Mitsu Wireless Controller and MelCloud
I have just had a PAR-WT60R Wireless controller fitted to an Ecodan Hydrobox and I would like to compare notes with someone who has a similar setup.
Firstly, the heating is switched off until 1st October, but MelCloud is showing "House Heating" as "Idle", whereas previous to the installation I think it stated "Stopped" or similar. Surely, it should only show "Idle" when in operating mode and having reached temperature?
(DHW is also showing "Idle" outside the timed operating period and I thought this also, previously showed "Stopped" only outside a timed period).
Secondly, the MelCloud "House heating" is currently showing "Room temperature" as 32C whereas the Wireless controller is showing a room temperature as 26C. I suspect the 32C temperature is being picked up from the thermocouple in the Hydrobox FTC6 which is located in an outside Pump Room. I seem to recall that I can change over the selected thermouple in the FTC6 menu, and would appreciate comments.
I haven't got round to looking at the menu yet, mainly because our outside temperature is currently 41C!
342sq m "Upside down" house in Algarve. Portugal
Mitsubishi PUHZ-120YUK 16kW ASHP
12 Solar Panels Growatt Inverter
2 x Growatt 7.5kW Batteries
Fronius EV Charger
Kia e- Niro 64kW
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
Yes, "Prohibit" was the word for when switched/ timed off.
So, apparently, my Melcloud is currently wrong for heating and possibly for DHW, but I am not sure if your DHW is currently switched on.
342sq m "Upside down" house in Algarve. Portugal
Mitsubishi PUHZ-120YUK 16kW ASHP
12 Solar Panels Growatt Inverter
2 x Growatt 7.5kW Batteries
Fronius EV Charger
Kia e- Niro 64kW
@davidalgarve My DHW is switched on.
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
It would seem that I have a problem (at least one!) in that both my heating and DHW are showing "Idle" when they are effectively timed off and the should be showing "Prohibit"
342sq m "Upside down" house in Algarve. Portugal
Mitsubishi PUHZ-120YUK 16kW ASHP
12 Solar Panels Growatt Inverter
2 x Growatt 7.5kW Batteries
Fronius EV Charger
Kia e- Niro 64kW
If they are 'off' because of a timed schedule, and this is their time to be 'off', it might be that it is actually in its 'idle' mode. I don't know that for sure, but in my post above, my CH is turned off in the main controller as opposed to a schedule, hence 'prohibit. The DHW is turned on but is showing 'idle' due to the temp still being above the reheat temp.
It will only show 'prohibit' if turned OFF. Not TIMED to be off. So far as I am aware.
I don't have schedules set. It's either on or off 24/7 or in Holiday Mode.
Retrofitted 11.2kw Mitsubishi Ecodan to new radiators commissioned November 2021.
14 x 500w Monocrystalline solar panels.
2 ESS Smile G3 10.1 batteries.
ESS Smile G3 5kw inverter.
@morgan I am finding it hard to accept that the display should read "Idle" when either the heating or DHW is "OFF", because I am reasonably sure that it showed "Prohibit" for this condition before the wireless control was added. It would also mean that no difference is recognised between "Up to temperature" and "Switched off"
I am still hoping for advice on the second point i.e. the fact that MelCloud (32C) is not reading the temperature of the Wireless Controller in the lounge (26C) and as such it cannot control - see photos.
I feel certain that Melcloud is still displaying the Hydrobox temperature 32C, but cannot recall where this selection takes place in the menu.
342sq m "Upside down" house in Algarve. Portugal
Mitsubishi PUHZ-120YUK 16kW ASHP
12 Solar Panels Growatt Inverter
2 x Growatt 7.5kW Batteries
Fronius EV Charger
Kia e- Niro 64kW
On the FTC5 I think this requires the dip switch on the control board switched to on when you plug in the external receiver. SW1-8 from memory. It then allows the external room thermostat to control the system.
Well it has now become obvious that the installation of the Wireless Controller is a complete washout.
Almost certainly, Melcloud is still seeing the Hydrobox temperature rather than the room temperature from the wireless controller.
More seriously, the heat pump is running at random times (often during expensive daytime tariff), totally disassociated with the schedule times set on the FTC6. This is mostly heating DHW, but on occasion has been trying to heat the house (when we are experiencing record ambient temperatures!) through towel rail etc, which do not have thermostats.
So a most unwelcome fight to unfold just to get back to where we were before they carried out the work.
342sq m "Upside down" house in Algarve. Portugal
Mitsubishi PUHZ-120YUK 16kW ASHP
12 Solar Panels Growatt Inverter
2 x Growatt 7.5kW Batteries
Fronius EV Charger
Kia e- Niro 64kW
Update: I have found that the contractor had changed one of the options to "Forced DHW", and this was probably part of the problem. Having switched this off, I am back to logical operation with Weather Compensation and early morning scheduled DHW.
