Joining the Renewable Heating Hub forums is completely free and only takes a minute. By registering you’ll be able to ask questions, join discussions, follow topics you’re interested in, bookmark useful threads and receive notifications when someone replies. Non-registered members also do not have access to our AI features. When choosing your username, please note that it cannot be changed later, so we recommend avoiding brand or product names. Before registering, please take a moment to read the Forum Rules & Terms of Use so we can keep the community helpful, respectful and informative for everyone. Thanks for joining!
[Solved] Low shower pressure after ASHP retrofit
Posted by: @jacs@derek-m not sure on the cylinder pressure but the flow drops massively when I open multiple taps, almost to a stop.
When you say that the flow drops massively, I assume this is at the shower head. It would appear that you have some form of restriction that is limiting the flow from or to the hot water cylinder, such that opening more taps will mean that this limited flow is being shared over more 'openings'. Because the shower head is higher than the taps it is more likely that this will lose flow first.
Try turning the shower 'cold' and open some cold taps. If the flow through the shower head remains constant then the problem is not with the shower, but is some form of restriction in the 'hot' pipework.
I would suggest that you check the pipework from the shower head back to the hot water cylinder for partially closed valves or thinner pipework. Also check the pipework from the mains supply to the hot water cylinder.
If, as Johnmo suggests, the problem is due to a pressure imbalance at the shower unit, you should ask your installer to fit a pressure reducing valve on the cold water feed to the shower unit. It should then be possible to set both the hot and cold feed to 3 bar.
@johnmo Hi, please can you confirm what balance flow is?
I turned the shower to cold and opened the cold taps and the shower flow didn't change.
Most mixers uses a balanced flow i.e. the flow pressure from hot and cold is the same. This is how it is normally achieved via the combined valve at the UVC
If you don't have this setup, you really need a check valve on the hot outlet of the cylinder to prevent reverse flow.
The alternative to the balanced flow connection on the combi valve is a prv at the cold water entry to the house set at 3bar or less. Mine is after stop cock, and strainer, then prv then to the rest of the house.
Your cold water test shows it's not a cold issue. So all that is left is the hot water supply. Testing hot on its own isn't really possible because there may always be a mix of cold going into the hot side of the mixer.
Problem resolved - there was a reducing valve under the bathtub restricting flow.
@jacs brilliant. Thanks for letting us know, and glad you’ve resolved it.
Get a copy of The Ultimate Guide to Heat Pumps
Subscribe and follow our YouTube channel!
Our newly fitted shower system was regularly running to cold if paused. The excellent plumber fitting the ashp solved it by fitting a pressure control valve on the inlet cold feed.
Different symptoms but same root cause the mixer shower needed balanced pressure feeds. Why the original plumber didn’t fit one is a good question.
2kW + Growatt & 4kW +Sunnyboy PV on south-facing roof Solar thermal. 9.5kWh Givenergy battery with AC3. MVHR. Vaillant 7kW ASHP (very pleased with SCOP >4) open system operating on WC
-
7.5kW Heat Loss, But Quoted a 10kW Midea. No Re-Pipe, No Buffer Tank. Does This Add Up?
3 weeks ago
-
Bosch CS5800i 5kW - Experience So Far
3 months ago
-
Has anyone seen this problem before? Huge anticycling times
6 months ago
-
My Octopus Cosy 6 Heat Pump Journey: From Quote to Completion
6 months ago
-
Yes, the "zoning with ASHP" topic again...
12 months ago
- 26 Forums
- 2,618 Topics
- 61.1 K Posts
- 991 Online
- 6,994 Members
Join Us!
Worth Watching
Latest Posts
-
RE: Renewables & Heat Pumps in the News
An article on funding for heat pumps in case anyone is ...
By Jeff , 2 hours ago
-
RE: Indevolt Batteries UK Support & Info Thread
Thanks @editor , @indevolt-uk Subject to any comments ...
By JamesPa , 10 hours ago
-
RE: Share Your Experiences with Heat Pump Manufacturer Support
@seoras Sorry to hear that. I found Vaillant very help...
By JamesPa , 10 hours ago
-
The Watchdog That Watched and Waited
On 9 January 2026, Consumer Energy Solutions collapsed ...
By Mars , 14 hours ago
-
RE: GSHP Kaput After 16 Years: New Compressor or Switch to ASHP? Advice Welcome
Cool Energy in Grimsby sell ground source heat pumps an...
By DerekDeLeon , 14 hours ago
-
RE: Valliant Heat Pump Settings
Thats arguably a sign of a good installer - they unders...
By JamesPa , 15 hours ago
-
RE: Electricity price predictions
Well, we have so many cases where rain water mixes with...
By Batpred , 16 hours ago
-
RE: Two heating zones to one zone
@profzarkov They arent obviously wrong, but the only...
By JamesPa , 18 hours ago
-
RE: Towns water feed to air source heat pump system
The DHW circuit cant be separated (well it could, you c...
By JamesPa , 18 hours ago
-
Solis AC-coupled 3kW storage inverter
Solis AC-coupled 3kW storage inverterPylontech batterie...
By MartinRobinson , 1 day ago
-
RE: My NIBE ASHP Nightmare: No Commissioning, High Bills and a Hostile Installer
As @transparent has observed above, this is not bad, an...
By cathodeRay , 1 day ago
-
RE: The Grid Says Yes.. Until It Doesn’t: Why Britain's Net Zero Push is Stalling at the Plug Socket
As I was reading this article Mars, I was thinking that...
By Toodles , 2 days ago
-
RE: Tell us about your Solar (PV) setup
Installed in May 2011: 16*Sharp 245 W monocrystalline p...
By txmartyn , 2 days ago
-
-
RE: Say hello and introduce yourself
That doesn't sound 'right' to me. The national Smart ...
By Transparent , 3 days ago
-
RE: Growatt battery disconnected
I doubt this will happen, but I will try and suggest it...
By Eliuccio , 3 days ago
-
Understood. That's why I decided from the outset on a ...
By JamesPa , 4 days ago
-
RE: My experience with 3 heat pump surveys: Heat Geek, British Gas & Octopus
On the litigation, I would not go there and definitely ...
By Batpred , 4 days ago
-
RE: Recommended home battery inverters + regulatory matters - help requested
I suppose if your pv inverter packs up, you have a plan...
By Batpred , 4 days ago
-
RE: New Vaillant aroTherm Plus in black - When will it come to the UK?
Firstly check you are using sound power not sound press...
By JamesPa , 4 days ago
-
That’s the solar up and running, I don’t think it’s the...
By David999 , 4 days ago
-
RE: Seeking ideas / information / commiseration - Pure Drive
I agree with @colinc that you can reuse some of it. A s...
By Batpred , 4 days ago
-
RE: Solar Power Output – Let’s Compare Generation Figures
@toodles Im trying me best to ignore orangeman, I figur...
By Papahuhu , 5 days ago