Samsung gen 6 - how to manually turn on/off immersion (booster)
Hi all,
New to the forums - I've just had a Samsung gen6 12kW ASHP installed, and initial impressions are good - install seems good and it's running well.
One thing I can't figure out is a quick/easy way to manually (and/or schedule) the immersion to come on/off.
We are on Octopus Agile tariff, so occasionally get very cheap or free electricity slots. I've disabled the scheduled legionella cycle (we empty and reheat the tank twice daily), and try to schedule DHW reheats during cheaper periods. But I'd like to be able to manually turn on/off the immersion to take advantage of cheap/free pricing slots to manually manage heating the DHW tank to higher temps when it's cheap/free (as a cheap/free store of energy and manual legionella protection). Is there an easy way to turn on/off the immersion?
In the control panel schedule, I use Standard DHW to schedule the overnight reheat, and it reheats in around 20-25mins depending on starting/ambient temps (Max Operating Time (3025) and Delay Time (3032) both set to 60min to prevent immersion from kicking in on normal DHW reheat cycle). I understand the Power option uses the immersion - does the Power option use the immersion for the whole cycle? If so, I could use this, but not sure how to then heat above my max DHW temp setting of 50C (FSV 3021) or does 3021 limit only apply to the ASHP, not the immersion?
I'd like to understand exactly how the legionella (disinfection) cycle operates? I have a set point of 47C for DHW, with a max temp set to 50C (FSV 3021). Does the legionella programme heat to 50C using the ASHP and then use the immersion to boost this to 60C (or whatever it's set at in FSV 3044), or does the whole cycle use the immersion (booster) heater?
Thanks in advance,
OS
Samsung 12kW gen6 ASHP with 50L volumiser and all new large radiators. 3.645kWp solar (south facing), Fox ESS inverter.
Solar generation completely offsets ASHP usage annually. We no longer burn ~1600L of kerosene annually.
@old_scientist HI OS, yeah you're right using the power mode or forced mode the delay timer for the immersion heater will be neglected and will switch on straight away.
You can use the over shoot setting #3033 and increase to 4, so it will heat 4 degrees over your set temperature.
So I think you can set a very long delay for the booster heater, when running the DWH on standard mode, that way the booster will almost never turn on. Then when you want to do a manual heat up, use the power/forced mode to fire up the immersion heater straight away.
Samsung Gen6 8kw ASHP in a two bed victorian mid terrace.
@ecobaker Thanks. Hopefully we may have some cheap pricing slots on Agile this weekend, so I will be able to have a play and observe how these settings behave in practice.
I have already set a long Delay Time (3032) of 60mins to prevent the immersion kicking in in normal operation, but have not tried Power or Forced mode yet to see how they behave. I'll check #3033, but I suspect it's at the default value of zero.
Not sure how I can use this to get to higher temps though (for manual legionella cycle), as the max temp is 55C, and the max overshoot is 4C, giving a combined max achievable temp of 59C?
Samsung 12kW gen6 ASHP with 50L volumiser and all new large radiators. 3.645kWp solar (south facing), Fox ESS inverter.
Solar generation completely offsets ASHP usage annually. We no longer burn ~1600L of kerosene annually.
@old_scientist My one thought is that if you’re getting 100% efficient very cheap hot water, is that still more expensive than 400% efficient heat at your standard rate?
How cheap are the cheap rates? It might not actually be worth doing because of the reduced efficiency.
Samsung Gen6 8kw ASHP in a two bed victorian mid terrace.
@ecobaker absolutely correct - I'd only manually kick in the immersion when prices turn negative, so (a) I can store energy by heating DHW as high as possible (above my normal set point), and (b) allow me to run the DHW through the immersion AND the heating simultaneously (in winter), thus capitalising on any negative pricing slots.
Under normal circumstances (i.e, if I'm paying for it), the immersion stays off as it's far more efficient to use the ASHP.
Samsung 12kW gen6 ASHP with 50L volumiser and all new large radiators. 3.645kWp solar (south facing), Fox ESS inverter.
Solar generation completely offsets ASHP usage annually. We no longer burn ~1600L of kerosene annually.
- 22 Forums
- 2,067 Topics
- 45.3 K Posts
- 51 Online
- 3,339 Members
Join Us!
Trusted Installers
Struggling to find a reliable heat pump installer? A poor installation can lead to inefficiencies and high running costs. We now connect homeowners with top-rated installers who deliver quality work and excellent service.
✅ Verified, trusted & experienced installers
✅ Nationwide coverage expanding
✅ Special offers available
Latest Posts
-
RE: Antifreeze top up for my heat pump - is this a rip off?
@johnmo This is not really an adequate response....
By ecodan-efficiency , 3 hours ago
-
RE: Nibe F2040 periodic warm water increase fails
No worries, thanks a lot for thinking along 🙂
By tribol , 6 hours ago
-
RE: Load Compensation and Weather Compensation
Still not quite. As I read this the body adjusts for f...
By JamesPa , 9 hours ago
-
RE: Enabling WiFi: Samsung ASHP on Smart Things App
@old_scientist That’s really interesting that you switc...
By Grahamh-uk , 11 hours ago
-
RE: Vaillant & OVO partner up to offer Heat Pump Plus
@ecodan-efficiency On the other hand, the fact that the...
By Richard24738 , 17 hours ago
-
RE: How accurate was your heat loss survey?
@scalextrix for our house 1950s detached the air leakag...
By Judith , 19 hours ago
-
-
RE: Air Changes per Hour - ACH and the MCS requirement
@matwin If you plan to commission one it might b...
By JamesPa , 1 day ago
-
RE: Jokes and fun posts about heat pumps and renewables
In a similar vein, this recent spell of sustained good ...
By Majordennisbloodnok , 2 days ago
-
RE: Home energy storage & battery register
By the end of next month... 8 kW PV + Tesla Powerwall...
By Algienon , 2 days ago
-
RE: Various different approaches to battery storage.
I thought I'd share my story/journey and experiences he...
By Old_Scientist , 2 days ago
-
RE: Commencing on an ASHP Installation Process
It varies by room, but the conservatory is assumed at 2...
By Sheriff Fatman , 2 days ago
-
RE: Renewables & Heat Pumps in the News
Here on the Forum we're going to need to be increasingl...
By Transparent , 3 days ago
-
What I Wish I Knew Before Installing a Heat Pump
I’m putting together the next Homeowners Q&A episod...
By Mars , 3 days ago
-
RE: Planning Update: 1 Metre Boundary Rule for Heat Pumps Has Been Scrapped
In Scotland they still follow the MCS rules, so the noi...
By Johnmo , 3 days ago
-
RE: Getting the best out of a heat pump - is Homely a possible answer?
@johnmo and @benson Thanks! I was aware there was a p...
By MarcT , 3 days ago
-
RE: Is your heat pump insured?
My insurer just asks the question: "Is your home heated...
By AndrewJ , 3 days ago
-
RE: Say hello and introduce yourself
@cathoderay Ah yes, that’s the name! The Heat Pimp, It’...
By Toodles , 4 days ago
-
By the way, I also think our industry need to get on bo...
By ASHP-BOBBA , 5 days ago