one but it's greyed out.
As for thermostats - e-mailed Homely a few times - no reply. Have they gone bust already?
Question - has anyone used Kaiflex Solar 2in2 pipe? They used it on my installation betwee the HP and three port valve and then across the loft to the heating circuit. It's 25.4mm inside diameter, stainless steel 'corrugated' pipe. I've spoken to a distributer and e-mailed the company in Germany. No replies. All I'm trying to find out is how does it compare to 28mm copper. Flow rate specs?
Power wise - see below. The control panel says it's running at a COP of 5.2. I suspect it's lying ...
@raiph Homely were still ‘at home’ this morning as I was chatting to technical support and sorting out a few things. As to the pipework; is corrugated pipe smooth on the inside? If not, then surely this is going to cause flow problems? Regards, Toodles.
Toodles, heats his home with cold draughts and cooks food with magnets.
@raiph Hi Ralph
It would be useful if you could annotate your graph with what is using the power at different times. Ideally you want to minimise any usage outside your overnight cheap rate.
A COP of 5.2 at the moment isnt outrageous during this warm spell at your flow temperature.
Are you heating your domestic hot water in a timed block or is it set up reheat when the cylinder temperture drops by a certain amount?
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody Hot water - at the moment it's on 'Standard' - it re-heats when the temperature drops 4 degrees from the set temperature. I'll add a graph at the end. I've switched to 'eco' - just to see what it does. I have set a hot water schedule which forces it to re-heat first thing in the morning. One problem - how do you change the time on the Control panel (i.e. MIM controller)?
A few questions:
Stll cannot find out about the Kaiflex Solar 2in2 pipe - specifically the flow rate - how does it compare to 28mm copper?
Diverter valve used - Honeywell Home 272889. Not exactly reliable due to its rubber ball. Is there an alternative (with the same port layout) that has a rotating shoe (self cleaning) that can handle the high flow rates of an ASHP? I'm trying to avoid the Swiss ones - wrong pipe/port layout plus expensive (EBSE).
At the moment I'm in the observation phase - no fiddling until I know what's going on. As an aid I've been using an EliTech Temperature Data Logger (£26 from Amazon). Great for the price.
Observation - 1 to 1.5 Degrees between flow and return measured at the Kaiflex to original pipework junction (i.e where it connects to the radiator circuit). Will monitor it at the HP connections. Bit low?
I've been trying to balance the rads with an IR camera - really need cooler weather. I have noticed the heat losses from the junk in the loft i.e. 3 port valve, 25l volumiser 28mm flow restrictor, Y strainer and about six valves. None of them lagged. Time to build an insulated box ...
No temp graph - doesn't like JPG files ...
@raiph So it will be cheaper to heat your domestic hot water overnight if you have a large enough tank to meet your daily needs. I dont heat my DHW using the heat pump so havent used the controller to set it up. I image its in schedules, you could try searching on youtube.
The flow rate of the Kaiflex pipe could be estimated from its internal diameter, I would think that it is fine for an 8 kW unit
Are you saying that your flow and return water temperatures are 1.5 C difference? If so that is too small. Ideally a 5C difference is stated, but certainly more than 3C. Have your radiators been sized correctly?
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Thanks Mike, time now correct.
HW cylinder in 'eco' mode. Possible feature(bug). Switch to eco. After the scheduled Off/On time it reverts to Standard mode. Will have a word with Samsung.
Radiator sizing. All sized to a flow temperature of 45 degrees C. Most OK at 43. Confirmed with Heating Engineer and Heatpunk software. All depends on the materials used in the Heat Loss Calcs. The other major factor is the ACH. Complicated by an MVHR system. Possibly the lowest heat loss of 4.3kW was correct or even an over estimate. Heat pump too big? The installers ignored the HLC and just fitted an 8K unit. I sized and changed the rads.
Kaiflex pipe. My concern is that it's a corrugated pipe so the water flow through it will not be laminar. An inner diameter of 25.4mm should be OK for a 8K HP. Looks like Kaiflex make the lagging and someone else produces the pipe, hence they have no idea of flow rates.
Delta T across the rads. So many factors involved. Flow rate for heating 19lpm. Hot water 26lpm. Do any of the MIM FSV settings control the pump speed i.e. is the high flow rate causing the low Delta T?
@raiph I would assume you could manually alter the pump speed, or if it is of a compatible type it can be controlled via Pulse Width Modulation directly from the HP controller. Ive done that and it works very well. What pump do you have?
