Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
[Solved] Low shower pressure after ASHP retrofit
Posted by: @jacs@derek-m not sure on the cylinder pressure but the flow drops massively when I open multiple taps, almost to a stop.
When you say that the flow drops massively, I assume this is at the shower head. It would appear that you have some form of restriction that is limiting the flow from or to the hot water cylinder, such that opening more taps will mean that this limited flow is being shared over more 'openings'. Because the shower head is higher than the taps it is more likely that this will lose flow first.
Try turning the shower 'cold' and open some cold taps. If the flow through the shower head remains constant then the problem is not with the shower, but is some form of restriction in the 'hot' pipework.
I would suggest that you check the pipework from the shower head back to the hot water cylinder for partially closed valves or thinner pipework. Also check the pipework from the mains supply to the hot water cylinder.
If, as Johnmo suggests, the problem is due to a pressure imbalance at the shower unit, you should ask your installer to fit a pressure reducing valve on the cold water feed to the shower unit. It should then be possible to set both the hot and cold feed to 3 bar.
@johnmo Hi, please can you confirm what balance flow is?
I turned the shower to cold and opened the cold taps and the shower flow didn't change.
Most mixers uses a balanced flow i.e. the flow pressure from hot and cold is the same. This is how it is normally achieved via the combined valve at the UVC
If you don't have this setup, you really need a check valve on the hot outlet of the cylinder to prevent reverse flow.
The alternative to the balanced flow connection on the combi valve is a prv at the cold water entry to the house set at 3bar or less. Mine is after stop cock, and strainer, then prv then to the rest of the house.
Your cold water test shows it's not a cold issue. So all that is left is the hot water supply. Testing hot on its own isn't really possible because there may always be a mix of cold going into the hot side of the mixer.
Problem resolved - there was a reducing valve under the bathtub restricting flow.
@jacs brilliant. Thanks for letting us know, and glad you’ve resolved it.
🔥 Britain’s Heat Pump Shitshow
How Installing a Heating System Became a National Nervous Breakdown
Free UK shipping.
Rewritten and updated for 2027
📘 From Zero to Heat Pump Hero
🛠️ Bodge Buster
New to heat pumps?
Take the Heat Pump Fundamentals course and use INTRO50 at checkout for 50% off.
Our newly fitted shower system was regularly running to cold if paused. The excellent plumber fitting the ashp solved it by fitting a pressure control valve on the inlet cold feed.
Different symptoms but same root cause the mixer shower needed balanced pressure feeds. Why the original plumber didn’t fit one is a good question.
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with SCOP >4) open system operating on WC
-
Has anyone seen this problem before? Huge anticycling times
4 weeks ago
-
7.5kW Heat Loss, But Quoted a 10kW Midea. No Re-Pipe, No Buffer Tank. Does This Add Up?
5 months ago
-
Bosch CS5800i 5kW - Experience So Far
7 months ago
-
My Octopus Cosy 6 Heat Pump Journey: From Quote to Completion
10 months ago
-
Yes, the "zoning with ASHP" topic again...
1 year ago
- 27 Forums
- 2,758 Topics
- 64.9 K Posts
- 1,171 Online
- 7,162 Members
Join Us!
Installer Finder
Degrees of Separation
Latest Posts
-
RE: Where heat loss surveys seem to go against practical reality
I am amazed that there is not something out there to me...
By JamesPa , 57 minutes ago
-
RE: Next steps on my ASHP journey: Radiators and Pipework
@bobflux The hydraulic simulator is very interesting...
By Rob of York , 7 hours ago
-
RE: 7kW EV Charger Options Advice
Thanks. Yes, we have patchy 4G. The only option we had ...
By Rusty , 12 hours ago
-
-
RE: Being screwed over by Volkswagen Audi Group
Thanks, @batpred. That integration is the one I have in...
By Majordennisbloodnok , 1 day ago
-
RE: How Accurate Is My DIY Heat Loss Calculation?
@batpred I suspect it will be more this year. I had 9 ...
By AndrewJ , 1 day ago
-
RE: Surface mount or bury primaries for heat pump installation?
@jamespa It's rusting 🙂
By tomasmcguinness , 1 day ago
-
RE: Glass lined Cylinder for private water supply
Thank you, once again, for your replies. Yes...
By ian33a , 1 day ago
-
It’s been out a few days and Amazon has already attache...
By Mars , 1 day ago
-
RE: Missing flow temperature in Heat Geek proposal
Yes, and this is another point I agree. We did find a f...
By Batpred , 2 days ago
-
RE: Problems with sizing a replacement for a Viessmann Vitocal 200-S
A very good point. In effect, the DHW pipework is an em...
By cathodeRay , 2 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@tim441 Here are those same three month periods for 202...
By Toodles , 3 days ago
-
RE: Adding additional Solar Panels to a DC coupled battery system
@transparent thank you for your reply above. As alway...
By Old_Scientist , 4 days ago
-
RE: Adventures in heat loss calculations
@rob-of-york — thanks for posting this, all very useful...
By cathodeRay , 6 days ago