Samsung E911 intermittent issue
Posted by: @netdonkey@editor it’s one of their agents. They did say the name of the company but can’t remember it!
just remembered the name! https://atlasservicessolutions.co.uk/
Just a quick update. It looks like it may be the actual Samsung is broken. Whether it's been caused by the 16 litres of glycol the installer put in for our 12 radiator system or not is still to be seen. Waiting for Samsung to open tomorrow to get them to come out
Just an update to let everyone know that we are now all back up and running after 2 weeks of no heat in the coldest January in a while.
We finally had the installed agree to drain the system and flush everything through. When he was disconnecting the ASHP from the outside flow and return he removed some lagging beside the shut off valves and spotted something he hadn't noticed before. The shut off valves also had filters in them
Opened them up and they were caked. Cleaned them out and did another flush for good measure and we are back with heating!
Thanks for everyones input into this!!
-
First time wall mounting an ASHP
2 months ago
-
How can I programme a setback for my Samsung Gen6 8kW heat pump?
2 months ago
-
Samsung problems
4 months ago
-
Sudden drop in COP
5 months ago
-
Samsung's Cold Shoulder: Should Heat Pump Manufacturers Be More Accountable?
2 years ago
- 26 Forums
- 2,364 Topics
- 53.6 K Posts
- 314 Online
- 6,029 Members
Join Us!
Worth Watching
Latest Posts
-
RE: ASHP sizing - value of Heat Transfer Coefficient
I'm a moderator on other, unrelated, forums and the com...
By Sheriff Fatman , 19 minutes ago
-
RE: Solis S6-EH1P8K-L-PLUS – Why I Chose It and What I’ve Learned So Far
I agree, @drei, that I dislike companies having control...
By Majordennisbloodnok , 37 minutes ago
-
Changing from 4-port buffer to volumizer
BackgroundI bought a house at the beginning of 2025. Th...
By Andy1618 , 1 hour ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
TC Thermostatic Radiator Valve TRV Plastic Decorators S...
By Toodles , 20 hours ago
-
RE: Ecodan unable to hit legionella target temp - what's the consensus?
UPDATE: Thanks everyone who commened with suggestions h...
By 9jwr9 , 1 day ago
-
-
How long will your energy contract last?
Some heat pump tariffs don’t run as long as a heat pu...
By Toodles , 3 days ago
-
@morgan They are unsupervised these days, can’t get the...
By Toodles , 3 days ago
-
-
RE: Setback savings - fact or fiction?
Exactly. We only need to compare conditions, to decide ...
By cathodeRay , 4 days ago
-
RE: Balancing financial efficiency and comfort using the Octopus Cosy tariff
I found because I have very low heat loss I can set bac...
By RadWhisperer , 4 days ago
-
RE: Need Help Optimising My Rushed ECO4 Install: 12kW Bosch Heat Pump
Welcome @mickamills We too have an oversized 12kW Sa...
By Old_Scientist , 4 days ago
-
RE: My Powerwall 3 Consumes 3-4 kWh/Day in Self-Consumption: Is This Normal?
@caron I can confirm that the power usage of the PW3 is...
By Old_Scientist , 4 days ago
-
RE: Speedcomfort radiator fans
Thats true, but having tried (and succeeded) in constru...
By JamesPa , 5 days ago
-
RE: Heat Pump Heats the House… But It’s Not Cosy. Emitter Changes or System Tweak?
@alastair There I was, feeling grumpy, he said “Cheer u...
By Toodles , 5 days ago
-
RE: Grant Aerona: Is there a setting to keep the 2-port valve open during pump blockade
Depends on OAT. Mine cycles at OAT>10 and of course...
By JamesPa , 5 days ago
-
RE: New Fogstar 15.5kWh upright solution
@transparent My conclusion is as you have noted, tha...
By Bash , 5 days ago
-
RE: Mitsubishi Ecodan R290 10kW performance
And to you too. Wishing you a very enjoyable festive s...
By Sheriff Fatman , 5 days ago
-
RE: External pipework insulation
They do? But that isn't apparent from the photos we'r...
By Transparent , 5 days ago
-
RE: Say hello and introduce yourself
@velcro welcome to the forums. Please feel free start a...
By Mars , 6 days ago