The corrugation probably will have an effect but difficult to know how big.
If you mean the 1.5C delta T is across the rads then that might just be that the flow temperature you are running at cant dump more heat into the house.
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
@bontwoody My HP - it's the variant that has everything in the box i.e. pump, expansion vessel et al. Will read the MIM controller manual to see what control there is for the pump. RTBM ...
@raiph So if its all in the box, my guess would be it is already using PWM to control the pump. It would be madness not to given that the facility is already built into the Gen 6
House-3 bed partial stone bungalow, 5kW Samsung Gen 6 ASHP (Self install)
6.9 kWp of PV
5kWh DC coupled battery
Blog: https://thegreeningofrosecottage.weebly.com/
Heatpump Stats: http://heatpumpmonitor.org/system/view?id=60
Posted by: @raiphKaiflex pipe. My concern is that it's a corrugated pipe so the water flow through it will not be laminar. An inner diameter of 25.4mm should be OK for a 8K HP.
To quantify the greater pressure drop of your corrugated pipe you could try using an online calculator like https://www.pressure-drop.online/
For example, at 20 l/min a 25.4mm corrugated pipe (5mm high corrugations every 10mm) has five times the pressure loss per metre than a 28mm copper pipe. 0.010 bar vs 0.002 bar per metre.
Your pump(s) will be using more energy to overcome this pressure drop than would be the case if your pipes were 28mm copper.
- 26 Forums
- 2,618 Topics
- 61.1 K Posts
- 642 Online
- 6,994 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Renewables & Heat Pumps in the News
An article on funding for heat pumps in case anyone is ...
By Jeff , 34 minutes ago
-
RE: Indevolt Batteries UK Support & Info Thread
Thanks @editor , @indevolt-uk Subject to any comments ...
By JamesPa , 8 hours ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
@seoras Sorry to hear that. I found Vaillant very help...
By JamesPa , 9 hours ago
-
The Watchdog That Watched and Waited
On 9 January 2026, Consumer Energy Solutions collapsed ...
By Mars , 12 hours ago
-
RE: GSHP Kaput After 16 Years: New Compressor or Switch to ASHP? Advice Welcome
Cool Energy in Grimsby sell ground source heat pumps an...
By DerekDeLeon , 13 hours ago
-
RE: Valliant Heat Pump Settings
Thats arguably a sign of a good installer - they unders...
By JamesPa , 14 hours ago
-
RE: Electricity price predictions
Well, we have so many cases where rain water mixes with...
By Batpred , 15 hours ago
-
RE: Two heating zones to one zone
@profzarkov They arent obviously wrong, but the only...
By JamesPa , 17 hours ago
-
RE: Towns water feed to air source heat pump system
The DHW circuit cant be separated (well it could, you c...
By JamesPa , 17 hours ago
-
Solis AC-coupled 3kW storage inverter
Solis AC-coupled 3kW storage inverterPylontech batterie...
By MartinRobinson , 23 hours ago
-
RE: My NIBE ASHP Nightmare: No Commissioning, High Bills and a Hostile Installer
As @transparent has observed above, this is not bad, an...
By cathodeRay , 1 day ago
-
RE: The Grid Says Yes.. Until It Doesn’t: Why Britain's Net Zero Push is Stalling at the Plug Socket
As I was reading this article Mars, I was thinking that...
By Toodles , 2 days ago
-
RE: Tell us about your Solar (PV) setup
Installed in May 2011: 16*Sharp 245 W monocrystalline p...
By txmartyn , 2 days ago
-
-
RE: Say hello and introduce yourself
That doesn't sound 'right' to me. The national Smart ...
By Transparent , 3 days ago
-
RE: Growatt battery disconnected
I doubt this will happen, but I will try and suggest it...
By Eliuccio , 3 days ago
-
Understood. That's why I decided from the outset on a ...
By JamesPa , 3 days ago
-
RE: My experience with 3 heat pump surveys: Heat Geek, British Gas & Octopus
On the litigation, I would not go there and definitely ...
By Batpred , 3 days ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
I suppose if your pv inverter packs up, you have a plan...
By Batpred , 4 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Firstly check you are using sound power not sound press...
By JamesPa , 4 days ago
-
That’s the solar up and running, I don’t think it’s the...
By David999 , 4 days ago
-
RE: Seeking ideas / information / commiseration - Pure Drive
I agree with @colinc that you can reuse some of it. A s...
By Batpred , 4 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@toodles Im trying me best to ignore orangeman, I figur...
By Papahuhu , 5 days ago