Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
New member - advice sought on Mitsubishi heat pump
Hello, just joined after going through most of the heat pump info on this site. Great site! - loads of useful info.
I'm new to heat pumps but am a chartered engineer with good electrical/electronic/mechanical knowledge - and a deal of practical electrical and plumbing installation. Recently acquired a 3 year old Mitsubishi (W85VAA) 8.5kW packaged heat pump together with an FTC6 control box. Heat loss calculations for house showed annual heating requirement of 6600 kWh (space heating load of 5.3kW) and recommended a 6kW ASHP.
House is a well-insulated timber frame construction in Bedfordshire with gas boiler to UFH on ground floor and radiators first floor. The current system is well-controlled and running fine so my thoughts (for which I would appreciate comments) is to utilise the ASHP in a hybrid situation until the boiler is end-of-life and then go full heat pump. My thoughts would be to connect the heat pump inside the house to a plate HEX in the return pipe to the boiler. That might sound crazy when there is already a plate HEX inside the outdoor unit but I really don't want glycol mix running round the whole system - and current controls are adequate! I guess the heat pump circuit would need a pump and expansion vessel inside the house. Comments and criticisms from the experts welcome!
Hi @jvs197 and welcome!
My first observation is that your 8.5kW ASHP is already oversized for your sumptuously-insulated house.
So your system design will need to avoid two possible events
- the HP cycling on/off, which uses more energy (and hence lowers the COP)
- the return water temperature to the HP being too warm... because it's unable to export enough heat into the boiler circuit via your HEX
At this point it is usual for a professional installer to insert an overly-expensive buffer-tank in the return pipe to the HP.
Heat is lost in that, thereby keeping the return water cool enough.
It's worse in your case because you aren't sending the output from the HP to anywhere else... just the HEX.
My next observation is that the rise in temperature of the return to the boiler is bringing forward the moment when it will drop out of condensing mode.
So it too would now be operating inefficiently.
The key to these issues must surely lie in a 'control' which prevents the boiler firing if the water arriving in it's return is above the temperature at which the condensing operation ceases.
It's typical of an Arduino project... which you may find appealing, given your background!
One of the first professionally implemented Heat Pump trials in the UK was done with funding assistance from the Welsh Government.
The Freedom Project implemented hybrid heat-pump systems in a number of housing authority homes.
Unusually, the highly competent engineers who designed the systems also supervised the installation and operation throughout the trial.
The results therefore show a level of competence which was in short supply from later BEIS-funded trials!
If I wanted to analyse the best way to implement a hybrid system, that's where I'd start.
The Freedom engineers were drawn from Western Power Distribution (electricity) and Wales & West Utilities (gas).
Some those engineers now work in senior roles within National Grid Electricity Distribution.
With a bit of ingenuity, you can probably work out their email addresses and contact them direct!
Save energy... recycle electrons!
Posted by: @jvs197Heat loss calculations for house showed annual heating requirement of 6600 kWh (space heating load of 5.3kW) and recommended a 6kW ASHP.
We swapped to a HP 2 years ago, after running a regular gas boiler for many years. We have smart meters, so could correlate daily gas kWh with the outdoor temperature. An advantage of gas boilers is that gas in very closely aligns to heat out - just assume an efficiency of 90%. Do you have figures for how many kWh/year of gas you have used? It's a great way to check the calculations!
I'm a little confused by the figs you gave - 6600kWh annually is lower than a heating load of 5.3kW would imply. Our measured numbers are 4500kWh/yr heat (using 1400kWh elec), 2kW peak heat load.
While "short cycling" of a heatpump is bad (more than 6 On/Off cycles per hour), there will inevitably be On/Off cycling when you need less than the minimum power of the heatpump which is perhaps 30% of full power. Cycling fatigues copper joints, and leaves heat in the outdoor stuff which is a waste. Our heatpump cycles once / hour, and can't be avoided as I see it.
The manufacturers will give minimum required system water volumes, so that there's enough thermal mass to cope with defrost. Zoning and TRV throttling reduces the minimum volume, and is the reason that a buffer is generally added. We don't have a buffer, have no zones, TRV's either removed or set to max.
Cheers, R
@transparent Thank you for your quick reply (anyone want an 8.5kW HP?!!)
Yes, I was a bit concerned that the HP is over-powered but then, with the assumptions made in heat loss calculations (I used the HeatPunk one), the final figures are only 'ballpark'. If I had an 11 or 14 kW Mitsubishi then I would certainly not go ahead - but 8.5...? In fact I have seen on this site that some over-sizing is quite acceptable in some folk's opinions.
Interesting point about boiler not condensing because return water temperature might be too high. I understand that it needs to be below 55 deg. The calculation for the heat pump was based on a flow from the HP at 45 deg - so no worries there.
Yes, need control to prevent boiler firing if return too hot - but that's a simple circuit (no need for microprocessors!). That point should not however be reached as explained above.
Thank you for your hint about 'FREEDOM'.
@robl Thank you for your reply. The 5.3kW figure came out of the heat loss calculation (using HeatPunk). Gas consumption over the last year was 9890kWh covering space heating and hot water (and a little for cooking). Took the consumption in July/Aug as predominantly meeting hot water requirement and assumed the same rate over the whole year - that was 3270. So space heating was 6620. I accept that figures were therefore approximate!
