Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
Advice on Vaillant Sensocomfort
Currently running our arotherm plus 5kw in manual mode for the heating, with the heat curve set at .45. Room temp mod is set to inactive. I'm aware that the controller ignores the desired temp set, and modulates to the heat curve, in manual mode however my question is what happens in time control mode? Does it work the same as manual mode and just modulate to the heat curve or is it trying to use the controller thermometer even though room temp mod is set to inactive? What happens in the setback period? I'd have liked it if there was a way to adjust the heat curve downwards in any setback period however it doesn't seem that that is possible, and I'm concerned it's running off room temp and therefore running less efficiently. I'm basically trying to work out if there is a way to run the ASHP very efficiently, whilst also adjusting the temps down slightly at night as we are finding our daytime temp of around 19c is too hot at night.
Am I right in thinking that the way to set up fully weather comp mode is by putting the controller into room temp mod inactive mode?
Lastly, any thoughts on the myvaillant app? We currently don't have it as I was happy to use the controller, however I wasn't aware before we got it how many movements through the menu I'd have to take just to turn things on and off! I'm also wondering if the app would be useful for monitoring useage etc.
I can’t answer your questions on the inactive mode since we’re not using at present (using expanded because we still have solar gain) but I can answer you can’t set WC coefficient dynamically but I can’t see why you would need to .
The app is very much worth getting you can scroll through days, consumption per hour, COP, room temp, outside temp and download full data set for a separate analysis from it. We been very pleased with daily COP of 6 usually and although early on Friday ~9am when it was recovering from set back and OAT was 2C the COP for the day was 3 by the end of the day’s temp profile the daily COP was 5. So it will definitely give you the information you need to optimise.
But it’s a pig to install correctly we needed Vaillant support (and we’re technically minded).
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with SCOP 4.7) open system operating on WC
@judith Sorted out the first issue with folk on the Vaillant fb page, it was a misunderstanding on my part.
Re the app - how do you find the data on cop etc stacks up against the data on the sensocomfort? Our hp is currently running at very low flow temps, around 24c, yet the scop recording is dropping from 4.25 to 3.8. The install is good, so I'm a bit concerned theres something going on in the background I need to adjust. One reason for getting the app would be to confirm that these numbers are correct.
The way I read the sensocomfort manual is the flow temperature on the curve only apply at a target indoor temp of 20. If you adjust this up or down the curve 'shifts about 5C for every 1C difference in the desires indoor tem.'. So in the day at 20C might be low 40C flow at an outside of 0C and with a 18C setback might be 30C flow at 0C outside.
I found https://energy-stats.uk/vaillant-arotherm-weather-curve-information/ which seems to back up the way I understand the manual.
Now I don't have a heat pump so this is what I understand with my system boiler & the sensocomfort controls. I'm pretty sure the behaviour is the same irrespective of heat source.
@gunboatdiplomat I found this useful for quickly working out diff flow rates.
https://heatcurve.psimonkey.org.uk/
The app and sensocomfort align for instantaneous readings but the app gives you the pattern over time and allows you to see heating and dhw independently. You might have the dhw set to keep refreshing the cylinder temperature for example and hence see cop variations which don’t make sense. We’re on timed for dhw.
I've not seen any difference in values between the two. You’ll need the sensocomfort to change the settings the app doesn’t do that much.
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with SCOP 4.7) open system operating on WC
Posted by: @jwilliams89@gunboatdiplomat I found this useful for quickly working out diff flow rates.
This is great! Where did you find it?
@ectoplasmosis Someone sent it to me on a post on FB. although interestingly the values are slightly different to those on the page on energy stats. Still a nice quick tool.
@jwilliams89 The reason for asking is that the tables on the Energy Stats website are incorrect, and in a way so is the Vaillant manual.
The actual heat curve equation is:
TFlow = a * (HC * (Tset - Tout))b + Tset
a = 2.55
b = 0.78
@jwilliams89 Yes, it is accurate. You can verify it by modifying your desired temperature and checking the new target flow temp on the controller.
@ectoplasmosis I did wonder. I was noticing this was more similar to the readings I was actually seeing.
- 26 Forums
- 2,590 Topics
- 60.3 K Posts
- 523 Online
- 6,922 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Air-to-air heat pumps - best models and installers
@ashp-bobba, do I remember correctly that you install A...
By Mars , 7 hours ago
-
RE: A2A vs A2W: Which Heat Pump Would You Pick?
There isn’t as far as I know, @djh, but you’re welcome ...
By Majordennisbloodnok , 11 hours ago
-
RE: Can anyone explain the following behaviour with a Grant Aerona 3 R30 / Smart Controller?
Final Update. Yesterday, I was going through the moti...
By Unsure , 13 hours ago
-
RE: How much can an east/west solar solar system be oversized?
Best performance occurs with PV string near inverter no...
By bobflux , 13 hours ago
-
RE: Forum updates, announcements & issues
Thank you Mars for all your dedication to improvements;...
By Toodles , 16 hours ago
-
RE: Who do I complain to about a poor ECO4 installation, can anyone advise?
Take it one step at a time. If you can get the dhw and...
By JamesPa , 22 hours ago
-
RE: Selling 2 x Kensa Shoebox 7kw GSHP (New)
Hi Jain, we’ve got an ashp so I’m afraid we won’t be yo...
By Judith , 22 hours ago
-
No buffer or low loss header Grant controller in sens...
By JamesPa , 1 day ago
-
RE: Are We Sleepwalking Into Another Race to the Bottom?
That's an amazing job to get all that in there! A truly...
By Batpred , 1 day ago
-
RE: Anyone concerned about GivEnergy?
Thanks for your advice - I'll keep trying with the inst...
By JohnDwyer , 2 days ago
-
RE: Plug and play solar. Thoughts?
I am also yet to find a case where an installation that...
By Batpred , 2 days ago
-
RE: British Gas vs Octopus Energy vs Heat Geek vs EDF vs Aira vs OVO vs EON.Next vs Boxt
This is what I got from OVO. At least it was quick.. ...
By Batpred , 2 days ago
-
RE: IVT greenline HT Plus E - Circulation Pump Constantly On
Welcome to the forums. Irrespective of which brand yo...
By Mars , 2 days ago
-
RE: 7.5kW Heat Loss, But Quoted a 10kW Midea. No Re-Pipe, No Buffer Tank. Does This Add Up?
Oh, how I love these old scientists!I'm in with your 5 ...
By LeJamaisContent , 2 days ago
-
RE: Jokes and fun posts about heat pumps and renewables
@jamespa Someone who is not easily phased I suppose.
By Toodles , 3 days ago
-
@downfield Once OE had removed our gas meter and capped...
By Toodles , 3 days ago
-
Living with a Low Loss Header (Or Measure For Measure, it’s All About the Pump)
I know, low loss headers (LLHs) aren’t necessarily ‘low...
By Toodles , 3 days ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
After seeing umpteen negative price slots again today, ...
By ChandyKris , 3 days ago
-
RE: The Reality Behind a Failed Heat Pump Installation – and an IWA Insurance Rejection
@ian-w Getting back to the problem in hand, what do yo...
By JamesPa , 3 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@papahuhu Generally, I leave Homely to take care of mat...
By Toodles , 3 days ago
-
@judith, glad you found the story interesting. On eff...
By Mars , 4 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
The vaillant controller and app do all of that (and mor...
By JamesPa , 4 days ago