Samsung E911 intermittent issue
Posted by: @netdonkey@editor it’s one of their agents. They did say the name of the company but can’t remember it!
just remembered the name! https://atlasservicessolutions.co.uk/
Just a quick update. It looks like it may be the actual Samsung is broken. Whether it's been caused by the 16 litres of glycol the installer put in for our 12 radiator system or not is still to be seen. Waiting for Samsung to open tomorrow to get them to come out
Just an update to let everyone know that we are now all back up and running after 2 weeks of no heat in the coldest January in a while.
We finally had the installed agree to drain the system and flush everything through. When he was disconnecting the ASHP from the outside flow and return he removed some lagging beside the shut off valves and spotted something he hadn't noticed before. The shut off valves also had filters in them
Opened them up and they were caked. Cleaned them out and did another flush for good measure and we are back with heating!
Thanks for everyones input into this!!
-
How can I programme a setback for my Samsung Gen6 8kW heat pump?
4 days ago
-
Samsung problems
1 month ago
-
Sudden drop in COP
2 months ago
-
Samsung's Cold Shoulder: Should Heat Pump Manufacturers Be More Accountable?
2 years ago
-
Any installer recommendations for Samsung ASHP?
2 years ago
- 26 Forums
- 2,208 Topics
- 48.7 K Posts
- 56 Online
- 5,868 Members
Join Us!
Podcast Picks
Latest Posts
-
@ashp-bobba Thanks. I'll be interested to find out why ...
By bontwoody , 12 minutes ago
-
RE: Bizarre Retro-fixes by AAC
@editor So the risk was an uncontrolled electrical elem...
By ASHP-BOBBA , 37 minutes ago
-
RE: Daikin 9kW to 8kW Swap Offer from Octopus
The ACH can actually make a huge difference. My heat l...
By Matban , 2 hours ago
-
Can that be interrogated using Modbus? Over an RS485 ...
By Transparent , 3 hours ago
-
If you've never played (or heard of) Pirate Fluxx, then...
By Transparent , 4 hours ago
-
RE: Samsung Heat pump with Yonos Pico circulating pump running all the time
Doesn't the Joule preplumbed cylinder include a buffer?
By JamesPa , 5 hours ago
-
RE: Renewables & Heat Pumps in the News
It rather depends on what we call 'local area' and 'tot...
By Transparent , 12 hours ago
-
RE: Mitsubishi Ecodan F8 error
Better than an early Windows/DOS error 'Faulty keyboard...
By JamesPa , 13 hours ago
-
I can now, I done an automation in Home Assist...
By DREI , 13 hours ago
-
RE: Bosch CS5800i 5kW - Experience So Far
What a difference a pump makes. We don't have OpenEne...
By Steelbadger , 13 hours ago
-
RE: Inventor (Midea) Heat Pump short cycling advice
I installed the 80L tank (volumizer) things got better ...
By immunity , 17 hours ago
-
RE: Testing new controls/monitoring for Midea Clone ASHP
@papahuhu at the end of the day if you are happy with h...
By benson , 1 day ago
-
RE: Can you recommend a Mitsubishi service engineer in the Rochdale area?
@dgclimatecontrol We'll all need annual servicing. How...
By Suzy-shadow , 1 day ago
-
RE: Octopus tariffs - a quick comparison
Does indeed need checking, @tim441. Neither Homely ...
By Majordennisbloodnok , 1 day ago
-
RE: How not to install a heat pump
Delighted to hear that the buffer has been replumbed as...
By JamesPa , 1 day ago
-
-
RE: The Hidden Secret to a Successful Heat Pump: Pipe Size Matters
@davidnolan22 So far as I can tell from the 'other p...
By JamesPa , 2 days ago
-
RE: 5 Star Service from Havenwise
I keep getting havenwise ads on my Facebook feed, so cl...
By benson , 2 days ago