Posted by: @jvs197I understand that it needs to be below 55 deg. The calculation for the heat pump was based on a flow from the HP at 45 deg - so no worries there.
Erm... what's the return water temperature for your boiler in its present situation?
If it's above 45degC, then your HP won't be able to add anything more to it.
Messrs Flanders and Swann told me that!
Save energy... recycle electrons!
I suggest that you experiment with your present gas system, so that you can determine how well an ashp could work. It’s what I did before installing our gshp. We had a ‘regular’ gas boiler- ie just a heat source, and a smart gas meter. I set the pump to mid, the boiler to low flow temp, the home thermostat to highest, all TRVs on full. Then ran the system for an hour to let it stabilise, upped the flow temp a little to stop it cycling on/off. When running stably, I used a thermocouple taped (and insulation over it) to the boiler flow and return, home air temperature and took a note of the smart meter gas power. From these measurements I accurately predicted the running temp that we would get with a heatpump, just by linearly extrapolating them. I got a 5C ( Tflow-Tair) rise per kW of heat, and a 2C deltaT. This predicts a flow temp of 21C+2.4kW*5. Our gshp is 2.4kW, and it runs at a flow of 32C. (Nb- we have 150mm of EWI now, so this approach works well for us - the original 1963 radiators are now ‘oversized’).
Strictly speaking rads aren’t quite linear, but it’s close enough I think if the difference is small.
-
High air source heat pump running costs – Vaillant AroTherm Plus
2 days ago
-
Bosch CS5800i 7kW replacing Greenstar Junior 28i
1 month ago
-
Rodents! A word of warning for heat pump owners
3 months ago
-
Ecodan Pump Issues… Circulation pump turns off when heat pump compressor turns off
3 months ago
-
Running my new Nibe ASHP efficiently
3 months ago
- 26 Forums
- 2,607 Topics
- 60.8 K Posts
- 641 Online
- 6,967 Members
Join Us!
Worth Watching
Latest Posts
-
-
RE: End-of-Life Heat Pumps: How Do You Dispose of an ASHP in the UK?
I brought my old R407C water to water heat pump to the ...
By bobflux , 53 minutes ago
-
Its good kit the Midea and significantly cheaper, you w...
By ASHP-BOBBA , 1 hour ago
-
RE: Indevolt Batteries UK Support & Info Thread
Have you tried cutting the grid feed to see what actual...
By JamesPa , 2 hours ago
-
Contractors pack for inta antifreeze valves are around ...
By ASHP-BOBBA , 2 hours ago
-
RE: Renewables & Heat Pumps in the News
Critics and naysayers will be negative whatever the gov...
By JamesPa , 2 hours ago
-
RE: Microbore heat pump installs
In principle you are almost certainly right, but in pra...
By JamesPa , 12 hours ago
-
RE: Electricity price predictions
@old_scientist We are a low mileage home, so bulk of ou...
By ChandyKris , 13 hours ago
-
There are just too many unknowns for me to comment on p...
By Transparent , 15 hours ago
-
RE: What is the main ‘dictator’ of Agile’s unit price?
@toodles I keep an eye on wholesale prices and energy m...
By ChandyKris , 16 hours ago
-
RE: Brand and installer questions for ASHP
Strange, perhaps it doesnt use modbus which the third p...
By JamesPa , 17 hours ago
-
RE: Upgrading my system, how far do I go?
For comparison, my PW3 with 11.04kW inverter, will char...
By Old_Scientist , 20 hours ago
-
RE: Changes to Tesla Powerwall Charging Regime?
Elon gate - legendary! I take my hat off to you @toodle...
By Old_Scientist , 24 hours ago
-
RE: Mitsubishi Ecodan not good enough ?
Thanks @goody, appreciate the feedback and sorry you ha...
By marcexec , 1 day ago
-
RE: Minimum and Zero Disrupt Heat Pump Installations
True (first sentence) Thats the reason to consider th...
By JamesPa , 2 days ago
-
RE: High air source heat pump running costs – Vaillant AroTherm Plus
Quite right. I was using a rough guesstimate of doublin...
By Majordennisbloodnok , 2 days ago
-
RE: My Grant R290 9kW Heat Pump Installation
Again, really don't know how accurate this is! &nb...
By petch , 2 days ago
-
RE: MCS Quality Audit – Has Anyone Had One? Did It Lead to Remediation?
@toodles The whole scheme is a shocking waste of money....
By Papahuhu , 2 days ago
-
RE: Anyone concerned about GivEnergy?
Many thanks for your, and the subsequent, answers tk qu...
By KevH , 3 days ago
-
RE: DIY or Don’t Touch? Solarman Smart Meter Install
Yes, and these guys would probably be my preferred inst...
By Batpred , 3 days ago
-
RE: Hot water tank lose heat rapidly on random days
@jamespa Hopefully their reasons are well intended! ...
By Bash , 3 days ago
-
RE: Ecoflow UK Support & Info Thread
As mentioned above, we’ve got our full review of the Ec...
By Mars , 3 days ago
-
RE: Say hello and introduce yourself
@sonosppp welcome to the forums. I see you've posted in...
By Mars , 4 days ago
-
RE: Guidance with installing a new heating system
@bobflux Great, thanks for the advice. The pipe has an ...
By Hamilton , 4 days ago
-
RE: Daikin Altherma 3 LT compressor longevity question
@optimistic-optimiser I have has a Daikin for a few yea...
By madsid , 5 days ago