I have not had any offers of support, but I wonder if someone could confirm my thoughts on the correct selection of thermistor for use with the wireless controller.
Operating with Weather Compensation (without any room thermostat), under "Room sensor setting", I have "Room RC1" (single zone) set to "Main Remote Controller". This meant that MelCloud read the temperature in the FT6 but it did nothing.
With the wireless controller in place, am I correct in assuming that, Room RC1 should be changed to read "TH1" and will therefore read the thermocouple in the PAR-WT60 wireless controller?
342sq m "Upside down" house in Algarve. Portugal
Mitsubishi PUHZ-120YUK 16kW ASHP
12 Solar Panels Growatt Inverter
2 x Growatt 7.5kW Batteries
Fronius EV Charger
Kia e- Niro 64kW
Hi David
We have an FTC7 but the settings seem to be similar to an FTC6. Our room sensor settings are:
Zone sensor selection sets zone 1 to RC1
Zone 1 programme sets programme 1 to RC1 from 00:00 (i.e. all day).
Looking at the FTC6 manual I'd guess Room RC zone select should be zone 1 and the Sensor setting for Zone 1 should be RC1 and a time of 00:00.
Hope that helps!
@robs Hi Rob,
I really appreciate your information, and this appears to me to be much clearer than that which is given in the manual under: "4 Customising your Settings for Your Home".
It seems that I was on the wrong track in suggesting TH1 and now recall that this is the thyrister in the FT6
However, just to be absolutely sure, before I attempt a second installation of the wireless remote, I am attaching photos of the 3 steps in making the settings. (Incidentally, I have left the "Time Zone" setting as was and this seems to be the same as yours, but I don't understand the significance of this in relation to sensors)
I would be grateful for your comments.
342sq m "Upside down" house in Algarve. Portugal
Mitsubishi PUHZ-120YUK 16kW ASHP
12 Solar Panels Growatt Inverter
2 x Growatt 7.5kW Batteries
Fronius EV Charger
Kia e- Niro 64kW
- 26 Forums
- 2,391 Topics
- 54.2 K Posts
- 361 Online
- 6,074 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Ecodan with FTC7 - True Weather Compensation
@sheriff-fatman Thanks for the reply I ho...
By danwright90 , 3 minutes ago
-
RE: ASHP Energy Consumption: Aira 12kW heat pump
I was supposed to write/comment about this last year, b...
By Mars , 11 minutes ago
-
RE: Installer Fitted 9kW Instead of 11kW Heat Pump and Changed MCS Paperwork - What do I do?
@mairia, I'm staggered that NAPIT have not been in touc...
By Mars , 19 minutes ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
Each inverter would be limited to 16A export. But they ...
By Batpred , 1 hour ago
-
RE: Advice for a novice on Mitsubishi Ecodan 6kW
Worth also adding that, assuming you know the rough ove...
By Sheriff Fatman , 2 hours ago
-
Daikin Atherma ASHP Cycling 6 Times an Hour?
I have a Daikin Atherma EDLQ07CAV unit and I've come he...
By John Marshall , 2 hours ago
-
RE: Octopus Cosy Heat Pump Owners & Discussion Thread
My Cosy6 heat output was 116kWh yesterday, giving an av...
By AgentGeorge , 3 hours ago
-
@majordennisbloodnok This is some really good stuff. I ...
By Steelbadger , 15 hours ago
-
RE: Gen 6 Samsung ASHP losing 20C of DHW in 60 min directly after generation
Shouldn’t your temp sensor be in the middle or lowest s...
By EcoBaker , 16 hours ago
-
RE: New Fogstar 15.5kWh upright solution
@batpred In all fairness you haven't provided any he...
By Bash , 16 hours ago
-
RE: Insulating a pitched roof with kingspan, has anyone done it?
Thank you everyone for all of the information, it looks...
By TRBob , 17 hours ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@transparent Yep, they didn’t even mention it. When ...
By Papahuhu , 18 hours ago
-
Air source heat pump circuit not operational
Hi - need some advice about one circuit on my heating s...
By Plummersknowe , 18 hours ago
-
RE: Setback savings - fact or fiction?
They are lovely, and I feel lucky to live in one, but t...
By cathodeRay , 19 hours ago
-
RE: Who's your electricity provider and what's your tariff?
Worth adding that, for this tariff, the Octopus app has...
By Batpred , 20 hours ago
-
RE: APP for remote Daikin ASHP Operation
Thanks, @newhouse87. Understood. I was only asking on...
By Majordennisbloodnok , 20 hours ago
-
@mike-patrick A propos, I think my heat pump generates ...
By dr_dongle , 20 hours ago
-
RE: Mitsu Zubadan flow temperature issue
Update: The flow temperature has now stabilized at 60C ...
By bontwoody , 21 hours ago
-
Balancing UFH flow rates, pump speeds etc
I have an old building with modern extension & ashp...
By Tim441 , 22 hours ago